Default Horz. Receptacle?

This receptacle is mounted horizontally about 12” above the sink. I know it is not right but is it allowed?
Attached Thumbnails
horz-receptacle-2061-096.jpg  
Reply With Quote
  #2  
Old 10/20/06, 1:18 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Horz. Receptacle?

Receptacles can't be mounted face up on countertops. YMMV as to what we called this space.

406.4(E) Receptacles in Countertops and Similar Work Surfaces in Dwelling Units. Receptacles shall not be installed in a face-up position in countertops or similar work surfaces.

I would point out this could constitute a hazard if things stored in this space spilled.
Reply With Quote
  #3  
Old 10/20/06, 1:45 PM
DSuelflow DSuelflow is offline
New User
 
Join Date: Jan 2006
Location: Eden, NC
Posts: 25
Please Note: DSuelflow is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Horz. Receptacle?

I agree. Like I said, I knew it was wrong, thanks for the ref. to show it is not allowed.
Reply With Quote
  #4  
Old 10/20/06, 1:54 PM
kkenny's Avatar
kkenny kkenny is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Oak Forest, IL
Posts: 475
Default Re: Horz. Receptacle?

Quote:
Originally Posted by DSuelflow
I know it is not right but is it allowed?
The NEC is written vaguely enough that it allows for local electrical inspectors to make their own call. I've been in discussions on this MB before with electricians from different states and like opines, interpretations are like butts, everyone has one. In this case it comes down to 2 things:

1. what the local EI allows
and
2. what concerns you are going to report to YOUR client

I can see that you already have concerns and I agree w/ Greg

Quote:
Originally Posted by Greg Fretwell
I would point out this could constitute a hazard if things stored in this space spilled.
If I think it is a safety hazard, whether within "code" or not I inform my client and explain my concern.

Who knows some EI somewhere might concider that small shelf/sill a workspace.

Kevin



Kevin M. Kenny, Sr.
Kenny Home Inspections
Oak Forest, Illinois 60452
Nachi #6070990

http://kennyhomeinspections.com

Reply With Quote
  #5  
Old 10/21/06, 9:27 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Horz. Receptacle?

I would not say it is written well enough that a local AHJ can make a "unwise' call.....i work with them every day.....they are also still learning.

It is well known that in the dwelling many people install floor receptacles that are face up...but to be properly done they need to be the "proper" type of receptacle and if done correctly will be fine....

I agree that if this location is above the sink......it could be a rough call....if it is NOT being counted as part of the counter top space requirement ( 4' ) and (2' of the sink edge) then it may not be considered a countertop receptacle....BUT it can be considered similar space because of its location which would be a problem in my opinion.

Suggestion would be to replace the plug with a GFCI.....or better yet if already on the GFCI...replace with a floor receptacle cover as a normal floor model that is approved for the position.

Now....you would have problems IF this receptacle is over the sink....and is wired in with the countertop....because if it is NOT part of the counter then it SHOULD NOT be wired in with the counter.....but again who knows what year and when it was done....codes have changed...

Now....lol..if it is a bathroom...ignore what i said...thehehe....it should be on GFCI to begin with.....and It is a problem...can't you see a cup of denture water spilling on it.....ahhh.....the look into the future...oh well...anyway I would most certainly note it...and it could be replaced in the same manner as the other I stated.....

So....with that said....I would suggest it be protected by GFCI....and replace the receptacle with a single floor receptacle cover and inner housing that reduces the chance of anything getting into it......

key here is.....

1.) Is it wired in with the Kitchen CounterTop.....?
2.) Is it a Similar Space......?
3.) Since it is already their..how do we protect it....?
4.) Is it a Kitchen Sink or Bathroom Sink...lol

Answers........Read my post above the QUESTIONS...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 10/21/06 at 9:52 AM..
Reply With Quote
  #6  
Old 10/21/06, 9:55 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Horz. Receptacle?

lol....sorry for the kitchen space references....I never can miss a moment to add educational info...sorry....lol...I think the image is a bathroom...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microwave receptacle jwardenski Electrical Inspections 17 9/9/07 8:18 PM
What's This Receptacle For? cmettel Electrical Inspections 7 5/25/07 8:35 AM
Bedroom receptacle dnasser Electrical Inspections 9 4/16/07 11:33 AM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 4:39 PM
Wiring a Receptacle jallingham Electrical Inspections 9 8/6/06 5:34 PM


All times are GMT -4. The time now is 5:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts