Default Hot Water Heater Wiring

The wiring for this hot water heater isn't in conduit. Is it required to be in conduit? Sorry for the simple question. I'm new at this and I'm trying to make sure I get it right.
Attached Thumbnails
hot-water-heater-wiring-dscf0681.jpg  
Reply With Quote
  #2  
Old 6/8/06, 6:10 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hot Water Heater Wiring

Howdy,

NO it does not have to be in Conduit....except in maybe ILLINOIS...lol...

But it does have to be supported correctly and in a proper connector and so on.

EDITED- YEP......Virginia allows it in NM.......Obviously NOT everywhere else....

Seems I DONT KNOW JACK.( well we all KNOW the protection issue..but in MY opinion in MY installs the protection is not a issue.)...and neither do the AHJ's in my STATE...

One of our OTHER masters should be able to assist you....



Paul W. Abernathy

Last edited by pabernathy; 6/9/06 at 10:04 PM..
Reply With Quote
  #3  
Old 6/8/06, 10:21 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Water Heater Wiring

Paul, it might be where he is. We are required to use a piece of flex with fittings to protect the NM. If there's no flex on the truck we just use liquidtite.
Reply With Quote
  #4  
Old 6/9/06, 7:08 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Water Heater Wiring

It must be protected.
NEC 334.15(B) Protection from Physical Damage.
Reply With Quote
  #5  
Old 6/9/06, 8:20 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Hot Water Heater Wiring

There was a similiar thread over at inspectionnews.com late last year. It apparently is not allowed in Florida, where Jerry Peck works, but we allow it here in San Diego (not sure about what they do up there in Santa Clarita ).



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 6/9/06, 8:46 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hot Water Heater Wiring

Physical Damage is always a thought when using NM...should go without saying now for the most part BUT in this case I just dont see the need unless the LOCAL ruling calls for it....you can't go writting up EVERYTHING you see unless you know exactly what the cause and effect of it is and it could just come back to haunt you.....

I have been wiring homes for 18 years......NOT once has any county I have installed in required any REAL protection on this usualy because the location is not in a place likely to endure physical damage.....

I think again or they SHOULD by now....any NM exposed has to be protected from physical damage....BUT I am telling you in MOST areas just plain NM will be fine to a water heater..Also may have been allowed at the time it was done...are you going to request an Electrician come back to sleeve this in a report?.......I did not start my electrical career yesteday Mr. Parks..........Mr. Lily is our HEAD inspector in the area for example and the current president of the IAEA and he would not require it to be protected other than what it is.....

I personally dont see a problem with it except for the support......again every AHJ is different so NO one answer is the RIGHT answer......



Paul W. Abernathy

Last edited by pabernathy; 6/9/06 at 8:50 AM..
Reply With Quote
  #7  
Old 6/9/06, 8:54 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Hot Water Heater Wiring

Quote:
Originally Posted by pabernathy
the location is not in a place likely to endure physical damage.....
That was my contention with Jerry Peck. He and I had one of our little disagreements over this issue.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 6/9/06, 9:05 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hot Water Heater Wiring

RRAY,

I will elaborate on that.......If I am the Inspector and I call out a SIMPLE NM to a water heater in a location that is not likely to be in a issue of physical damage per say.......and I call that out and the Home Owners calls ME the electrician out for THAT......I can see the Electrician RAZZING the HI to death about it.....Just too petty REGARDLESS of the NM protection rule....

If the Water Heater is slammed in a closet and the wires are subject to things being stacked on it, damaged is possible for the most part.

If someone does not think I am 100% aware of the Protection rule on NM then well..........they have not read my other posts...

Fact is.......how many AHJ's allow plain SE to come down to the Meter Cab and then down into the wall....on the surface.....ALOT and without protection even.......We could go on ALL day about protection but is is really up to the AHJ to FORCE that call when in doubt......

Kinda like sending your KID to the playground in BODY ARMOR.....sure he will be safer but....come on......we have to have some lines as again is it not BLACK and WHITE....AHJ's have room to require.

Me telling the GUY..YES it has to be in a protective CONDUIT is the same thing....May not in other areas....MAY BE in HIS area.....MAY NOT be in VIRGINIA which it is not.........none of the AHJ's will require it and I know them...most all of them.....

SO it is a loaded question....BUT nothing I am going to call out in this case except I would like to see more cable as it seems tight....and no support to the NM......but again the question was does it have to be in Conduit.......what so you say......to keep it short...YES or NO....I say.......NO based on MY experience and it may be different in other areas...like ILLINOIS.....but I can't list all states it may be different....lol

I am a DIEHARD CODE GUY.......but this one is gray for me...I personally in over 18 years of wiring homes have never sleeved the NM in conduit or LT to protect it.....and NEVER has it been called out and I know the CODE rather well....



Paul W. Abernathy
Reply With Quote
  #9  
Old 6/9/06, 11:26 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Water Heater Wiring

Quote:
Originally Posted by inspector@carolina.rr.com
The wiring for this hot water heater isn't in conduit. Is it required to be in conduit? Sorry for the simple question. I'm new at this and I'm trying to make sure I get it right.
Another Opinion: 334.15 Exposed Work

(A) To Follow Surface. Cable shall closely follow the surface of the building finish or of running boards.

334.30 (B) Unsupported Cables. Nonmetallic-sheathed cable shall be permitted to be unsupported where the cable:

(1) Is fished between access points through concealed spaces in finished buildings or structures and supporting is impracticable.

(2) Is not more than 1.4 m (4 1/ 2 ft) from the last point of cable support to the point of connection to a luminaire (lighting fixture) or other piece of electrical equipment and the cable and point of connection are within an accessible ceiling.

Section 334.30(B)(2) permits short, unsupported lengths of nonmetallic-sheathed cable for luminaire and equipment connections.

Reference: 2005 NEC

This wiring method is not permitted to be used as described, and may also be not of the proper temperature rating.

This has been a well known fact by the electrical industry for many years!
Reply With Quote
  #10  
Old 6/9/06, 11:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Hot Water Heater Wiring

As I continue in this industry, I find more and more things that the AHJs allow here in San Diego that don't seem to be allowed in other areas of the country, or even in California, further north of me, like in Santa Clarita in Jeff Pope's neighborhood. We do allow what's shown in the picture here in San Diego. Of course, after the power crisis of 2000-2001, most everyone has replaced their electric water heaters with gas water heaters or tankless water heaters.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 6/9/06, 12:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Hot Water Heater Wiring

I have never seen an electric WH wired in this manner, so I've never had a reason to research it.

I have only seen it in FMC or LFMC (as I would expect). Usually, directly to a switch or breaker.

I must say, I certainly don't like the look of the NM wiring method and I will call my AHJ if I ever come across it



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 6/9/06, 12:35 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Water Heater Wiring

Paul agreed that your AHJ may not require it.

Every ESI in the central Ohio area will fail you for not protecting it.

Safety is the issue. The above is an unsafe condition.

Tuesday evening I'll confirm this with the past president of the Ohio Chapter of the IAEI.
Reply With Quote
  #13  
Old 6/9/06, 12:57 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Hot Water Heater Wiring

I live in Florida and 99 times out of 100 you will find the NM cable coming out of hole, thats right, a hole, knocked in the wall without any kind of support, j box or anything remotely resembling neat, clean workmanship. The only place it is normally secured is at the top of the WH where you may find an NM clamp. Then again you may not. The AHJ passes it every time. These are the same guys that allows Weaver clamps to be used on the ground rods and buried in the yard. Most of those corrode completely away in a couple of years. Find many cases where just the old rusted screws can be found, with the grounding conductor standing proudly in the air.
Reply With Quote
  #14  
Old 6/9/06, 9:21 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hot Water Heater Wiring

lol....All I can say is..........I have wired THOUSANDS of homes with NM to the water heater........Have well over 150 electrician friends in VA who also do the same thing....lol.........now I may be a NEC Consultant and I know about physical protection...

But I can promise you this JOE.......my NEXT water heater wiring will be NM like it has been since 1988 when I did my very first house.....



Paul W. Abernathy
Reply With Quote
  #15  
Old 6/9/06, 9:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hot Water Heater Wiring

EDITED-

Just not worth my time.....when I give an OPINION on something other than just SPOUTING code I get ripped....so I will keep my OPINIONS to myself....

Got a Water Heater to wire Monday....Guess WHAT.....I am using NM.....call the local inspector JOE and tell him to fail me...



Paul W. Abernathy

Last edited by pabernathy; 6/9/06 at 9:51 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/24/07 11:28 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM


All times are GMT -4. The time now is 3:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts