Question Help on an electrical puzzle

I did a condo inspection yesterday and ran into a puzzling situation. There was a single 220v dedicated circuit near the living room window (for AC unit). There was one 20 amp breaker that was serving two circuits (wire nut connection in box, definately not the 220v outlet). The client wanted to find out which 2 circuits involved. I do not use circuit tracer. With permission, he turned off all breakers. While I used tic tracer on outlets only, client reactivated breakers. 2 bathrooms (lights and outlets) determined to be on same circuit.
Since AC outlet was 2 pole breaker, I felt that this circuit not involved. Just for fun I placed tic tracer in 220v outlet. When client turned on breaker below 220v AC, the tic tracer indicated power yet breaker was off. Did this twice-same results. When 220v AC breaker switched off, tic tracer indicated no power. Reactivated breaker below again-tic tracer indicated power. Could this be "ghosting" or an indication of wiring issue or tic tracer sensitivity?
Any help would be welcome as I am stumped.
Thanks in advance for the assist.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
  #2  
Old 5/28/07, 4:34 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

Quote:
Originally Posted by kfonoimoana
Could this be "ghosting" or an indication of wiring issue or tic tracer sensitivity?
Very likely.

It would be somewhat normal to have an electric baseboard heater and a 240V window air conditioner receptacle powered by the same circuit in a "full" panel. This is permissible, since the heating unit and the cooling unit operate during different seasons.

Best I got...
Reply With Quote
  #3  
Old 5/28/07, 5:02 PM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Help on an electrical puzzle

Thanks for the reply Marc. There is no heating unit. The breaker below the 220v AC breaker was for living room outlets. Next time this happens I will check voltage.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
  #4  
Old 5/28/07, 5:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

TIC tracers are nice to determine if power MIGHT be present, but they are not a reliable indicator that power is ACTUALLY present. Consider them more of a personal safety device, and less of a troubleshooting tool, unless and until you feel comfortable interpreting the results.

It's certainly heroic of you to attempt to provide the client with the answer to his question, but this is an effort that is probably best left to an electrician. Many people will have an electrician into their newly purchased home for something or other soon enough, so he can ask the sparky at that point if he's still curious.

Reference this NEMA one-page bulletin on 'Phantom Voltage':
http://www.nema.org/stds/eng-bulleti...ulletin-88.pdf

Last edited by Marc D. Shunk; 5/28/07 at 5:10 PM..
Reply With Quote
  #5  
Old 5/28/07, 8:29 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

Quote:
Originally Posted by Marc D. Shunk
TIC tracers are nice to determine if power MIGHT be present, but they are not a reliable indicator that power is ACTUALLY present. Consider them more of a personal safety device, and less of a troubleshooting tool, unless and until you feel comfortable interpreting the results.

It's certainly heroic of you to attempt to provide the client with the answer to his question, but this is an effort that is probably best left to an electrician. Many people will have an electrician into their newly purchased home for something or other soon enough, so he can ask the sparky at that point if he's still curious.

Reference this NEMA one-page bulletin on 'Phantom Voltage':
http://www.nema.org/stds/eng-bulleti...ulletin-88.pdf
Somebody give this man another one of them green squares.

Very good post is a forum that needs this type of information, my hat is off to you Marc.
Reply With Quote
  #6  
Old 5/28/07, 8:53 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 2,889
Default Re: Help on an electrical puzzle

Very good dialog Kent and Mark
Reply With Quote
  #7  
Old 5/28/07, 9:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help on an electrical puzzle

Many of the tickers today have the ability to detect induction and static voltage that will cause lights to activate BUT most with audio will not actually activate the audio ( beeping ) unless actual AC voltage is present in the repective range of the unit being used.

What type of wiring are we speaking of...BX, Romex, NMC or what have you.....this could tell us something as well if using BX and using the outside case as the EGC....could be an increased G-N leakage as well.....

Anyway...does the ticker you are using have the features I stated above....glows on all currents and only beeps on actual AC voltage between the spectrum of the ticker....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 5/28/07, 10:05 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

The best tester is a table lamp or a radio if you are working alone..
Reply With Quote
  #9  
Old 5/28/07, 10:20 PM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Help on an electrical puzzle

Paul,

I use a Greenlee GT-11 with both light and audible alarm, do not know the specifics. Ticker lit up and beeped.

Greg,

The unit was empty so no lamp available. I did have ideal multitester which I used to determine voltage (210v) but did not think to test circuit when I discovered anomoly. I thought about it when I was on the road home. I will use it next time I run into similar issue.

Marc,

I read the attachment on your post and it was quite helpful. I explained to my client (in my limited way) that it was possible that the tic tracer was not providing accurate info. as it could be sensing current form an adjacent source.

Thanks again for the input.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com

Last edited by kfonoimoana; 5/28/07 at 10:31 PM..
Reply With Quote
  #10  
Old 5/29/07, 2:53 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

Good old fashioned voltage meters work every time.
Reply With Quote
  #11  
Old 5/29/07, 3:06 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

Hi kent..Since both sets of breakers control conductors running to the L/R is it possible that the 110v conductor is passing through the same box causing your induction tester or tic tracer to pick up a signal?
Reply With Quote
  #12  
Old 5/29/07, 4:24 AM
kfonoimoana's Avatar
kfonoimoana kfonoimoana is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Laie, Hi
Posts: 49
Default Re: Help on an electrical puzzle

Robert,

I suppose so. Next time I'll remember to meter it to be sure. I also just switched tic tracers from sperry to greenlee and maybe the greenlee is more sensitive.



Kent Fonoimoana
TRIsland Home Inspections, LLC
Laie, Hawaii

"For your Peace in Paradise"
http://www.TRIsland.com
Reply With Quote
  #13  
Old 5/29/07, 9:18 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help on an electrical puzzle

Quote:
Originally Posted by kfonoimoana
Robert,

I suppose so. Next time I'll remember to meter it to be sure. I also just switched tic tracers from sperry to greenlee and maybe the greenlee is more sensitive.
Very sensitive.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 5/29/07, 6:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help on an electrical puzzle

Quote:
Originally Posted by pabernathy
Very sensitive.....
Yes, they are very sensitive. Matter of fact, I used one once and called it a piece of crap. It started to cry right there in my hands... that's how sensitive it is. Be careful about that, unless you have tissues.
Reply With Quote
  #15  
Old 5/29/07, 6:26 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help on an electrical puzzle

lololololo



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Some good questions that always need answers jtedesco1 Electrical 5 6/16/06 10:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 10:24 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts