Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information
Default Help. What is the correct way to report a breaker that is too big.

I keep seeing reports that call a breaker too big for the circuit it's protecting as "Over Protected."

Why wouldn't it be "Under Protected?"

A breaker that is allowing too much current to pass through wires that are too small would be under protecting the wires... no?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #2  
Old 8/30/07, 1:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help. What is the correct way to report a breaker that is too big.

Nick,

Oversizing a breaker would not be safe in the same term as oversizing a fuse would not be safe.

If a conductor is 14 AWG and is designed to be protected by a 15A OCPD...in order to ensure the wire does not overheat....putting larger breaker on it would reduce the likelyhood the breaker would trip before the conductor exceeds it rating.

Now where you see smaller conductors on larger breakers under the exception of the NEC is for allowance of start up conditions and so on and demands someone having that KNOWELDGE of why it is done..but in general in normal branch circuits oversizing a breaker is the same as oversizing a fuse....the OCPD is there to protect the conductor itself..and in turn the house....

Over Protected is not a good term........UnderSized Breaker or improperly sized breaker is the better term in the case of the example I posted above.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #3  
Old 8/30/07, 1:13 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 16,045
Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information
Default Re: Help. What is the correct way to report a breaker that is too big.

Good answer, but it's not to my question.

My question is not the use of the term "oversized breaker" but the term "overprotected circuit"

IMHO an overprotected circuit is one that has an "undersized" (small) not oversized breaker.

What say ye Guru?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #4  
Old 8/30/07, 1:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,321
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Help. What is the correct way to report a breaker that is too big.

Should read "Breaker is oversized for conductors being protected and be corrected by a qualified electrician. Failure to do so may result in a fire if the circuit is overloaded.
Reply With Quote
  #5  
Old 8/30/07, 1:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Help. What is the correct way to report a breaker that is too big.

"Over-fused" is the term I use whether it's a breaker or fuse.

I've never heard the term "over-protected" used for the condition you've described.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #6  
Old 8/30/07, 1:17 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pace (Pensacola), FL
Posts: 2,970
Doug Edwards,  CMI .
Default Re: Help. What is the correct way to report a breaker that is too big.

We see it often in the Service Disconnects. Wire is 15 AWG with a 20 amp disconnect (breaker). I've been told by electricians this is not critical for this application. What is the truth? Their response is the Service disconnect is little more than an On/Off switch.



Doug Edwards, CMI


"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

John Stuart Mill






Reply With Quote
  #7  
Old 8/30/07, 1:18 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 16,045
Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information
Default Re: Help. What is the correct way to report a breaker that is too big.

Jeff, you use "over-fused" to describe a breaker that is too small or too big?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #8  
Old 8/30/07, 1:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help. What is the correct way to report a breaker that is too big.

Quote:
Originally Posted by gromicko
Good answer, but it's not to my question.

My question is not the use of the term "oversized breaker" but the term "overprotected circuit"

IMHO an overprotected circuit is one that is "undersized" not oversized.

What say ye Guru?
Depends on why you are using that term and if someone insists on using an improper term to get through life.

Lets talk about a general branch circuit...if I place a 30A breaker on a 14 AWG conductor ( not using the exceptions here )...then the conductor has a rating of 15A as defined by the NEC.....now if the load upon that breaker exceeds the 15A rating ( for simplicity sake ) it will heat up and eventually trip the breaker......now at the rating of a 30A breaker...chances are it will far exceed its relative rating where as a normal 15A breaker would have tripped.......saving a potential ground fault condition and so on possibly.

Your question is because of a use of an improper term.....

NOw I would agree with your view......could it be considered over protected by putting lets say a 15A breaker on a 30A circuit with 10 AWG conductors...sure....but being over protected would imply it will still function and in the case of the standard rating of the breaker which in this case is 30A it will shut down in a condition where it should not.....so I guess you could say it is over protected....if it helps ya sleep at night...I prefer to in this example call it Improperly Sized to the conductors being served.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #9  
Old 8/30/07, 1:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Help. What is the correct way to report a breaker that is too big.

Too big. . .

An over-fused circuit is one where the breaker is too large to adequately protect the conductors. . .



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #10  
Old 8/30/07, 1:20 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 16,045
Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information
Default Re: Help. What is the correct way to report a breaker that is too big.

I see breakers that are too big being referred to as "excessive overcurrent protection."

IMHO this is wrong. A big breaker is not protecting excessively, it is under protecting for overcurrent. No?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #11  
Old 8/30/07, 1:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Help. What is the correct way to report a breaker that is too big.

See OVERFUSED

http://www.inspectech.com/content/glossary.asp



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #12  
Old 8/30/07, 1:23 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 16,045
Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information Nick Gromicko is very trusted source of information
Default Re: Help. What is the correct way to report a breaker that is too big.

I say that "over protected", "over protection", "excessive overcurrent protection" are phrases that are being used incorrectly to describe a breaker that is too big.

Anyone disagree?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #13  
Old 8/30/07, 1:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,321
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Help. What is the correct way to report a breaker that is too big.

Nick the terms-Excessive overcurrent protection and Over protected are used incorrectly when describing the situation you posted. It's that simple and anyone using those terms doesn't get it!
Reply With Quote
  #14  
Old 8/30/07, 1:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help. What is the correct way to report a breaker that is too big.

Quote:
Originally Posted by gromicko
I see breakers that are too big being referred to as "excessive overcurrent protection."

IMHO this is wrong. A big breaker is not protecting excessively, it is under protecting for overcurrent. No?
Yes, in the case of the examples it is NOT offering the protection it is designed for in the case of an overload.

Being a breaker normally is an inverse timed breaker its trip point changes based on the level of fault current but thats a whole different story.

Best terms to use -

Undersized Breaker or Oversized Breaker........or Undersized Fuse or Oversized Fuse....clean simple and to the point.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote