Distribution panel:
4 wire feeder from disconnect, ground wire disconnected from terminal. Don't understand

Also, EGC at distribution panel. Thought it was to be at disconnect.

Last edited by waksell; 5/6/07 at 2:06 PM..
Reply With Quote
  #2  
Old 1/27/07, 11:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

Wesley,

Obviously someone has been MESSIN in the panel. Your terminology is leaving me a little confused on what you are asking but lets see here...

You refer to a Distribution Panel...Which One....a Main Distribution Panel or a Remote Distribution Panel in your second question.....

The EGC refers to the Equipment Grounding Conductor....and what exactly is the Disconnect refering to.....

The way you posted this is VERY confusing....even I am not able to break down what you are asking.



Paul W. Abernathy
Reply With Quote
  #3  
Old 1/27/07, 11:52 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

OK, service disconnect box is outside by the meter.

Distribution panel is inside the condo.

Four feeder wires from disconnect box to distribution panel, hot, hot, neutral, ground.

The ground wire is disconnected from the grounding bus in the distribution panel.

But a bare copper wire, looks like #4, goes from grounding bus up through wall, attic, who nows.
Reply With Quote
  #4  
Old 1/27/07, 11:59 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Help quick, writing report

Did the service panel or meter have an EGC too?

Just report what you see, it needs to be corrected.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 1/28/07, 12:01 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

OK,

Thats MUCH better.......sorry

The (4) wires from the outside main disconnect sounds right, not sure why the ground wire is unconnected ( or actually the Bonding Conductor ) should be connected within the remote distribution panel ( indoor one ) and the Neutral and Grounding buss bars should be separated and the NEUTRAL one isolated.

If the EGC for that remote distribution panel is not connected then it should be written up as missing the connection to the terminal bar.

Now as for the " bare copper wire" going up into the attic from the inside distribution panel.....could simply be for bonding as the GEC should take place at the FIRST disconnection means, meter enclosure or grounded conductor at the mast head.......

Could simply be someone bonding a pipe and so on in the attic location..are you able to view the attic location above the panel area.



Paul W. Abernathy
Reply With Quote
  #6  
Old 1/28/07, 12:47 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

Thanks Paul. I think I figured out what to say.
Reply With Quote
  #7  
Old 1/28/07, 1:05 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

How about...

Upon inspection I noticed your EGC that runs from your main disconnection means to your remote distribution panel was disconnected and should be re-connected and evaluated by a licensed electrical contractor.



Paul W. Abernathy
Reply With Quote
  #8  
Old 1/28/07, 1:09 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

That sounds better than I had. Thanks.

Should I say anything about the bare copper wire going up into the attic?

I thought EGC stood for Earth Grounding Conductor
Reply With Quote
  #9  
Old 1/28/07, 1:13 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

lol......yeah well don't get me STARTED on the NEC and how I think it is written backwards for the most part.

Nope...EGC stands for " Equipment Grounding Conductor " but it should be written as EBC- Equipment Bonding Conductor if I had my way...lol

Is their a EGC located at the Disconnect OUTSIDE or at the Meter Enclosure?



Paul W. Abernathy
Reply With Quote
  #10  
Old 1/28/07, 1:45 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

Forgot to look.............I'm so ashamed.....
Reply With Quote
  #11  
Old 1/28/07, 1:52 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

Then I would not worry about it.......just go with the statement on the EGC being loose and chalk it up to a learning experience. Life is short...relax and party on...



Paul W. Abernathy
Reply With Quote
  #12  
Old 1/28/07, 1:58 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

Hey Paul, I posted something in HVAC and am not getting any bites. Can you look?
Reply With Quote
  #13  
Old 1/28/07, 9:01 AM
rking4 rking4 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Williamstown, NJ
Posts: 8
Default Re: Help quick, writing report

I know thus is going to sound strange, but my father in-law looked at the post and he is an old retired master electrician and he told me that in some high risk areas of lightning strikes they would attach the grounding line to the bonding system of the electrical. So... he could be off his rocker or there might be some validity to it, but this is the first time I have ever heard of this. It was also a tip that you are in Florida.
Reply With Quote
  #14  
Old 1/28/07, 11:31 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Help quick, writing report

Richard,

I think what your father in law is saying is that they bond the Lightning Protection System to the existing GEC and GES which is correct and should be done. It is not always done but SHOULD be done.

The issue is this can happen BUT it needs to be bonded to the GEC or GES at the actual GEC or GES itself and usually not at the remote distribution panel location....but again it could be possible.

We would have to assume IF their was a lightning system in place but we don't know that based on the post itself.

Lightning is a major concern in Florida, This could be the case but is really beyond your scope and assuming makes it worse than just not knowing and defering.

Wesley....did you see AIR TERMINALS on the roof of the dwelling when you walked on it....?



Paul W. Abernathy
Reply With Quote
  #15  
Old 1/28/07, 3:05 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help quick, writing report

Quote:
Originally Posted by pabernathy
Wesley....did you see AIR TERMINALS on the roof of the dwelling when you walked on it....?
Nope. It was a condo and the HOA handles roof. Not inspected per contract.

I don't do two story anyway. Took a fall back in 79 while installing rain gutter, broke nine bones. Aluminum extension ladder up 28', pin for swivel foot came out and I rode it down. Landed on concrete standing up and ladder crushed tops of my feet. Fell over and broke wrist when I hit A/C unit. Casts on both legs to the knees for six months. Seriously put a damper on my barhopping days.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Report writing by others........ bkelly1 General Inspection Discussion 66 5/23/07 4:26 AM