Default Help please

What do you make of this? Underground service ran though the crawl
Attached Thumbnails
help-please-101.jpg   help-please-102.jpg  




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/22/11, 10:14 PM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Help please

Was that the service from the street, or a feeder for a sub panel in another building?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #3  
Old 2/22/11, 10:26 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: Help please

Quote:
Originally Posted by bsmith View Post
Was that the service from the street, or a feeder for a sub panel in another building?
From the street under a new addition.




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #4  
Old 2/22/11, 10:56 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: Help please

Is this allowed? OK?




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #5  
Old 2/23/11, 1:27 AM
rmangas's Avatar
rmangas rmangas is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Wisconsin
Posts: 57
Default Re: Help please

I would think not, considering it is sitting on the ground (considered inside the building/not buried), susceptible to damage, not secured and the opening to the lateral pipe is open to water intrusion (moisture or flooding).

It should be protected, if not still buried, secured off of the ground and a pipe should be in the opening through the foundation wall into the house; I would say the pipe that seems to go out to the service feeder should be off of the ground and protected from water intrusion.

I would just write it up as needing to be evaluated by a qualified Electrician.
Reply With Quote
  #6  
Old 2/23/11, 2:35 AM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: Help please

Generaly speaking, service entrance cable can travel a maximum of 10' inside the house before entering the service disconnect. I suppose it comes down to if the cable is in a location where mechanical damage could be anticipted. Looks like a safety hazzard to me.



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
  #7  
Old 2/23/11, 5:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help please

This is not allowed by the NEC. Service entrance conductors are not permitted to be run exposed on the floor of a crawl space. Also they must terminate in a disconnect nearest their point of entry into the structure.

Quote:
VI. Service Equipment — Disconnecting Means
230.70 General.
Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
Reply With Quote
  #8  
Old 2/23/11, 9:37 AM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Help please

If I'm understanding you correctly, this is a service lateral. With no means of disconnect until the lateral reaches the panel, that is a very dangerous condition.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #9  
Old 2/23/11, 9:50 AM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: Help please

Quote:
Originally Posted by bsmith View Post
If I'm understanding you correctly, this is a service lateral. With no means of disconnect until the lateral reaches the panel, that is a very dangerous condition.
No it runs from the street to the meter. Its underground until it reaches this crawlspace which happens to be an addition to the house.




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #10  
Old 2/23/11, 7:32 PM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Help please

Is there a means of disconnect at the meter, or at the panel? If it's at the panel, that is a dangerous situation.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #11  
Old 2/23/11, 7:39 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: Help please

Quote:
Originally Posted by bsmith View Post
Is there a means of disconnect at the meter, or at the panel? If it's at the panel, that is a dangerous situation.
Only by removing the meter




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts