Ok I have a 284 Litre (75 Gallon) HWT tank on a 240V 20 AMP breaker. The hot water heater states 3800/4500W upper and 3800/4500W Lower with 4500W Max Load. It is a GSW.

OHMS LAW comes up with 18.75 AMPS

This needs a 30 AMP breaker right?
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/27/10, 9:16 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Hwt amps

Quote:
Originally Posted by mnicholet View Post
Ok I have a 284 Litre (75 Gallon) HWT tank on a 240V 20 AMP breaker. The hot water heater states 3800/4500W upper and 3800/4500W Lower with 4500W Max Load. It is a GSW.

OHMS LAW comes up with 18.75 AMPS

This needs a 30 AMP breaker right?
Right and 10 gauge wiring!



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #3  
Old 4/28/10, 5:04 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hwt amps

The load is as you've stated 4500 watts:

4500w/240v=18.75 amps

The NEC considers a HWH a continuous load therefore the circuit must be sized at 125% of the nameplate value:

18.75 amps * 125% = 23.4 amps.

This could be on a 25 amp OCPD with #10 AWG conductors.

Quote:
422.13 Storage-Type Water Heaters.
A fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall be considered a continuous load for the purposes of sizing branch circuits.
Quote:
II. Branch-Circuit Ratings
210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
Reply With Quote
  #4  
Old 4/28/10, 8:30 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Hwt amps

Robert,

Correct but 25 Amps breakers are not common so the 30 Amps are used.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 4/28/10, 3:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hwt amps

Quote:
Originally Posted by mgratton View Post
Robert,

Correct but 25 Amps breakers are not common so the 30 Amps are used.
That is true, but 25 amps is considered a standard size OCPD by the NEC.

I just wanted to point out that using a 25 amp OCPD in this application would be code compliant and that a 30 amp is not required.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Total Amps and missing AC breaker dalvares Electrical Inspections 17 12/27/08 1:17 PM
Panel amps scroenne Electrical Inspections 3 8/7/08 7:01 PM
to many amps shegert Electrical Inspections 6 7/19/08 10:30 PM
Upgrade 60 amps to 100 amps jbettencourt Electrical Inspections 4 7/17/08 9:07 PM
How many Amps??? psmothers Electrical Inspections 7 8/9/06 2:01 PM


All times are GMT -4. The time now is 8:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts