Does an exterior spa (wired to a 50 amp double pole GFCI breaker in the distrubution panel inside the home) require a disconnect near the tub. I have heard yes and no. Can someone give me the correct answer and NEC code?
Any help would be appreciated. Thanks, Steven |
|
#2
|
||||
|
||||
|
No. NEC 680.62
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Jeff,
Steven |
|
#4
|
|||
|
|||
|
Why SURE we can.....lol......
Art 680.12 States the unit MUST have a Maintenance Disconnecting Means. So in short....Yes...it needs the disconnect..... Paul W. Abernathy |
|
#5
|
|||
|
|||
|
JEFF.....big difference between a Therapeutic Tubs covered in 680.62 and standard SPA and Hot Tubs covered in Art 680 and appended in 680.40 IV
Paul W. Abernathy |
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Now then this rule 680.12 was added because of the death of a small child!
Last edited by jtedesco1; 3/4/06 at 8:28 PM.. |
|
#7
|
|||
|
|||
|
Yep.......covered that article above joe in my first reply....
Paul W. Abernathy |
|
#8
|
||||
|
||||
|
I did give the wrong code reference (my apologies), however, my interpretation of the question was whether or not an additional disconnect was needed.
I was on my way out the door and did not give much info. If the panel is within sight of the spa equipment, no additional disconnect is required, correct? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Damn Jeff, that's the first time i've seen you get proven wrong.....almost.
|
|
#10
|
||||
|
||||
|
I thought I was wrong once. . .
But I was mistaken IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
|||
|
|||
|
Actually.....jeff he did not state anything about the main panel being within sight or near the tub. The general question was if a disconnect is required and the answer is yet. It was made more clear in 2002 NEC to remove the issues of the lighting receptacles and so on to narrow it down to service issues and safety.
Hey brother.....we all can be wrong once.......You more than make up for it in your ZINCO lessons....... Ahh...I got ya...on your question....well the code specifically says : Each means shall be accessible and within sight from it's equipment. The intent of the disconnection means to be installed within sight of the spa and hot tub ( pool for that matter ) to allow service personnel to disconnect the power while servicing these units. This requirement ensures that a disconnect is available at all times to workers servicing and equipment such as motors, heaters and control panels. This was revised from previous NEC sections in the 2002 NEC. The idea is.....is your panel TRULY in sight and if so..is it ALWAYS accessible in all cases....what if the door is locked, you can't be their when it is being serviced and well the list can go on. The concept of putting the disconnect within sight of the unit means it is always accessible....without the chance of it not being accessible......Hope that explains it better. Paul W. Abernathy |
|
#12
|
|||
|
|||
|
Every spa maufacturer states in their installation manuals that there must be a disconnect readily accessible to the spa occupants, but installed at least 5 feet from the spa.
They also reference 422.20 and 680.42. tg |
|
#13
|
|||
|
|||
|
Yep.....guess the answer was in the MAIN question...is a disconnect required...and as answered...YES....
And yes it gets more detailed but the CODE haters usualy hate for us to go into to much detail...thehehe...... Paul W. Abernathy |
|
#14
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
I have seen the disconnects as a GFCI receptacle behing the access panel of the unit.
The other asumption is that the township, or state, is using a version of the electrical code where this requirement is stated. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Top Ten Wiring Hazards Threaten Life and Property | jtedesco1 | Electrical Inspections | 3 | 9/2/08 5:15 PM |
| Top Ten Wiring Hazards | jtedesco1 | Electrical Inspections | 6 | 9/1/08 8:26 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Wiring question in panel | dmacy | Electrical Inspections | 23 | 2/14/07 11:27 AM |
| Question on sump pump alarm wiring. | jspringstead | Electrical Inspections | 1 | 2/2/06 1:14 AM |