... of which there are only a couple in a home when compared to the load total.
|
|
#47
|
|||
|
|||
|
Quote:
Once again you have me confused. Nick asks that this be commented on and post here in this thread. I thought that he wanted this for continuing education for Home Inspectors. Are you saying this is something that is going to be used for training material in Iraq? |
|
#48
|
|||
|
|||
|
We both know that a lot of the material contained within is completly wrong don't we
|
|
#49
|
||||
|
||||
|
Please Note:
jbushart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Wrong....according to....?
|
|
#50
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I think the main objection is to the material being referred to as new or possibly unique to NACHI, and the requisite baiting of electricians to review it, where a membership would be required to do so. From a business standpoint, it was worth a try. Otherwise, it had the appearance of a low class ploy to the thinking man.
Last edited by Marc D. Shunk; 10/12/08 at 11:19 AM. |
|
#51
|
|||
|
|||
|
250.4(A)(5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path. How about the NEC saying that some of the material covered in the text is absolutely incorrect! The one thing that I have learned about this site is the inability of some to learn. They seem to be stuck is the yesteryear and refuse to budge. There is a misconception that grounding or connecting to earth some how makes an electrical system safe. This is far from the truth. Bonding at the service is what makes an electrical system safe. The ground rod, water pipe, concrete encased electrode and the other five electrodes in no way makes the system safe, it only protects from; 250.4 General Requirements for Grounding and Bonding. The following general requirements identify what grounding and bonding of electrical systems are required to accomplish. The prescriptive methods contained in Article 250 shall be followed to comply with the performance requirements of this section. (A) Grounded Systems. (1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation. It is the bonding of the equipment grounding conductors, service enclosure and grounding electrodes back to the source that protects equipment and personal from current flow; 250.4(A)(5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the ELECTRICAL SUPPLY SOURCE.The earth shall not be considered as an effective ground-fault current path. According to the NEC it is incorrect. Then we have math that we can always fall back on. Ohm’s Law is a math equation and will prove that the earth is not a conductor for lower voltages such as 120/240. |
|
#52
|
|||
|
|||
|
Because it was Nick that ask and not the real authors. Are you saying the material is correct?
|
|
#53
|
||||
|
||||
|
Please Note:
jbushart is a non-member guest and is in no way affiliated with InterNACHI or its members.
I know that electricians limit themselves to this source, but I hope in reviewing HI courses you will take into consideration that the NEC is not the only code out there AND that home inspectors, unlike electricians, are not handcuffed by it.
Because the NEC is silent on certain things...Home Inspectors need not be. Additionally, we will use recent reports published by various agencies as references for conditions that we may feel to be unsafe...that are perfectly fine with NEC (purple wire nut copper pigtails to aluminum conductors comes to mind). Wrong, according to the NEC, is not necessarily wrong for our purposes. |
|
#54
|
|||
|
|||
|
Quote:
Quote:
I think that I understand fully. I also understand both through real life experiences and through post made here on this forum that a lot of the information used by Home Inspectors are so far outdated that Noah wouldn’t use them when he built his boat. I also understand that when a Home Inspector makes a call on something that is neither a code violation nor unsafe just because he is making the call based on wrong information given him is a class he took it hurts not only him but the organization as a whole. Both through life experiences and post I have read on this forum there is a big misunderstanding when it comes to grounding. This misunderstanding comes from material such as Nick has asked the electricians to comment on in this thread. In the material that Nick is asking about the comment is made in two separate places that grounding is to prevent someone from being electrocuted. Grounding will in no way stop anyone from being electrocuted. Bonding will be what protects the person from being hurt. In the material that Nick is asking about the author makes the statement that the ground rod carries current all the way back to the utility generator. This simply is not true. There is no connection at all between the grounding electrode system at a building and the utility generator. It is not my intent of preach code but to ensure that the material in some sort of way is at least partly correct. One fact that the author of the material point out and I do not dispute is that a complete path from one side of the source to the other must be in tack in order for current to flow. From the secondary of the pole transformer current can not return to the utility generator as there is no connection from the generator and the secondary of the transformer. Any current that might flow on the grounding electrode of the building will have to return to the secondary of the transformer and can go to no other place. Just the first few pages of what I have read lead me to believe that the original author has complied a bunch of material from several different places and from different time frames and is calling it modern material. The diagrams he uses shows this material is more than a few years old. For the most part he has done a fairly good job but the grounding parts are far from being correct. Anyone trying to use this material for grounding will end up getting someone hurt of even killed. It is old material and completely out of date. |
|
#55
|
|||
|
|||
|
Quote:
Well Joe as a member of this forum please enlighten me. Just what do I not understand? Please explain it to me and be sure to do it in a way that this lowly hillbilly can understand. I don’t feel that I am wasting my time any time that I try to explain electrical theory to anyone who don’t have a full understanding. If you think that I am wasting your time there is a simple solution, don’t read them. Once again I ask you if you agree with the material that Nick has ask the electricians to look over? Do you agree with the grounding aspects as outlined by the original author? |
|
#56
|
|||
|
|||
|
Quote:
Why are you avoiding answering my questions?????? Are they two hard to answer??????? Do you not know the answer???? Why do you keep asking for me to contact these people when it was Nick that asked me to take a look at the material and post anything I found that I disagreed with????? Will you Please answer my questions???? Well Joe as a member of this forum please enlighten me. Just what do I not understand? Please explain it to me and be sure to do it in a way that this lowly hillbilly can understand. I don’t feel that I am wasting my time any time that I try to explain electrical theory to anyone who don’t have a full understanding. If you think that I am wasting your time there is a simple solution, don’t read them. Once again I ask you if you agree with the material that Nick has ask the electricians to look over? Do you agree with the grounding aspects as outlined by the original author? Respectively Mike Edited to add: Oh and by the way Joe what you have posted above is not what Nick asded to have us look at now is it? Isn't what Nick asked us to look at a condensed version with a couple of changes to the language? Isn't what Nick asked us to look at accessible from this site? Last edited by jwhitt; 10/12/08 at 6:38 PM. |
|
#57
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
I will like to help ya with this.,, However ,.. Unforteally I only can get into first page but for the rest there is not much I can do due I am not a member of this orgazation.
Nick., If you can find a way to tempory bypass this so I can able read the rest if that ok with you ? Merci,Marc |
|
#58
|
|||
|
|||
|
Quote:
The earth, by virtue of the moisture contained within the soil, serves as a very effective conductor. Therefore, in power transmission, instead of having both the hot and neutral wires carried by the transmission poles, one lead of the generator is connected to the ground, which serves as a conductor. All electrical utility wires are carried by the transmission towers and are considered hot or charged. At the house, or point where the electricity is to be used, the circuit is completed by another connection to the ground. The electric power utility provides a ground somewhere in its local distribution system; therefore, there is a ground wire in addition to the hot wires within the service drop. In FIGURE 11.1, this ground can be seen at the power pole that contains the step-down transformer. In addition to the ground connection provided by the electric utility, every building is required to have an independent ground, called a system ground. The system ground is a connection to ground from one of the current-carrying conductors of the electrical system. System grounding, applied to limit overvoltages in the event of a fault, provides personnel safety, provides a positive means of detecting and isolating ground faults, and improves service reliability. Therefore, the system ground’s main purpose is to protect the electrical system itself –it offers limited protection to the user. The system ground serves the same purpose as the power company’s ground. However, it has a lower resistance because it is closer to the building. The equipment ground protects people from potential harm during the |