Okay this is a GFCI 60 amp hot tub circuit breaker. Why in the world is the ground and neutral wires screwed directly into the circuit breaker? The neutral goes from the breaker to the ground bar. The ground goes to the hot tub. Circuit breaker looks almost designed to be wired this way but I have never seen anything like this.
|
| Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The problem here could be that they ran a 2 wire UF cable and needed a 3-wire supply (not sure if any tubs require a 3-wire supply) to the tub so they used the bare EGC as a neutral. The GFCI CB requires a connection to the neutral bar to function so that's why you see the white conductor jumped over. If the tub only required a straight 240 volt connection then the bare ground conductor needs to be landed on the ground bus. Since there is no main I would assume that this is a sub-panel which means that the EGC's and the neutral conductors must be separated. The UF cable is only permitted on the interior portion of the dwelling. It cannot go directly to the tub.
Quote:
|
|
#3
|
||||
|
||||
|
They didn't get it right.
It should be a four-wire circuit from the spa (HHNG). The breaker should have 2 hot connections to the spa, with one neutral connection to the spa and one neutral connection to the isolated neutral terminal (bus bar). The grounding conductor from the spa should be attached to the bonded grounding terminal at the panel. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Thanks Jeff! So the ground conductor should not go back to the circuit breaker and the neutral should not go from the breaker to the neutral bus bar is that correct?
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The GFCI circuit breaker needs a connection to the neutral bar to function. The circuit neutral (if there is one) would land on the GFCI breaker. In a straight 240 volt configuration, without a branch circuit neutral, you would still need to connect the circuit breaker to the neutral bar. Last edited by Robert Meier; 3/9/10 at 10:55 AM.. Reason: spelling |
|
#6
|
||||
|
||||
|
Two neutrals should be attached to the breaker. One terminates in the panel at an isolated neutral terminal (which has not been provided at this sub panel), and the other goes to the spa circuit.
The grounding conductor from the spa should not be attached to the breaker. It should be attached to the grounding terminal in the panel. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Sorry Robert - I see you've covered some of this but there is some lag time while your posts are being "moderated."
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
No problem Jeff. Actually Chris just cleared me so now my posts will enter in real time. It's kind of funny to read through a thread when your post has been sitting around waiting for hours and suddenly appears and at times makes no sense because it seems out of sequence.
|
|
#9
|
|||
|
|||
|
Harry,
You up for Sonny's on Friday? 1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#10
|
||||
|
||||
|
Bruce,
If I don't get an inspection for then, sounds good. Meet halfway at 39th Avenue Sonny's. |
|
#11
|
||||
|
||||
|
Thanks Jeff and Robert! Got it now. Conductors at bottom are to service sub-panel in home. This is a main panel adjacent to the meter.
Last edited by hmcbride; 3/9/10 at 6:52 PM.. |
|
#12
|
||||
|
||||
|
Quote:
There is "service" equipment, and there is "other" equipment. The panel you have pictured is very unlikely to be "service" equipment, in which case, it's "other" equipment (aka sub panel). The conductors connected to the main lugs are feeders to that panel. In other words, that panel is being "fed" from another. The panel "adjacent to the meter" is your "service" equipment. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Do you have any other photo's maybe showing the entire installation?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Article 240 : Overcurrent Protection Article | pabernathy | Electrical Inspections | 0 | 5/23/07 11:40 AM |