Default hot legs 4/0, neutral leg 2/0 at main

The enclosure and diconnect were both rated at 200 amps. The hot conductors were 4/0 aluminum (200 amps) , the neutral conductor was 2/0 aluminum (150 amps). I know the rating of the disconnect shouldn't exceed the rating of the service entrance conductors, and this rule does include the neutral conductor too, right?

Also, this was a pretty clean-looking Square D box, but with no schematic showing where the bonding screw for the neutral bus bars should be. There is a grounding conductor bonding the neutral and grounding bus bars, is this how it's typically done? I expected to see a scew that would bond the box.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 1:39 AM..
Reply With Quote
  #2  
Old 6/14/07, 6:36 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: hot legs 4/0, neutral leg 2/0 at main

Kenton,

The reason the grounded entrance conductor can be smaller is because on 220 V circuits like a water heater or AC or Electric range the current does not flow back through the neutral as it is flowing from one hot leg to the other. It requires a bit of calculation but it is permited.

------------------------------------------

Size the Neutral Conductor: 220.22

310-15(B)(6) states that the neutral service and/or feeder conductor can be smaller than the ungrounded (hot) conductors, provided the requirements of 215.2, 220.22 and 230.42 are met. 250.24(B)(1) states that the neutral cannot be smaller than the required grounding electrode conductor specified in Table 250.66

------------------------------

SERVICE-ENTRANCE CONDUCTORS shall be copper or aluminum. Aluminum is not recommended. The minimum size "hot" conductors shall be # 6 except when the service is for any dwelling the minimum size shall be # 4. The consumer shall be responsible for determining whether larger conductors are required based upon load requirements. The NEUTRAL conductor shall be the same size as the "hot" conductors or a maximum of two standard size smaller. No conductor shall be smaller than # 6. The ampacity of all conductors shall be per the National Electrical Code. See the Conductor Chart for minimum size "hot" conductors. Each conductor shall extend a minimum of 36" out from the weatherhead.

Last edited by mlarson; 6/14/07 at 6:48 AM..
Reply With Quote
  #3  
Old 6/14/07, 7:13 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hot legs 4/0, neutral leg 2/0 at main

4/0, 4/0, 2/0 AL, or 2/0, 2/0, 1/0 CU, is absolutely typical service entrance cable.


No, there is no bond screw in that panel. The hole is empty. They compensated for this by using a #4cu from the neutral bar to the added ground bar. This is perfectly fine.
Actually it is a bit of wasted work. There was no reason for the added bars and no reason to separate the grounds and neutrals.
They probably did it for more space on the bars. Looking at it if they did not add a bar the factory neutral bars would have been full.
Reply With Quote
  #4  
Old 6/14/07, 8:03 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: hot legs 4/0, neutral leg 2/0 at main

Quote:
Originally Posted by Speedy Petey
4/0, 4/0, 2/0 AL, or 2/0, 2/0, 1/0 CU, is absolutely typical service entrance cable.
Yep...those are the sizes I use...



Paul W. Abernathy
Reply With Quote
  #5  
Old 6/14/07, 8:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hot legs 4/0, neutral leg 2/0 at main

That yellow stripe tells me that this is utility grade URD, which is not permitted inside the home. URD is not an NEC approved conductor. Some URD is dual rated as XHHW. XHHW is an NEC approved conductor type. The URD with the yellow strips is 99% of the time regular old underground URD, and is a violation as pictured.
Reply With Quote
  #6  
Old 6/14/07, 9:49 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hot legs 4/0, neutral leg 2/0 at main

Honestly Marc, I never knew that. That is all I can get around here and it is what everyone uses.
Reply With Quote
  #7  
Old 6/14/07, 11:09 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: hot legs 4/0, neutral leg 2/0 at main

Marc do you know why it is not allowed as far as what sort of problem that neutral might cause.
Reply With Quote
  #8  
Old 6/15/07, 4:55 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hot legs 4/0, neutral leg 2/0 at main

Quote:
Originally Posted by relliott
Marc do you know why it is not allowed as far as what sort of problem that neutral might cause.
The aluminium conductor is fine. The insulation is the problem. URD does not have an NEC compliant insulation type. URD will freely burn, for instance.
Reply With Quote
  #9  
Old 6/15/07, 7:38 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: hot legs 4/0, neutral leg 2/0 at main

I knew there had to be a reason, but was actualy thinking under ground would be tougher without considering that aspect,cool,thank you.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM
Main Electrical Shut-off? jpassailaigue General Inspection Discussion 10 3/24/06 2:19 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 3:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts