http://education.nachi.org/show.php?course_id=53
Post corrections and comments here please. Course developed by member Russ Meyers. Thanks Russ! Nick Gromicko, CMI Founder World's biggest, best inspection association "Planet InterNACHI... resistance is futile" |
| Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
All contributors will be recognized on the last page of the course. Please help.
Nick Gromicko, CMI Founder World's biggest, best inspection association "Planet InterNACHI... resistance is futile" |
|
#3
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Could you make it available with out all that resigning up?
I signed up but I still can't get to anything Last edited by Mike Whitt; 10/11/08 at 11:01 AM. |
|
#4
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Can't get past the first page on anything there. Have tried several times and just can't get there. Would be glad to help but I just can't seem to figure out how to see it Have been working for more time than it would take to take the test just trying to see it Would be glad to take a look but there don't seem to be a way for me to access it Have I made my point clear that I can't see it? I don't think that I would pay a fee just to help someone on a problem but if you can make it possible for me to see it I will gladly make my comments good and bad Last edited by Mike Whitt; 10/11/08 at 11:35 AM. Reason: To make a point |
|
#5
|
||||
|
||||
|
Quote:
as a non-member you cannot access beyond the first page Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#6
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I will be glad to add my two cents and share my knowledge with the Home Inspectors as long as it doesn't cost me anything. Being that I only work part time and the banks are failing my income is very limited and I am starving to death. I have taken to eating road kill in order to survive and not die from starvation. The last time I counted my life savings it took me almost an hour to count my money. I put the pennies in one pile and the nickels in another, didn’t have any dimes and quarters as I had already used all of them to pay the light bill. I have taken to driving my car down hill all the time as I can’t afford to buy gas for it. The wife is getting tired of pushing back up the hill for our next trip?????? Seriously, I would be glad to proof it item in question as long as I don’t have to pay an annual due in order to do so. Is that asking too much? |
|
#7
|
||||
|
||||
|
I thought we already had one done by Gerry a long time ago and I assisted him on it.
Paul W. Abernathy,CMI,CEI,CEPE ICC, DCHD & IAEI Certified Electrical Inspector & Plans Examiner Some Must Reads - http://mssparky.com/2008/09/kbrs-tom...o-what-a-team/ http://www.terrylove.com/forums/show...4&postcount=33 http://www.nachi.org/bbsystem/viewtopic.php?t=17083 |
|
#8
|
||||
|
||||
|
Statement made in the presentation:
Armored cable must be supported by a strap or staple every 6 feet and within 24 inches of every switch or junction box, except for concealed runs in old work where it is impossible to mount straps. Corrections you need to make : (B) Securing. Unless otherwise provided, Type AC cable shall be secured within 300 mm (12 in.) of every outletbox, junction box, cabinet, or fitting and at intervals not exceeding 1.4 m (4 1/2 ft) where installed on or across framing members. (C) Supporting. Unless otherwise provided, Type AC cable shall be supported at intervals not exceeding 1.4 m (41.2 ft). Horizontal runs of Type AC cable installed in wooden or metal framing members or similar supporting means shall be considered supported where such support does not exceed 1.4-m (41.2-ft) intervals. Note : MC Cable is the cable allowed to be supported very 6' (B) Securing. Unless otherwise provided, cables shall be securedat intervals not exceeding 1.8 m (6 ft). Cables containing four or fewer conductors sized no larger than 10 AWG shall be secured within 300 mm (12 in.) of every box, cabinet, fitting, or other cable termination. (C) Supporting. Unless otherwise provided, cables shall be supported at intervals not exceeding 1.8-m (6-ft) Horizontal runs of Type MC cable installed in wooden or metal framing members or similar supporting means shall be considered supported and secured where such support does not exceed 1.8-m (6-ft) intervals. On the part with Ekectric Circuits....it might be better serves to explain it a little differently.. "Section 220-3b of the code requires two small appliance circuits to serve only appliance outlets in the kitchen, laundry, pantry, family room, dining room, and breakfast room. Both circuits must be extended to the kitchen and serve the counter top areas; either one or both of these circuits may serve the other rooms. No lighting outlets may be connected to these circuits, and they must be wired with 12-gauge wire and protected by a 20-ampere over-current device. Each circuit will have a capacity of 20 x 115 (2,300 watts). This is not too much when you consider that toasters often require more than 1,600 watts." My suggestions are in RED, and your other info gets the point accross..again it is not for electricians who should already know this info so it is good to keep it brief and to the point. Under the grounded outlet statement it reads: If the conventional two-opening outlet is used, it may be grounded if the screw that holds the outlet cover plate is electrically connected to the third-wire ground. The tester should light when one lead is in contact with a clean paint-free metal outlet cover plate screw and the hot side of the outlet. If the tester does not light, the outlet is not grounded. If a two-opening outlet is grounded, it may be adapted for use by a three-wire appliance by using an adapter. The loose-wire portion or screw tab of the adapter should be secured behind the metal screw of the outlet plate cover. Many appliances, such as electric shavers and some new hand tools, are double insulated and are safe without having a third ground wire. Green Comments : If the receptalce is a 2 wire system chances are the center screw that holds the cover is not going to be grounded.....be careful someone does not do a bootleg to fool you on this....I am not sure I would actually make that statement.. Blue: The adapters with the wire form them are not approved anymore I will give more suggestions, I just sold my Bike and I have to run to DMV with the guy......have fun guys Paul W. Abernathy,CMI,CEI,CEPE ICC, DCHD & IAEI Certified Electrical Inspector & Plans Examiner Some Must Reads - http://mssparky.com/2008/09/kbrs-tom...o-what-a-team/ http://www.terrylove.com/forums/show...4&postcount=33 http://www.nachi.org/bbsystem/viewtopic.php?t=17083 Last edited by pabernathy; 10/11/08 at 2:02 PM. |
|
#9
|
||||
|
||||
|
Thanks Paul!
Nick Gromicko, CMI Founder World's biggest, best inspection association "Planet InterNACHI... resistance is futile" |
|
#10
|
||||
|
||||
|
Quote:
I just took this exam again and feel I have taken it 3 times. Remember, I am a Carpenter by trade and know enough about electrical to be dangerous. ha. ha. Anyways, I got a 91 this time. It is unfortunate that we do not get to see which ones we got wrong. Same mistakes probably happen again and again because of that. Few questions popped up while taking the exam. Since when are the amount of 15 amp circuits determined or related to square footage. I have always been told that a 15 amp circuit had 8 receptacles max. and 20amp circuit could have 11. Paul, could you elaborate on this? I also notice armored cable was called BX. Wasn't that the original armored cable that we use to use that was also called Greenfield.? I thought in today's world it was called MC. Correct me please. Hot wires are never white was stated. Am I wrong in my thinking that sometimes it could be and painted black. Now these are items I notice in the Field of Construction, so any interpetation of the right way or how it should be would be helpful to me. Paul, thanks for reviewing this with all of us. I am sure we will all learn something out of this whole thing. Your contributions are very well appreciated. Thank you. Marcel Cyr Home Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards mcyrhammer@verizon.net Commercial Builder Ouellet Associaties Inc. www.oaconstruction.com |
|
#11
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Got this in an email from a student, “Mike why are you being so rude to Nick as he was only asking for help”
If this student though that I was being rude to Nick there is probably several others out there that think the same way so I feel as though I should address this now before it gets out of hand. It was my full intention to be funny. Yes I agree that I do have a sick sense of humor as can been seen here. Quote:
I also thought that this would put a grin on someone face as we all know no one is going to pay a utility bill using dimes and quarters unless they use a wheelbarrow to roll them in with. Quote:
So please, should anyone find my post offensive just try and look at the one making the post. I promise I was only trying to be funny. |
|
#12
|
||||
|
||||
|
Marcel, Here is your question : Since when are the amount of 15 amp circuits determined or related to square footage. I have always been told that a 15 amp circuit had 8 receptacles max. and 20amp circuit could have 11. Paul, could you elaborate on this? My Answer: Nothing in the NEC actually tells us how many receptacles we can place on a circuit as it applies to residential applications. We do have statements that direct us to evenly proportions of branch circuit layouts and so on but dirrectly we do not. Many people confuse the 90vA per receptacle required on commerical calculatiosn for receptacles but it does not really apply to residential applications. Now what you have to look at is this......how many luminaires are you also putting on the circuit along with those receptacles.....would be poor design if you had say 12-13 amps of known lighting loads on a circuit and then put a crude load of receptacles on it also.....so it is all a design thing but again the NEC does not tell us how many per circuit in residential applications...but common sense does. Your other question was : Wasn't that the original armored cable that we use to use that was also called Greenfield.? I thought in today's world it was called MC. Correct me please. Ok...we have both MC and AC in todays world.....as well as MCAP as well as Hospital Grade MC......and so on. MC Cable has a Equipment Ground ran with the conductors and AC Cable uses the outer case as the equipment ground |