Default Hot tub panel

Inspected a house today that had a separate sub panel - found a) ground and neutral combined and b) a second ground rod driven and conncted to the ground/neutral of this subpanel. Is there something about hot tub wiring that makes either of these ok?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #2  
Old 7/25/08, 4:00 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: Hot tub panel

Quote:
Originally Posted by fnewman
Inspected a house today that had a separate sub panel - found a) ground and neutral combined and b) a second ground rod driven and conncted to the ground/neutral of this subpanel. Is there something about hot tub wiring that makes either of these ok?
In a sub-panel the grounds and neutrals must be on a separate terminal bus.

The neutral terminal cannot be bonded to the panel--it must "float".

The earth ground conductor must be attached to the ground terminal, the ground terminal must be bonded to the panel.
Reply With Quote
  #3  
Old 7/25/08, 4:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Hot tub panel

The "hot-tub" has nothing to do with anything. A remote panel can be wired that way if certain conditions are met.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 7/25/08, 4:05 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot tub panel

Jae, Jeff is correct here. This can be quite compliant under certain circumstances, IF the panel is detached from the structure.
Reply With Quote
  #5  
Old 7/25/08, 4:08 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Hot tub panel

Quote:
Originally Posted by jpope
The "hot-tub" has nothing to do with anything. A remote panel can be wired that way if certain conditions are met.
OK-forgetting the "hot tub", what would the certain conditions be?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 7/25/08, 5:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Hot tub panel

There must be no other metallic connection between the panels - such as metallic piping, conduit, fences, foundation steel, etc.

There should also be a disconnect for the remote panel, located in the service panel (or the panel feeding the remote panel).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 7/25/08, 5:37 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Hot tub panel

Quote:
Originally Posted by jpope
There must be no other metallic connection between the panels - such as metallic piping, conduit, fences, foundation steel, etc.

There should also be a disconnect for the remote panel, located in the service panel (or the panel feeding the remote panel).
This panel is mounted on a vinyl/wood wall and fed with 2/C w/gnd, non-metallic sheathed cable from a dedicated breaker in the main panel, so based on the above, combining the neutral and ground and connecting a local ground rod would be ok? I've learned something new today - thanks !!



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 7/25/08, 5:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Hot tub panel

In many instances, the most difficult part (from the perspective of an HI) is verifying the absence of any additional metallic paths.

It sounds as if yours may be just fine. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 7/25/08, 5:58 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Hot tub panel

Yes, that can be difficult in some cases. I happen to know the contractor who built this particular house and am pretty familiar with the building practices in the area, so can be 99+% certain that no metallic conduit or other connection is involved. The exposed exterior conduit is all PVC as well.

It is interesting, because in the year or so I have been visiting this forum, I don't recall seeing this discussion before (usually the answer is always that 'subpanels require separate neutral and ground, etc.'). However, I would think this situation could easily exist in a majority of contenorary wood frame homes. Thanks again.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #10  
Old 7/25/08, 6:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Hot tub panel

The exception only applies to remote (sub) panels that are not attached the the building where the service equipment is located. Whenever the panels are part of the same structure/building, the neutrals must not be grounded at any point, other than at the service equipment.

I believe this exception is being eliminated in the '08 NEC. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 7/25/08, 7:43 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Talking Re: Hot tub panel

Interesting - so if the panel (like this one) is mounted on the outside wall of the house the exception does not apply, but if on a fence 10' away surrounding the hot tub it would be ok? I guess that's what keeps it interesting and confuses the average installer!

After 40+ years in heavy industrial electrial engineering work, I am still trying to get my arms around the residential portions of the NEC. However, whatever changes come with the '08 code probably won't matter a lot out in the county around here as there is no AHJ!

Given all the above, I will probably put this installation in my report for follow-up but the 'qualified electrician' they are likely to call will say it is ok.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #12  
Old 7/25/08, 9:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Hot tub panel

Quote:
Originally Posted by fnewman
Interesting - if on a fence 10' away surrounding the hot tub it would be ok?
Not necessarily.

It's always been my position that a Home Inspector is well within their "rights" as a generalist to defer a remote panel installation that is not a four-wire feed, with isolated neutrals, because it can be difficult to determine if the installation is compliant.

If I cannot conclusively rule-out the potential for an "additional metallic path/connection," I will defer the installation for verification.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 7/26/08, 12:39 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot tub panel

Quote:
Originally Posted by fnewman
This panel is mounted on a vinyl/wood wall and fed with 2/C w/gnd, non-metallic sheathed cable from a dedicated breaker in the main panel, so based on the above, combining the neutral and ground and connecting a local ground rod would be ok?
Actually no, this is not ok.
The ground of a two-wire NM cable CANNOT be used as a grounding and a grounded conductor. The bare wire in NM cable is NOT meant to carry current.

One of the specific circumstances is that the grounded conductor MUST be insulate or be part of a Type SE cable, such as SEU.
Reply With Quote
  #14  
Old 7/26/08, 1:13 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot tub panel

It doesn't sound like a separate structure is involved here. If so, how does the NM get there? Not only is the NM not allowed to carry neutral current on it's bare grounding conductor like Petey said, it is also not allowed in a wet location.
Reply With Quote
  #15  
Old 7/26/08, 2:00 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot tub panel

Defer it to an electrician who works on pools and spas. That is not usually the garden variety residential sparky
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical for Dummies mcyr Electrical 16 6/9/08 10:59 PM
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts