Ok I have a 284 Litre (75 Gallon) HWT tank on a 240V 20 AMP breaker. The hot water heater states 3800/4500W upper and 3800/4500W Lower with 4500W Max Load. It is a GSW.
OHMS LAW comes up with 18.75 AMPS This needs a 30 AMP breaker right? |
| Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Right and 10 gauge wiring!
Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The load is as you've stated 4500 watts:
4500w/240v=18.75 amps The NEC considers a HWH a continuous load therefore the circuit must be sized at 125% of the nameplate value: 18.75 amps * 125% = 23.4 amps. This could be on a 25 amp OCPD with #10 AWG conductors. Quote:
Quote:
|
|
#4
|
||||
|
||||
|
Robert,
Correct but 25 Amps breakers are not common so the 30 Amps are used. Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I just wanted to point out that using a 25 amp OCPD in this application would be code compliant and that a 30 amp is not required. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Total Amps and missing AC breaker | dalvares | Electrical Inspections | 17 | 12/27/08 1:17 PM |
| Panel amps | scroenne | Electrical Inspections | 3 | 8/7/08 7:01 PM |
| to many amps | shegert | Electrical Inspections | 6 | 7/19/08 10:30 PM |
| Upgrade 60 amps to 100 amps | jbettencourt | Electrical Inspections | 4 | 7/17/08 9:07 PM |
| How many Amps??? | psmothers | Electrical Inspections | 7 | 8/9/06 2:01 PM |