Default Hydro tub bonding

Does the pump motor require bonding when house is on PEX water supply?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 6/2/09 at 12:56 AM..
Reply With Quote
  #2  
Old 5/16/08, 1:17 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydro tub bonding

If there is no metal of any kind in contact with the water no bonding is required
Reply With Quote
  #3  
Old 5/16/08, 5:09 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydro tub bonding

I totally agree. Just because that lug is empty does NOT automatically mean "defect".
Reply With Quote
  #4  
Old 5/16/08, 10:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydro tub bonding

Just thought I should add that if this jetted tub also happened to have an inline heater (most don't, some do), that heater will have a similar lug. With all non-metallic pipework, the lug on the motor would still get connected to the lug on the heater unit.
Reply With Quote
  #5  
Old 5/17/08, 7:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Hydro tub bonding

yeppers......and for goodness sake dont let anyone tell you the lug on the motor requires a #8 AWG bonding conductor back to the panel........the lug is for the equipotential plane at the hydromessage tub........nothing more.....nothing less.

I concur with mike and mark........hey dont they have a candy named after them....no wait...thats mike and ike....sorry.....



Paul W. Abernathy

Last edited by pabernathy; 5/17/08 at 8:00 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 8:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts