Default Having a bad day

I was having trouble getting the camera to focus properly but not enough to create this kind of temp on a neutral wire. Be curious to know what the sparky is going to find on this one. Of all the panels I scan this was my first to come up with a high temp on a neutral wire. I just kinda stood there with this dead brain took a minute to register
Attached Thumbnails
having-bad-day-70-stoneridge-pc-9-4-11-097.jpg   having-bad-day-70-stoneridge-pc-9-4-11-029.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/5/11, 9:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Having a bad day

Since it appears that these are all two wire circuits my guess would be that it's a loose neutral connection, otherwise you should find a similar temperature at the hot conductor connected to the CB.
Reply With Quote
  #3  
Old 9/5/11, 9:07 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Having a bad day

Quote:
Originally Posted by cbottger View Post
I was having trouble getting the camera to focus properly but not enough to create this kind of temp on a neutral wire. Be curious to know what the sparky is going to find on this one. Of all the panels I scan this was my first to come up with a high temp on a neutral wire. I just kinda stood there with this dead brain took a minute to register
Looks to me like the Neutral could be carrying the return from two hot wires on the same leg.
This can happen on some panels if the breaker is installed incorrectly.
If that is the case easy fix move the two pole breaker down one position ..... Roy




Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 9/5/11, 9:13 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Having a bad day

Quote:
Originally Posted by Robert Meier View Post
Since it appears that these are all two wire circuits my guess would be that it's a loose neutral connection, otherwise you should find a similar temperature at the hot conductor connected to the CB.
Suspected loose connection my self but I was being a good boy and did not place a screw driver into the panel as much as I wanted to



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 9/5/11, 9:23 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Having a bad day

Quote:
Originally Posted by rcooke View Post
Looks to me like the Neutral could be carrying the return from two hot wires on the same leg.
This can happen on some panels if the breaker is installed incorrectly.
If that is the case easy fix move the two pole breaker down one position ..... Roy

Roy,

I'm assuming that you're referencing a MWBC which shares a neutral. Wouldn't there be a red conductor in the panel if there were a three wire cable with a shared neutral?
Reply With Quote
  #6  
Old 9/5/11, 9:55 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Having a bad day

Quote:
Originally Posted by Robert Meier View Post
Roy,

I'm assuming that you're referencing a MWBC which shares a neutral. Wouldn't there be a red conductor in the panel if there were a three wire cable with a shared neutral?
Yes thanks did not look close enough saw two pole Breakers and I now agree it looks like a loose Neutral . Thanks .

This forum is great gets us all looking and learning



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 9/5/11, 12:04 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Having a bad day

AGREED! I do not touch but I look really close at the connections. If I don't see good contact I call it out every time.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off