Default Home Inspector Electrical Report



The Bonding Jumper is missing. It is supposed to be installed to bond the water pipes when the water meter is removed for repair or replacement to protect the water company personnel from an electric shock hazard.




Last edited by jtedesco1; 1/18/08 at 8:40 AM..
Reply With Quote
  #2  
Old 1/18/08, 7:53 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Home Inspector Electrical Report

Quote:
Originally Posted by jtedesco1
Please send me one of your worst electrical defects so that I can include it in my new NACHI book, pictures will be helpful.


joetedesco@comcast.net

The Bonding Jumper is missing. It is supposed to be installed to bond the water pipes when the water meter is removed for repair or replacement to protect the water company personnel from an electric shock hazard.


What if the grounding wire clamp is: (1) on copper tubing, (2) on the street side of the meter and (3) on the street side of the house water shut-off? Does it still need a bonding jumper then?
Reply With Quote
  #3  
Old 1/18/08, 8:02 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Home Inspector Electrical Report

Could it be installed up high out of the scope of the picture?

Could the Grounding Electrode Conductor be installed at the point of entry and the interior pipe then be bonded elsewhere in the building to satisfy 250.104?

In this picture say that the 250.52(A)(1) GEC was already installed at the point of entry of the building could not the 250,104 bond be installed as pictured?

In other words the bonding jumper is not necessarily required to be right there at the meter.

Reply With Quote
  #4  
Old 1/18/08, 8:10 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Home Inspector Electrical Report

Quote:
Originally Posted by Brian A. MacNeish
What if the grounding wire clamp is: (1) on copper tubing, (2) on the street side of the meter and (3) on the street side of the house water shut-off? Does it still need a bonding jumper then?
Effective Grounding Path The connection of a grounding electrode conductor or bonding jumper to a grounding electrode must be made in a manner that will ensure a permanent and effective grounding path. Where necessary to ensure the grounding path for a metal piping system used as a grounding electrode, effective bonding must be provided around insulated joints and around any equipment likely to be disconnected for repairs or replacement. Bonding conductors shall be of sufficient length to permit removal of such equipment while retaining the integrity of the bond.

Examples of equipment likely to be disconnected for repairs or replacement are water meters and water filter systems.
Reply With Quote
  #5  
Old 1/18/08, 8:20 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: Home Inspector Electrical Report

Is it really required to protect water company personnel in the event they remove the meter, or is it installed to help ensure that the metallic piping throughoput the structure is grounded , regardless of presence of the weater meter, in the event that thie piping should somehow become energized.
Reply With Quote
  #6  
Old 1/18/08, 8:25 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Home Inspector Electrical Report

Quote:
Originally Posted by jfarsetta
Is it really required to protect water company personnel in the event they remove the meter, or is it installed to help ensure that the metallic piping throughoput the structure is grounded , regardless of presence of the weater meter, in the event that thie piping should somehow become energized.
Joe, the substantiation for this requirement included the scenario described.

Also the bonding jumper will be required around unions, etc., too when the GEC is connected to a water pipe on the load side of the water meter.

Last edited by jtedesco1; 1/18/08 at 8:43 AM..
Reply With Quote
  #7  
Old 1/18/08, 12:48 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,216
Default Re: Home Inspector Electrical Report

I have met several (4 or 5) plumbers on home inspections that have said that they received an electrical shock when removing a water meter. They did this because 1) a bonding jumper was not installed over the meter, and 2) they worked too hastily without thinking of the need for one. I understand the exceptions to the rule (code) as Mike points out. But for me personally, I recommend a bonding jumper to be installed in a manner stated by Joe Tedesco on every water meter that I inspect. Every one. Sounds silly, right?

Someone once told me that my recommendation for a water jumper around the meter was not necessary. And I replied, "Well, did you write your recommendation down on paper and sign it - just as we home inspectors have to in our inspection reports? And write also that you will guarantee that no one will ever get hurt because of the absent jumper at the meter that you suggest is OK today." No plumber ever did take that responsibility.

It's one thing to quote code; it's another thing to take responsibility.




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
  #8  
Old 1/18/08, 1:07 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Home Inspector Electrical Report

Ben

Let’s think about this for just a minute. If an interior metal water pipe is bonded from any point on that pipe back to the panel would not the metal of the water pipe conduct any current imposed on it to the bonding jumper?

If the bonding jumper on an interior metal water pipe is bonded from the nearest point from the water meter or filter back to the grounding electrode wouldn’t the metal of the pipe carry any current imposed on it from the end of the pipe back to the bonding jumper?

The bonding jumper that goes across the meter is doing nothing more than bonding the interior metal pipe to the grounding electrode as the metal water pipe that is in contact with earth is just that, a grounding electrode.

There is no more danger in someone getting shocked from one than the other. This has nothing to do with code requirements but on the simple principles of electricity.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Scumbag NAHI hits new low at ASTM meeting yesterd cmccann General Inspection Discussion 25 2/22/07 4:31 PM
Home Inspector Listings Part Two jbowman Misc. Discussion 8 8/29/06 9:52 PM


All times are GMT -4. The time now is 12:18 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts