  #1  
Old 6/2/10, 8:33 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Horizontal Receptacle

Hey Guys-

What are the requirements for a horizontal receptacle located above the floor, like on a fireplace or in a window seal? Thanks.

Kenny
Attached Thumbnails
horizontal-receptacle-img_9929.jpg   horizontal-receptacle-img_9931.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/2/10, 10:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Horizontal Receptacle

If anyone sets a drink up there during a party, liquid could easily enter the outlet. It's a bad idea in my view and I'd probably recommend relocating it to a wall.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 6/2/10, 11:11 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Horizontal Receptacle

Quote:
Originally Posted by krigler View Post
Hey Guys-

What are the requirements for a horizontal receptacle located above the floor, like on a fireplace or in a window seal? Thanks.

Kenny
There are no "Requirements".
Reply With Quote
  #4  
Old 6/2/10, 4:14 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Horizontal Receptacle

They are permitted to be face up in locations other than dwelling counter-tops. Floor receptacles are permitted face up too but require a listed box.

Quote:
406.4 Receptacle Mounting.
(E) Receptacles in Countertops and Similar Work Surfaces in Dwelling Units. Receptacles shall not be installed in a face-up position in countertops or similar work surfaces.
Quote:
314.27 Outlet Boxes.
(C) Floor Boxes. Boxes listed specifically for this application shall be used for receptacles located in the floor.
Reply With Quote
  #5  
Old 6/2/10, 5:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Horizontal Receptacle

Fireplace mantel is not a code authorized location to set your drink!

Call that one out!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 6/2/10, 6:26 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Horizontal Receptacle

Quote:
Originally Posted by jfunderburk View Post
If anyone sets a drink up there during a party (What if they set a drink there and there isn't any party?)
, liquid could easily enter the outlet. It's a bad idea in my view and I'd probably recommend relocating it to a wall.
I usually do recommend that, but nobody ever pays any attention to me.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 6/2/10, 6:43 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Horizontal Receptacle

Quote:
Originally Posted by dandersen View Post
Fireplace mantel is not a code authorized location to set your drink!

Call that one out!
Unless your grilling a pig.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #8  
Old 6/2/10, 6:45 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Horizontal Receptacle

Quote:
Originally Posted by jwilliams4 View Post
I usually do recommend that, but nobody ever pays any attention to me.
Jae,
Just curious why you would recommend moving it to the wall? When you find these receptacles do they seem like they've been a problem?
Reply With Quote
  #9  
Old 6/2/10, 6:59 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Horizontal Receptacle

Wayne, we do that outdoors over here!

We do loose a lot of beers because we don't have adequate place to put the drink though!!!

Come to think of it, Your right! Move those darn outlets!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 6/2/10, 8:08 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Horizontal Receptacle

Quote:
Originally Posted by dandersen View Post
Wayne, we do that outdoors over here!

We do loose a lot of beers because we don't have adequate place to put the drink though!!!

Come to think of it, Your right! Move those darn outlets!
Or replace them with proper ones...

http://www.lewelectric.com/PDF%20fil...%20Catalog.pdf



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #11  
Old 6/3/10, 8:45 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Horizontal Receptacle

Quote:
Originally Posted by Robert Meier View Post
They are permitted to be face up in locations other than dwelling counter-tops. Floor receptacles are permitted face up too but require a listed box.
Thanks Robert. I wanted to make sure the above the floor face-up receptacles didn't have the same requirements as the floor receptacles.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rusting on Flue with Long Horizontal Run krigler Inspecting HVAC Systems 4 4/15/10 12:37 AM
What would this receptacle outlet be used for? kluce Electrical Inspections 11 6/11/09 10:32 PM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 3:39 PM


All times are GMT -4. The time now is 8:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts