Default A Hot Wall

Voltage indicator went off light a Christmas tree.
1870's home suspect knob and tube (none visible) with remodeled bathroom that has wire lath and plaster wall. OUCH
Attached Thumbnails
hot-wall-114_9004-small-voltage.jpg voltage.JPG
Views:	198
Size:	86.2 KB
ID:	22795  
Reply With Quote
  #2  
Old 7/20/08, 10:15 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: A Hot Wall

good catch




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #3  
Old 7/20/08, 10:57 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: A Hot Wall

Peter, 2 questions...

How did you detect the voltage in the wall?

What made you check?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 7/20/08, 11:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: A Hot Wall

Quote:
Originally Posted by mnahrgang
Peter, 2 questions...

How did you detect the voltage in the wall?

What made you check?
And did the GFCI test normal?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #5  
Old 7/20/08, 11:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A Hot Wall

This is interesting, but I think there's at least a 50% chance that no problem exists.
Reply With Quote
  #6  
Old 7/21/08, 1:01 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: A Hot Wall

Our voltage detectors will go off when you get close to energized NM - that doesn't mean that a defect exists, it just means there are energized components in the area.

If you could get indications from a voltage meter, then I would be concerned.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/21/08, 7:06 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: A Hot Wall

Hit a wire with a fastener!?



"I create controversy whether they like it or not"



Reply With Quote
  #8  
Old 7/21/08, 7:36 AM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: A Hot Wall

The GFCI protected outlet polarity was acceptable, and tripped off with the internal tester, and my device so it tested normal.
When the device was in the off-open circuit position, I put my voltage indicator in the two prong wall light fixture over the sink. The outlet was still on. As I moved the voltage indictor from the fixture to the GFCI device, accidentally along the wall, I noticed the wall issue.
I then checked other areas ( per the photo )

I did not have anyother equipment with me to check the wall, plus I could not inspect the load center as the screws were rusted. Recommended a licensed electrician evaluate this condition and the entire electrical system and conduct all necessary repairs.

I remember reading a post about a fastener through a wire and how the whole wall was hot, well, I think I finally found one to.
Reply With Quote
  #9  
Old 7/21/08, 8:53 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: A Hot Wall

Never put your trust into a tick tracer... there are many variables that can cause them to give a false reading. Just by moving it across a surface, the vibration can set the thing off. They get old and 'oversensitive'.
Reply With Quote
  #10  
Old 7/21/08, 8:55 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: A Hot Wall

The voltage detector I have blinks and alarms if AC it detected.
If it is static or DC the sound will not alert.

Paul Abernathy sold them a while back and with NACHI logos on them.

Here it is sans logo.

No switch to leave on or where out. Best of this type I have ever owned.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]

Last edited by mlarson; 7/21/08 at 9:11 AM..
Reply With Quote
  #11  
Old 7/21/08, 7:31 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A Hot Wall

Yep....The ones I had were the best. I kept a few for myself.



Paul W. Abernathy
Reply With Quote
  #12  
Old 7/21/08, 8:27 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A Hot Wall

Quote:
Originally Posted by pbennett1
The GFCI protected outlet polarity was acceptable, and tripped off with the internal tester, and my device so it tested normal.
When the device was in the off-open circuit position, I put my voltage indicator in the two prong wall light fixture over the sink. The outlet was still on.
They may have fed the properly wired and working GFCI receptacle from this location. There would still be voltage on the wires even though the GFCI had tripped.

As I moved the voltage indictor from the fixture to the GFCI device, accidentally along the wall, I noticed the wall issue.
This would be the still energized wire feeding the GFCI.

I then checked other areas ( per the photo )
The other postive signal could be another wire feeding some other device/circuit or going up to a light from a switch in the room (if one) sharing a common wall or etc, etc, etc.

I did not have anyother equipment with me to check the wall, plus I could not inspect the load center as the screws were rusted. Recommended a licensed electrician evaluate this condition and the entire electrical system and conduct all necessary repairs.

I remember reading a post about a fastener through a wire and how the whole wall was hot, well, I think I finally found one to.
I'm with M. Shunk on this one. There are signs of proper wiring at the GFCI recept......just how far does this extend??
Reply With Quote
  #13  
Old 7/22/08, 11:42 AM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: A Hot Wall

Yes, I know that. I actually place the indictor on the wall, going very slowly.
Thanks,
Peter
Reply With Quote
  #14  
Old 7/22/08, 12:34 PM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: A Hot Wall

Peter try moving it slowly on any wall surface you may be a bit surprised. I'm more at a %5 chance of anything being wrong but keep us posted.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #15  
Old 7/22/08, 8:17 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A Hot Wall

Sadly, I am reminded of this accident where the metal studs were energized. Read the story and see the video below:

http://www.nachi.org/forum/f19/person-electrocuted-energized-metal-building-1914/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 10:48 AM
No Brick Ties - Wall Buldge Stew Structural Inspections 1 4/22/06 6:56 AM


All times are GMT -4. The time now is 3:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts