  #1  
Old 1/19/09, 2:57 PM
Ryan Brown Ryan Brown is offline
New User
 
Join Date: Jan 2009
Posts: 3
Please Note: Ryan Brown is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Help with old AL wire house

I recently bought a foreclosure in Columbia, MD and it was wired with AL wiring (built in 1974). I have already replaced most plugs and switches in the house with AL/CU rated ones, as the previous were all CU only. I have run into a bit of a problem though, and thats for the GFCI's. I am going to need one in each bathroom and then 1 in the kitchen, only problem is I cannot find a GFCI that is AL rated. Do they make them?

If not what is the best way to proceed? Use the purple ideals to pigtail copper and use a normal GFCI. Or use a GFCI breaker for the kitchen circuit and the bathroom circuit?

I also found that both bathrooms are on the same circuit which is only on a 15 amp breaker. There is also some plugs in the bedroom that are on that same circuit. That is not code these days correct? Should this be something that needs to be addressed immediately?

Thank You
Reply With Quote
  #2  
Old 1/19/09, 3:21 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Ryan,

You will not find a GFI receptacle rated for use with AL wire. You could use a GFI breaker instead. You probably could not fit the GFI receptacle in the box anyway.

Be careful working with that wiring. I had quite a few that were broken or broke off just by moving the wires in the box.

Current codes would not have the bathroom receptacles sharing circuits with other rooms, except for other bath and powder room receptacles. They would also be on a 20 amp circuit.

If you need further help send a PM.
Reply With Quote
  #3  
Old 1/19/09, 5:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Help with old AL wire house

Quote:
Originally Posted by Jim Port View Post
You could use a GFI breaker instead.
Bingo.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 1/19/09, 6:10 PM
Ryan Brown Ryan Brown is offline
New User
 
Join Date: Jan 2009
Posts: 3
Please Note: Ryan Brown is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Am I going to run into any problems with the bathrooms only being on a 15amp breaker and not 20amp?
Reply With Quote
  #5  
Old 1/19/09, 8:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Help with old AL wire house

Why would you put a 15 amp breaker on a 20 amp circuit? Purchase a 20 amp GFCI breaker. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/19/09, 8:18 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Unless he has #10 AL he will be limited to the 15 amp breaker size. #12 AL is only good for 15 amps.

At the time that house was built the requirement for the 20 amp circuit may not have existed. My Code books don't go back that far.
Reply With Quote
  #7  
Old 1/19/09, 8:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Help with old AL wire house

You're right Jim. I wasn't paying attention

Quote:
Originally Posted by Ryan Brown View Post
I also found that both bathrooms are on the same circuit which is only on a 15 amp breaker. There is also some plugs in the bedroom that are on that same circuit. That is not code these days correct? Should this be something that needs to be addressed immediately?
Unless you are re-wiring the house, there's generally no rule that says you must bring the home up to current standards - codes are not retroactive.

A 20 amp circuit is certainly preferable, but you're limited to the existing conductor size.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 1/19/09, 9:07 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

The problem you may run into is that the 15 am is more likely to trip, especially since it is shared outside the bathroom. Blow dryers and curling irons may bring this problem to light.
Reply With Quote
  #9  
Old 1/19/09, 9:48 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Help with old AL wire house

You can pigtail the Al to new Cu wire.
http://www.cpsc.gov/cpscpub/pubs/516.pdf

http://copalum.com/
Reply With Quote
  #10  
Old 1/19/09, 11:00 PM
Ryan Brown Ryan Brown is offline
New User
 
Join Date: Jan 2009
Posts: 3
Please Note: Ryan Brown is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Thanks for the info, I think the 20amp and 15 amp GFCI breakers will be the best solution as well, esp. since i already have the normal AL/CU plugs purchased.

As far as the normal 15amp AL/CU plugs go, are they pretty safe in the long term? Are they something I should check every year to see how tight the terminals still are? Or would that be overkill? I have read many things about AL wire and it seems like everyone immediatly screams your house will burn down, but if done correctly I assume there should be minimal worries.
Reply With Quote
  #11  
Old 1/20/09, 1:40 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Help with old AL wire house

Unless you copalum crimp it, or rewire it, the connections should be inspected on a periodic basis.
Reply With Quote
  #12  
Old 1/20/09, 5:42 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Quote:
Originally Posted by Ryan Brown View Post
Thanks for the info, I think the 20amp and 15 amp GFCI breakers will be the best solution as well, esp. since i already have the normal AL/CU plugs purchased.

As far as the normal 15amp AL/CU plugs go, are they pretty safe in the long term? Are they something I should check every year to see how tight the terminals still are? Or would that be overkill? I have read many things about AL wire and it seems like everyone immediatly screams your house will burn down, but if done correctly I assume there should be minimal worries.
About 5 years ago, I did a short interview about Al wire for a local Tv station. My piece was followed by a Fire Chief (25 years service) of a station right in the middle of a 1960-70's subdivision all done with aluminum wiring. He claimed he could not remember a fire in that locale that was attributed to the AL wire. Not that care/inspection should not be used.......just that it is maybe not as bad as perceived by the public.

Install lots of smoke detectors (I tell this to all my clients......they are cheap protection).
Reply With Quote
  #13  
Old 1/20/09, 3:51 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with old AL wire house

Quote:
Originally Posted by Ryan Brown View Post
Thanks for the info, I think the 20amp and 15 amp GFCI breakers will be the best solution as well, esp. since i already have the normal AL/CU plugs purchased.

As far as the normal 15amp AL/CU plugs go, are they pretty safe in the long term? Are they something I should check every year to see how tight the terminals still are? Or would that be overkill? I have read many things about AL wire and it seems like everyone immediatly screams your house will burn down, but if done correctly I assume there should be minimal worries.
Up in my part of the world, 15A is normal for bathrooms and in middle-aged homes, a 15A GFI breaker in the panel serves the outdoor receptacles as well as the baths. The Canuck rule is 12 outlets max on 15A. Should not cause nuisance tripping, but I'm no electrician and the above would not be code compliant. An electrician would see if you do indeed have #12 gauge AL and advise you further.

I never encourage home-owner wiring for this reason. If there's ever a fire in the wall, "Who touched the wiring last?"

John Kogel
www.allsafehome.ca
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Meth House? tallen General Inspection Discussion 27 4/6/09 6:21 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Waste line on OUTSIDE of house gkeene Plumbing Inspections 6 9/18/07 9:15 PM
Radon mitigation system at neighbors house? jsmith3 Ancillary Inspection Services & Additional Topics 3 5/20/06 8:42 PM


All times are GMT -4. The time now is 3:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts