Default Help Determining Reportable Service Size

Hi guys

View picture @ http://www.cthhi.com/defects.htm

Any guidance is appreciated. The listing claimed a 100 amp service however:

1. The distribution panel is rated for 72 amps,
2. The main breaker which feeds the panel is rated for 100amps. I could not open the main breaker box because it was tied shut.
3. The Aluminum service wires entering the distribution panel from the main breaker box appear to me to be AWG 3 or so.

The photo I have attached is blown up to show the true size of the service cables which measure nearly 1/2" wide including the insulation. Yes I noticed the double tap on the service cables.

I reported this as "appears to be 60 amp service" based on the size of the aluminum service wire and the rating on the distribution panel. Here in Canada I believe that 60 amp service for aluminum wire requires AWG 4. If it were a 100amp service the aluminum wire would be required to be AWG 1. Surely this wire is not AWG 1.

What do you think?
Thanks
Craig
Reply With Quote
  #2  
Old 7/17/06, 10:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Help Determining Reportable Service Size

If the panel was rated for 72 amps with a 100 amp disconnect, that would be a "reportable defect."

The double tap is a big issue. Those conductors surely can't handle the 100 amp potential from the disconnect.

The conductors appear to be tinned-copper rather than AL, and the one on the right (feed from the disconnect?) appears to have been over heated.

Main breaker tied shut? Reportable defect.

The entire system is aged and has been modified by someone other than a professional. Defer all of it. . .



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #3  
Old 7/17/06, 11:00 PM
Joseph T. Burkeson's Avatar
Joseph T. Burkeson Joseph T. Burkeson is offline
InterNACHI Member
 
Join Date: May 2003
Location: Riverview, FL
Posts: 5,857
Joseph T. Burkeson .
Default Re: Help Determining Reportable Service Size

Quote:
Originally Posted by jpope
The conductors appear to be tinned-copper rather than AL, and the one on the right (feed from the disconnect?) appears to have been over heated.
Jeff,

Good catch, very sharp eye, you must have at one time or another work as an electrician?



"Every Man Dies; Not Every Man Really Lives" ~ William Ross Wallace



God Hates Shrimp
Reply With Quote
  #4  
Old 7/17/06, 11:06 PM
cbarrows cbarrows is offline
New User
 
Join Date: Mar 2006
Location: Ottawa, ON
Posts: 57
cbarrows hasn't had much positive or negative feedback
Please Note: cbarrows is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help Determining Reportable Service Size

Jeff

Thanks for the response. What would you report as the service size?

Thanks
Craig
Reply With Quote
  #5  
Old 7/17/06, 11:14 PM
Joseph T. Burkeson's Avatar
Joseph T. Burkeson Joseph T. Burkeson is offline
InterNACHI Member
 
Join Date: May 2003
Location: Riverview, FL
Posts: 5,857
Joseph T. Burkeson .
Default Re: Help Determining Reportable Service Size

The tinned-copper is rated at 100 Amp



"Every Man Dies; Not Every Man Really Lives" ~ William Ross Wallace



God Hates Shrimp
Reply With Quote
  #6  
Old 7/18/06, 12:10 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Help Determining Reportable Service Size

Quote:
Originally Posted by jburkeson
Good catch, very sharp eye, you must have at one time or another work as an electrician?
Actually, no. I've always hated electricity

The rating would be 72 amps based on the panel rating. However, the 100 amp disconnect is improper.

It was probably a 60 amp service at one point and was over-fused by (possibly) the same person that double tapped the conductors.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #7  
Old 7/18/06, 2:21 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,858
Russel Ray .
Default Re: Help Determining Reportable Service Size

Coming home from having a margarita at On The Border, the van in front of me had this bumper sticker:

"Wiring is not a hobby. Hire a licensed electrician."



  • Need a positive networking site? Click here to join Active Rain, a networking community of 125,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 7/19/06, 4:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help Determining Reportable Service Size

Also check that "Grounding" wire that appears to be bonding to the panel case by simply wrapping around one of the screws in the back of the panel....



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #9  
Old 7/19/06, 8:12 PM
sspradling sspradling is online now
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 224
sspradling is generally well trusted
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help Determining Reportable Service Size

Nice clear photos, craig
Stu
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about Determining Electric Service Size sbelda General Inspection Discussion 2 8/18/07 3:48 PM
Service size and panels ndueker Electrical 7 4/16/07 11:41 AM
Size of service?? cbuell Electrical 4 4/14/07 5:50 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical 13 2/8/07 2:18 PM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM


All times are GMT -4. The time now is 6:15 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics