Observed some of the aluminum wiring in the main panel and in electical box in the house.
All electrical components tested good, electrical outlets, AC, heater,
kitchen appliance.....etc.
What type of disclosure should be made of some of the wiring being
aluminum? Most of the wiring coming from the main panel was copper.


David








An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/27/11, 3:21 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Aluminum wire is installed on 120 VAC branch electrical circuits in the subject house. These single strand, branch circuit aluminum wires were used widely in houses during the mid 1960s and 1970s. According to the U.S. Consumer Product Safety Commission, problems due to expansion can cause overheating at connections between the wire and devices (switches and outlets) or at splices, which has resulted in fires. For further information on aluminum wiring contact the U.S. Consumer Product Safety Commision.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 8/27/11, 4:56 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Quote:
Originally Posted by kwood View Post
Aluminum wire is installed on 120 VAC branch electrical circuits in the subject house. These single strand, branch circuit aluminum wires were used widely in houses during the mid 1960s and 1970s. According to the U.S. Consumer Product Safety Commission, problems due to expansion can cause overheating at connections between the wire and devices (switches and outlets) or at splices, which has resulted in fires. For further information on aluminum wiring contact the U.S. Consumer Product Safety Commision.
Thanks...David



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #4  
Old 8/27/11, 5:10 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Quote:
Originally Posted by kwood View Post
Aluminum wire is installed on 120 VAC branch electrical circuits in the subject house. These single strand, branch circuit aluminum wires were used widely in houses during the mid 1960s and 1970s. According to the U.S. Consumer Product Safety Commission, problems due to expansion can cause overheating at connections between the wire and devices (switches and outlets) or at splices, which has resulted in fires. For further information on aluminum wiring contact the U.S. Consumer Product Safety Commision.
Pretty good. But instead of just providing info, you should also recommend a complete evaluation of the home's wiring by a competent and licensed electrician prior to the close of escrow.

"The system includes solid-core aluminum wire that has long been suspect, and with good reason. Aluminum wire does not conduct current as efficiently as copper wire, and because it oxidizes it can act as an insulator instead of a conductor, building up resistance to conduction and heat in the process. Also, as a poor conductor, it has a tendency to expand and contract more, and thereby become loose at any one of the multiple connections such as switches, outlets, and elsewhere. This type of system can positively be a fire-hazard and is no longer allowed in new construction. Therefore, you should seek the counsel of a competent and licensed electrician prior to the close of escrow who is familiar with this issue, and with the recommended procedures to correct the known deficiencies, such as Copalum crimping."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 8/27/11, 5:27 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

You are right Joe but I wanted him to go to the safety site and make up the rest on his own.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 8/27/11, 5:32 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Quote:
Originally Posted by jfunderburk View Post
Pretty good. But instead of just providing info, you should also recommend a complete evaluation of the home's wiring by a competent and licensed electrician prior to the close of escrow.

"The system includes solid-core aluminum wire that has long been suspect, and with good reason. Aluminum wire does not conduct current as efficiently as copper wire, and because it oxidizes it can act as an insulator instead of a conductor, building up resistance to conduction and heat in the process. Also, as a poor conductor, it has a tendency to expand and contract more, and thereby become loose at any one of the multiple connections such as switches, outlets, and elsewhere. This type of system can positively be a fire-hazard and is no longer allowed in new construction. Therefore, you should seek the counsel of a competent and licensed electrician prior to the close of escrow who is familiar with this issue, and with the recommended procedures to correct the known deficiencies, such as Copalum crimping."

Thanks....



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #7  
Old 8/27/11, 5:38 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

My own version ...

The house has older solid conductor aluminum wiring which has a know history of problems, and has been linked to many house fires, so it is considered a fire hazard. The wiring needs evaluation and repair by a qualified electrician familiar with aluminum wiring problems. Repairs can include replacement of the wire where easily accessible, or installation of short pieces of copper wire called "pigtails" attached at both ends of the aluminum wire with special connectors. For additional information see CPSC Publication #516.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 8/27/11, 6:19 PM
jtedesco3 jtedesco3 is offline
New User
 
Join Date: Jul 2011
Location: Boston, MA
Posts: 38
Please Note: jtedesco3 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

This site is full of good information too.
Reply With Quote
  #9  
Old 8/27/11, 6:52 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Quote:
Originally Posted by roconnor View Post
My own version ...

The house has older solid conductor aluminum wiring which has a know history of problems, and has been linked to many house fires, so it is considered a fire hazard. The wiring needs evaluation and repair by a qualified electrician familiar with aluminum wiring problems. Repairs can include replacement of the wire where easily accessible, or installation of short pieces of copper wire called "pigtails" attached at both ends of the aluminum wire with special connectors. For additional information see CPSC Publication #516.
Great version.... Im going to save the whole thread.



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #10  
Old 8/27/11, 8:09 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

NC Licensure Board Recommended Language

Home Inspection Report & Summary Page – Recommended language for Aluminum Wiring.
Single strand aluminum wire is present on 120 volt branch circuits in this house. This single strand, branch circuit aluminum wire was used widely during the 1960s and 1970s. According to reports published by the U.S. Consumer Product Safety Commission (CPSC), problems due to overheating at the connections between the wire and devices such as switches, outlets, and light fixtures may have been responsible for house fires. It is recommended that the circuits using single strand aluminum wiring be evaluated and modified as may be deemed necessary by a licensed electrical contractor who is familiar with the problems inherent in this type of wiring. For more information on aluminum household wiring, refer to the National Electrical Code and the C.P.S.C. booklet "Repairing Aluminum Wiring." The toll-free hotline number for obtaining this booklet is 1-800-638-2772, or you can visit:
http://www.cpsc.gov/cpscpub/pubs/516.pdf.
Reply With Quote
  #11  
Old 8/28/11, 1:23 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: House Built in 1971, Some Aluminum wiring in the main panel....need advise

Solid Strand AL wiring is a fairly well known issue.. document what you see and advise the buyers to gain the services of an electrician.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Main Panel wiring sstanczyk Electrical Inspections 2 2/9/06 8:55 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts