Question Holiday Lighting question

I see this everywhere this time of the season.

Houses, buildings COVERED in lights. I mean every square foot has a light in it, yard, house, roof, window....

The Mfg's, IBEW and associations warn no more then three strings per installation on one Receptacle.. I don't see this being the case or possible with some of these displays..

So

What do the electrical pro's have to point out or say about these "festive" lighting displays?

Dangerous, potentially dangerous, Exceeding the limits of safety, Pushing equipment ratings? That house is a "toaster"?

What is on your place? I use candles....

Paul
Greg
Speedy
Reply With Quote
  #2  
Old 12/28/06, 12:46 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: Holiday Lighting question

I've been wondering too, how they manage to use so many strings unless folks are using quite a few extension cords also.
I had put 6 strings of those "icycle" lights on my home, all joined together off one extension cord, and when I went to turn them on for testing, found that they wouldn't stay lit for more than 5 minutes before going out!
The mini-fuses in the plug ends were blowing...
After a little troubleshooting, and after the 3rd time of this happening,
and me finally splitting the length down to 3 strings, and another extension cord,
they stayed lit...










Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #3  
Old 12/28/06, 12:51 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

lol....well I don't get real LIGHTY with my house....too lazy to put them up as I know they have to come down...

What I do hope is when they are putting up these lights they are running them from a GFCI protected receptacle.

Now it probably applies to 527.3 but again they will probably not be up longer than 90 days under that section anyway.

I get more concerned with HOW they run the wiring....through windows, up walls and so on......are they subject to damage that could possibly cause a fire.....who knows.

If the manufacture says not more than 3 per receptacle...well the manufacturer has the final say on that....but we know most dont read the instructions anyway........so to me you wont stop them....but as long as it is protected by the OCPD...and if possible on GFCI then they are about as protected as they could be.

What problem I do have is leaving it up all year long......that to me would violate 527.3(D) and also exceed the time restraints on the allowance.

I am sure others will have their own opinions as well...these are just mine.

Forgot to add - My wife started pulling down the lights the day after...she was more than ready to put them away..lol



Paul W. Abernathy

Last edited by pabernathy; 12/29/06 at 9:14 AM..
Reply With Quote
  #4  
Old 12/29/06, 12:18 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Holiday Lighting question

The NEC really seems to go on vacation in December. That is why they started putting fuses in the plugs. I suppose a lot of them got wrapped in aluminum foil.
I don't worry too much about the building wiring if it is properly protected (240.4(D)) but the things that happen on the load side of the receptacle can get pretty scary. As a general rule, splitting the load up across a lot of extension cords is better than that one glowing cord I see. At least the little animals have a place to get warm..
I made up repeater boxes for my wife so I can still have one point of control and use a couple circuits. It is an aluminum FS box with an SSR in it and a receptacle and a long SJOW cord. There is also a long low voltage wire that goes to a wall wart. Plug the wall wart into the main light circuit and the power to another one. That way when the main lights come on, the SSR makes and the load from another circuit is switched on. I have one dedicated 20 on a timer for lights, the rest go into other circuits. It also lets me go pretty far from the main light circuit without stringing extension cords, just a low voltage wire.
Reply With Quote
  #5  
Old 12/30/06, 9:47 AM
mcotten mcotten is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Hoffman Estates, IL
Posts: 19
Default Re: Holiday Lighting question

I was talking to a gut that put up more than 15,000 lights. I asked him how he gets the strands so long. He said that he replaces the fuses in the lights with a cut off nails. He said he can put as many stands of lights together as he can. He did say he had a subpanel installed with 10 20 amp circuits for his Christmas lights.

Michael Cotten
Cornerstone Home Inspections Inc



Michael Cotten
Cornerstone Home Inspections Inc
www.cornerstonehomeinspect.net
cornerstone235@aol.com
Reply With Quote
  #6  
Old 12/30/06, 1:52 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

Michael...Now that is just frightening........alas what people will do to be festive...lol



Paul W. Abernathy
Reply With Quote
  #7  
Old 12/30/06, 2:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Holiday Lighting question

We don't need no stink'n fuses.

I wonder if his fire insurance policy will pay up after it's discovered he removed the fusing?
Reply With Quote
  #8  
Old 12/30/06, 2:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

There ya go....we need to talk the insurance associations into allowing us HI's to do holiday inspections for this very issue.....get on it NICK.....make it so # 1



Paul W. Abernathy
Reply With Quote
  #9  
Old 12/30/06, 3:08 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Holiday Lighting question

Holiday lighting in a public area in violation of NEC 210.8(B):


Reply With Quote
  #10  
Old 12/30/06, 3:53 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

Marc,

Most Excellent example of the upgrade/addition from the 2002 NEC to the 2005 NEC for Sec 210.8(B)(4).


Quote:
(4) Outdoors in public spaces—for the purpose of this section
a public space is defined as any space that is for
use by, or is accessible to, the public
May I use those images in one of my presentations I give on 2002 to 2005 NEC Changes/Updates.

If you wish me not to I totally understand.




Paul W. Abernathy
Reply With Quote
  #11  
Old 12/30/06, 4:03 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Holiday Lighting question

Quote:
Originally Posted by mcotten
I was talking to a gut that put up more than 15,000 lights. I asked him how he gets the strands so long. He said that he replaces the fuses in the lights with a cut off nails. He said he can put as many stands of lights together as he can. He did say he had a subpanel installed with 10 20 amp circuits for his Christmas lights.

Michael Cotten
Cornerstone Home Inspections Inc
I watched a program durring the holidays that highlighted several homes in Richmond, VA and their holiday displays. One guy bragged about doing this in order to achieve his displays (replacing light strand fuses with snipped nail shanks). I watched in disbelief but became even more concerned when the program, station, and narrator did nothing to condone this practice or even advise about the safety hazards and ramifications.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #12  
Old 12/30/06, 4:09 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

I think an argument could also be made in the lower picture that it violated 406.8(B) as well.

We can only hope they have GFCI ahead of that protecting the entire setup....chances are they dont sad to say.



Paul W. Abernathy
Reply With Quote
  #13  
Old 12/30/06, 4:14 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Holiday Lighting question

http://lindsaylights.com/



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #14  
Old 12/30/06, 4:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Holiday Lighting question

Joseph,

That is amazing...as the house seems to typical in size. I see that the guy boosts that he consumes 44,000 watts of power.

I simply would like to see his houses electrical setup....does not take an OHMS law wizard to know what he is pulling in AMPS.

But I see they got it down to 30,000 watts recently....thanks to LED's they said......amazing.



Paul W. Abernathy
Reply With Quote
  #15  
Old 12/30/06, 4:22 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Holiday Lighting question

My wife has family in Thornhill, Ontario.

They live a few blocks away from this home.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Interesting Question? jmckenna1 Miscellaneous Discussion for Inspectors 9 11/25/07 1:13 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM