I have my own thoughts on this but would like to hear what others think so I will tell my story.

New construction client is worried about location outside of city limits no city inspections. I have been following the construction stages of this home and client wanted a full structural and mechanical inspection before close of escrow and called me to do it. To make a long story short the interior of the home has not been completed to the point of inspection. The plumbing contractor was trenching for the septic system and cut the main electrical feeds to the home. The electrician came and made a temporary splice to allow construction to continue. The plumbing contractor tells the owner that the size of the incoming electrical feeds are not the proper size for the home and they should be replaced anyway. This home has one main 225 amp rated panel being fed with 4-0 copper wire in buried plastic pipe and two additional sub-panels that are fed from the main. According to what I read in the IRC 3-0 is the size for 225 amp main so I basically don't have a problem with 4-0. My problem is I am afraid the electrican is not going to re-run the main feed and just bury the temp splice. My thinking is the plumbing contractors insurance should pay for the replacement of the complete line I would not want a underground splice on new service. Here are some pics of the splice and all three panels tell me what you think.
Attached Thumbnails
have-problem-85-overlook-1-19-09-005-3-.jpg.jpg
Views:	102
Size:	72.8 KB
ID:	26319   have-problem-85-overlook-1-19-09-005-4-.jpg.jpg
Views:	100
Size:	78.5 KB
ID:	26320   have-problem-85-overlook-1-19-09-005-23-.jpg.jpg
Views:	94
Size:	70.5 KB
ID:	26321   have-problem-85-overlook-1-19-09-005-51-.jpg.jpg
Views:	129
Size:	95.9 KB
ID:	26322  



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.

Last edited by cbottger; 1/19/09 at 3:06 PM..
Reply With Quote
  #2  
Old 1/19/09, 3:15 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 359
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I have a problem

Who does the underground feed belong to, the utility or the future homeowner?

Why does the plumber think the wires are the wrong size?

If it were me I would want the wires replaced at the plumbers expense.

Also 225 is an unusual size for a main breaker. Was it really a 200 amp main?
Reply With Quote
  #3  
Old 1/19/09, 3:45 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 3,195
Default Re: I have a problem

I seen lots of 225 Amp , Any way i would think the plumber needs to pay for the cut wires ( should of got a locate before digging) . i would inform the owners and tell them whats going on and that the wires and broken conduit be replaced
Reply With Quote
  #4  
Old 1/19/09, 4:14 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 4,015
Default Re: I have a problem

How are they going to bury a splice box and remain in compliance?

That conduit looks like under rated PVC for that application? Or am I seeing things?

Also, the wire in the service panel is not the same as underground. Where is the meter can? From the looks of things, it changed somewhere along the way.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 1/19/09 at 4:18 PM..
Reply With Quote
  #5  
Old 1/19/09, 4:42 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I have a problem

That is a direct bury splice on direct bury cable. NO splice box is required or necessary. Heck, the conduit is not even necessary.

That said, there is no way in hell I'd allow this on a NEW job if I were the electrician. HE has to warranty his work and HIS name is on the job, NOT the plumber.
Reply With Quote
  #6  
Old 1/19/09, 5:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: I have a problem

So if the plumber knocks down the house, he can say "it wasn't built right to begin with," and that relieves him of any responsibility? I don't think so.

The plumber should pay to have it restored to its original condition.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 1/19/09, 5:26 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,342
Default Re: I have a problem

Maybe state what happened, in your report, and recommend client verify in writing that the splice is adequate (I can't tell how deep the trench is.)and guarantied by the electrician. He fixed it.

Let others fight it out.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 1/19/09, 5:29 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: I have a problem

Ok I am back had to run do a IR scan for a plumber contractor water leak in the ground.

My thinking and I could be wrong was the plumbing contractor that cut the service just told the home owner that the wire size was improper hoping the electrician was dumb enough to replace at his cost I think the plumber was trying to avoid liability. I don't feel a new service should have a spliced of any nature and yes the plumbing contractor should of had the service located before digging but he did not, his problem and he should pay for it.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #9  
Old 1/19/09, 5:33 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: I have a problem

Quote:
Originally Posted by jpope View Post
So if the plumber knocks down the house, he can say "it wasn't built right to begin with," and that relieves him of any responsibility? I don't think so.

The plumber should pay to have it restored to its original condition
.
Hi Jeff I think we are on the same page



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 1/19/09, 5:34 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: I have a problem

Quote:
Originally Posted by lkage View Post
Maybe state what happened, in your report, and recommend client verify in writing that the splice is adequate (I can't tell how deep the trench is.)and guarantied by the electrician. He fixed it.

Let others fight it out.
I luv a good fight



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #11  
Old 1/19/09, 5:54 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: I have a problem

Ok I am going to have to eat crow here been looking at my own pics there is a splice in the main panel indicating that the buried cable is aluminum and has a copper pig tail to the top of the main. The 4-0 aluminum is only rated for 200 amps so in essence we have a 200 amp service even though the main breaker is 225. I have not performed the inspection on this home yet I was just there sneaking a peak as requested by the owner.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #12  
Old 1/19/09, 7:00 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 3,195
Default Re: I have a problem

even though it maybe direct buried wire , now it is in conduit which is broke and has sharp edges showing i would think it should be repaired or when it is back filled it may cut into the insulation . Besides that the electrician should state that the main water line coming in is not big enough.
Reply With Quote
  #13  
Old 1/19/09, 8:00 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 359
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I have a problem

Not sure why anyone would not just bring the AL into the panel lugs. Could have just rotated the panel 180 and gone straight into the lugs.

Since the 4/0 AL is only good for 200 amps the main breaker is oversized and should be changed.

Last edited by Jim Port; 1/19/09 at 8:21 PM..
Reply With Quote
  #14  
Old 1/19/09, 8:25 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: I have a problem

Quote:
Originally Posted by Jim Port View Post
Not sure why anyone would not just bring the AL into the panel lugs.

Since the 4/0 AL is only good for 200 amps the main breaker is oversized and should be changed.
Jim a lot of strange thing happening in this home I will have a much better look when I go back for the real inspection and If I have to will look at the connection at the on ground transformer box where this buried feeder connects. I see a lot of electricians here not connect the aluminum to the top of the main they use a squeeze connection on the aluminum to copper and then take the copper on to the main



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #15  
Old 1/19/09, 8:32 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: I have a problem

If this underground cable is connected directly to a transformer at the back of the yard, this cable most likely belongs to the power company. That stated the sizing of the USE cable is covered by a different code. Granted the one splice looks good but the taped up one doesn't. I would want it entirely replaced at the plumbers expense.
Another point is underground utility locaters typically don't locate private lines. So if this line is homeowner owned, they would usually have to hire an electrician to locate it.

Last edited by rromoser; 1/19/09 at 8:36 PM.. Reason: hit wrong key
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
furnace problem ? Aaron lore General Inspection Discussion 11 2/5/09 1:04 PM
Is MAC a problem bemelander General Inspection Discussion 2 9/6/07 11:34 AM
Camera Problem nwagner Misc. Discussion 19 7/30/07 10:10 PM
Plumbing problem at home. mnahrgang Plumbing 25 7/10/07 5:32 PM


All times are GMT -4. The time now is 4:00 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts