Default Hot spot in panel

This panel has aluminum and copper wiring. No obvious deficiencies noted in the panel. Aside from the fridge and a few lights, nothing was drawing in the house. The breakers in question were listed as "lights and outlets". Comments?
Attached Thumbnails
hot-spot-panel-dc_0017.jpg   hot-spot-panel-ir_0016.jpg  
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/31/10, 8:44 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Hot spot in panel

29.1 deg. C is a nice day.

Did you measure the current through that breaker?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 3/31/10, 8:51 AM
Ralph A. Schade Ralph A. Schade is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Kitchener-Waterloo Ont
Posts: 43
Default Re: Hot spot in panel

No, I normally don't go as far as testing current. Typically, I don't get breakers heating up to 29.1C but it's the 41.7C that really concerns me.
Reply With Quote
  #4  
Old 3/31/10, 8:57 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Hot spot in panel

Ralph,

There is just not enough info to advise you. Sorry.

Could be a loose connection
Could be a loaded circuit.
could be perfectly normal.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 3/31/10, 10:18 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Hot spot in panel

In my experience, it is likely an abnormal condition that should be investigated. It appears that the connection to the bus may be loose causing a high(er) temp connection. It is not very common to see that much difference in temps n a panel, even if the circuit is loaded. You can't be wrong by calling it out - otherwise why bother with measuring the temps in the first p,ace?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 3/31/10, 10:21 AM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: Hot spot in panel

You are right to be concerned about the temp spread, that is alot for F nevermind C. The conductors' temp all appear normal and the heat appears to be highly centralized at the point where the breaker tabs connect to the bus bar. My guess would be that the tabs are bent, defromed, seperated, broken..I think you get my drift here.
Good luck
Reply With Quote
  #7  
Old 3/31/10, 5:20 PM
Ralph A. Schade Ralph A. Schade is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Kitchener-Waterloo Ont
Posts: 43
Default Re: Hot spot in panel

Thanks to all that responded. I recommended that a qualified electrician should correct the concern, to my clients. Then I told the agent to advise the vendors to have an electrician look at it asap. I called the vendors 2 days later to ask if the listing or buying agent had mentioned anything. Nada!
There was a host of issues noted, which I would not disclose. My clients had walked on the deal. However, I did feel that it was my moral obligation to notify them about the electrical issue. You'd think the agent would feel the same way, even if it was for a possible future deal with the vendors in their new home.
Reply With Quote
  #8  
Old 3/31/10, 5:27 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot spot in panel

Quote:
Originally Posted by rschade View Post
No, I normally don't go as far as testing current. Typically, I don't get breakers heating up to 29.1C but it's the 41.7C that really concerns me.

41.7° C is only 107° F. Is that really cause for alarm?
Reply With Quote
  #9  
Old 3/31/10, 10:10 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 732
Default Re: Hot spot in panel

Quote:
Originally Posted by rschade View Post
Thanks to all that responded. I recommended that a qualified electrician should correct the concern, to my clients. Then I told the agent to advise the vendors to have an electrician look at it asap. I called the vendors 2 days later to ask if the listing or buying agent had mentioned anything. Nada!
There was a host of issues noted, which I would not disclose. My clients had walked on the deal. However, I did feel that it was my moral obligation to notify them about the electrical issue. You'd think the agent would feel the same way, even if it was for a possible future deal with the vendors in their new home.
Sounds like the right thing to do,



Greensboro Home Inspection
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspection.html

Raleigh Home Inspection
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

BassRumors.com
Providing a blog, news, and forum dedicated to bass fishing.
Reply With Quote
  #10  
Old 3/31/10, 11:09 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Hot spot in panel

Looks like it's about 22C above ambient (put a spot on the background for ambient). Worthy of mention, evaluation, not to get excited over.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #11  
Old 4/1/10, 3:59 AM
Ralph A. Schade Ralph A. Schade is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Kitchener-Waterloo Ont
Posts: 43
Default Re: Hot spot in panel

Quote:
Originally Posted by Robert Meier View Post
41.7° C is only 107° F. Is that really cause for alarm?
Dunno, are you suggesting it's normal and may not get worse?
Reply With Quote
  #12  
Old 4/1/10, 4:45 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot spot in panel

Quote:
Originally Posted by rschade View Post
Dunno, are you suggesting it's normal and may not get worse?

I'm not sure. I was just asking for my own knowledge. I've touched dimmer switches that were hot during normal operation so I was wondering if a CB at this temperature was actually a potential problem or not.
Reply With Quote
  #13  
Old 4/1/10, 5:35 AM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot spot in panel

I recommend you obtain some standards as guidance when performing infrared inspections. Guessing don't cut it. You need guidelines.
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/1/10, 8:58 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Hot spot in panel

Quote:
Originally Posted by Robert Meier View Post
41.7° C is only 107° F. Is that really cause for alarm?
Not necessarily "alarm", but when that is the only breaker with elevated temp and the others in the panel are more like 65-70 F, it is abnormal. Something like dimmers have an "excuse" for being warm - standard breakers usually do not (exceptions are some GFCI and AFCI breakers).



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #15  
Old 4/1/10, 4:13 PM
Ralph A. Schade Ralph A. Schade is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Kitchener-Waterloo Ont
Posts: 43
Default Re: Hot spot in panel

Quote:
Originally Posted by ldapkus View Post
I recommend you obtain some standards as guidance when performing infrared inspections. Guessing don't cut it. You need guidelines.
Thanks Linus, I'm sure that the booklet may come in handy and would be an interesting read. However, I really don't do quantitative scans at this time and having scanned thousands of panels, this is definately an anomaly which should be addressed. No guessing about it. I think that a hot spot such as this, while there is no apparent draw, is an issue. Never mind putting a demand on the circuit! What stumped me is the fact that the wires and the breakers appeared to be secure. I plan on following up with the vendor and will let you all know what it was.
I want to thank everyone for their input and opinions because I think it helps us all along.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts