Default Hot neutral reverse

I found an outlet, that when tested showed as being a hot neutral reverse.
Then when I opened the panel I found a red wire connected to the neutral buss bar. Does that explain the outlet problem?
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/15/11, 11:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Hot neutral reverse

Quote:
Originally Posted by rdrangstveit View Post
I found an outlet, that when tested showed as being a hot neutral reverse.
Then when I opened the panel I found a red wire connected to the neutral buss bar. Does that explain the outlet problem?
Possibly, if the white wire was on the breaker. Not really important for you to figure out the reason why.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 12/15/11, 1:53 PM
Roy Drangstveit's Avatar
Roy Drangstveit Roy Drangstveit is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Prior Lake, MN
Posts: 149
Default Re: Hot neutral reverse

Here are a few pictures of that panel. There is a white wire on a breaker.Tell me if you see any more problemshot-neutral-reverse-picture-082.jpg

hot-neutral-reverse-picture-079.jpg

hot-neutral-reverse-picture-085.jpg

hot-neutral-reverse-picture-086.jpg
Reply With Quote
  #4  
Old 12/15/11, 5:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot neutral reverse

The white conductor appears to be part of a 2-wire circuit so it may not be the problem. You would need to inspect further to find the actual cause of the reverse. Removing the receptacle and looking would be the first thing I would do.
Reply With Quote
  #5  
Old 12/15/11, 8:12 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot neutral reverse

The white on the breaker is a hot from a 240 volt circuit.
Reply With Quote
  #6  
Old 12/17/11, 4:39 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Hot neutral reverse

There is only one way to test......





Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #7  
Old 12/18/11, 10:25 AM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Hot neutral reverse

Quote:
There is only one way to test......
I tried this but kept getting a weird buzzing feelinf in my body? Are you sure this works Steve?



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #8  
Old 12/18/11, 2:12 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Hot neutral reverse

Quote:
Originally Posted by jszczesny View Post
I tried this but kept getting a weird buzzing feelinf in my body? Are you sure this works Steve?
You have to lick the fork first....




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #9  
Old 12/18/11, 4:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Hot neutral reverse

Quote:
Originally Posted by sstanczyk View Post
You have to lick the fork first....
Shows how much you know. You have to insert the fork while holding it in your mouth...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 12/19/11, 10:32 AM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 734
Default Re: Hot neutral reverse

Quote:
Originally Posted by jpope View Post
Shows how much you know. You have to insert the fork while holding it in your mouth...
And using a plastic fork won't work as well either. I always recommend stainless steel.



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections
www.redfishinspections.com
Reply With Quote
  #11  
Old 12/19/11, 12:56 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Hot neutral reverse

Quote:
Originally Posted by wmisegades View Post
And using a plastic fork won't work as well either. I always recommend stainless steel.
Good tip.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 12/19/11, 1:26 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot neutral reverse

Quote:
Originally Posted by wmisegades View Post
And using a plastic fork won't work as well either. I always recommend stainless steel.

I recommend silver since it's the best conductor.
Reply With Quote
  #13  
Old 12/19/11, 1:47 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Hot neutral reverse

Quote:
Originally Posted by Robert Meier View Post
I recommend silver since it's the best conductor.
So those born with a silver spoon in their mouth must be plumbers?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/19/11, 4:32 PM
Aubrey J. Kahn Aubrey J. Kahn is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Kissimmee, Fl
Posts: 1,121
Default Re: Hot neutral reverse

Don't forget for best results be sure to stand in a 5gal bucket of water while testing.
Reply With Quote
  #15  
Old 12/20/11, 1:30 PM
Michael Ardai Michael Ardai is offline
New User
 
Join Date: Jan 2004
Posts: 4
Please Note: Michael Ardai is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot neutral reverse

Looks like there's a pair of thhn wires leaving the panel on the upper right. Not related to the reversed outlet, but still wrong...
/mike
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Reverse Osmosis phinsperger Plumbing Inspections 3 10/30/07 6:28 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 8:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts