Default Is this an IC Rated Luminary?

Just finished an inspection today. LOTS of moisture in the attic. Happened to bump a luminary under the insulation and took some pictures (attached). Doesn't appear to be IC rated or if it is, it wasn't properly installed since the interface of the luminary and drywall was not sealed.
I did a look-up on the UL label (E17885), but that wasn't any help. What do you think?
Attached Thumbnails
ic-rated-luminary-p1230911.jpg   ic-rated-luminary-p1230906.jpg   ic-rated-luminary-p1230925.jpg   ic-rated-luminary-p1230926.jpg   ic-rated-luminary-p1230924.jpg  




Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/1/11, 4:45 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an IC Rated Luminary?

It should say it somewhere on the interior label of the fixture. If you look at the junction box on the side of the fixture is the thermal overload sticking out of it? If so I would bet that it is not an IC type.
Reply With Quote
  #3  
Old 3/1/11, 4:54 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

I didn't see anything. Considering the j-box is not sealed I would guess no. The only rating I saw was for damp location and suspended ceiling.
Attached Thumbnails
ic-rated-luminary-p1230901.jpg   ic-rated-luminary-p1230900.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 3/1/11, 4:54 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an IC Rated Luminary?

AFAIK IC rated does not require sealing the drywall housing interface. I have never seen this for the brand I typically install. IC just allows the insulation to contact the housing.

I think the information you may need is on the label on the outside of the housing. If you could see the model number and brand on the inside label it would help.
Reply With Quote
  #5  
Old 3/1/11, 4:56 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

I just attached the outside pics



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 3/1/11, 4:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Is this an IC Rated Luminary?

There are two methods to determine.
Check like you did for the IC rating and also check for air slots that would tell you they are not.
From what I see they are IC rated.
ic-rated-luminary-can-lights.jpg
Reply With Quote
  #7  
Old 3/1/11, 5:03 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

Quote:
Originally Posted by belliott View Post
There are two methods to determine.
Check like you did for the IC rating and also check for air slots that would tell you they are not.
From what I see they are IC rated.
Attachment 42595
I did not see any slots in the sides of the can. I did see lots of air infiltration from the living space to the attic space. I thought IC ratings also include a maximum flow rate through the luminary of 2 cfm max. I know this is getting way to technical for a HI, but the attic was saturated with moisture.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #8  
Old 3/1/11, 5:10 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Is this an IC Rated Luminary?

Quote:
Originally Posted by gliebig View Post
I did not see any slots in the sides of the can. I did see lots of air infiltration from the living space to the attic space. I thought IC ratings also include a maximum flow rate through the luminary of 2 cfm max. I know this is getting way to technical for a HI, but the attic was saturated with moisture.
May have nothing to do with the can lights at all unless they are not covered and are allowing condensation from below through them and the venting is lacking.
Were you getting good air flow in the attic from roof/soffit,ridge vents,gable,etc.?

I swear that sheathing looks like it was stained.(as in varnish)

Last edited by belliott; 3/1/11 at 5:13 PM..
Reply With Quote
  #9  
Old 3/1/11, 5:19 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

No, Some of the soffits were covered with insulation. There were 4-8 inch roof louvers. 1120 sq feet. 3.7 sq ft vent area required. 1.87 sq feet on roof which is just over 4 louvers. One additional roof louver and installation of air chutes is what I recommended in the report.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #10  
Old 3/1/11, 6:07 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Is this an IC Rated Luminary?

That is a Commercial Electric unit manufactured by Jimway and distributed by Home Depot. According to what I found out, it is an IC rated can. Jimway / Commercial Electric Non-IC cans are cream colored and their IC rated cans are the galvanized color. There would have been a label just past the interior frame that holds the plug / fixture.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #11  
Old 3/1/11, 6:11 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

Thanks. I couldn't get in that far without disassembly which is going beyond the SOP. There was an Energy Code sticker on the inside issued by the state of Washington. It was the green one in my original post.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #12  
Old 3/1/11, 6:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an IC Rated Luminary?

Just a note that IC is a different rating than AT (air-tight).

Why would the junction box need to be sealed? There is no interface to the conditioned space.
Reply With Quote
  #13  
Old 3/1/11, 6:24 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Is this an IC Rated Luminary?

Is type AT listed somewhere? I saw type IC listed in NEC 2008 410.116.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/1/11, 7:10 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an IC Rated Luminary?

Quote:
Originally Posted by Jim Port View Post
Just a note that IC is a different rating than AT (air-tight).

Why would the junction box need to be sealed? There is no interface to the conditioned space.
It may be IC approved and loose to air movement......... it can't be airsealed on site for energy conservation and prevention of moist air migrating to the attic. It was tested and approved in its "loose" state and must remain that way to maintain its "tested/certified" status.
Reply With Quote
  #15  
Old 3/2/11, 4:22 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Is this an IC Rated Luminary?

Quote:
Originally Posted by sstanczyk View Post
That is a Commercial Electric unit manufactured by Jimway and distributed by Home Depot. According to what I found out, it is an IC rated can. Jimway / Commercial Electric Non-IC cans are cream colored and their IC rated cans are the galvanized color. There would have been a label just past the interior frame that holds the plug / fixture.
He is correct! Silver cans tend to be IC rated, and white ones are not. The white ones will always have a label on them telling you this.
Go to HD and look at the can lights next time.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fire Rated Garage Door ederousse Structural Inspections 5 12/10/10 12:35 PM
Fire Rated Assemblies mcyr Commercial Inspections 2 8/29/10 8:28 AM
Fire Rated Garage Door? jfunderburk Interior Inspections 3 7/21/07 10:01 AM
Door to Attic. To be rated or not? jlybolt Interior Inspections 8 6/1/07 1:04 AM
Manablock in rated wall jlybolt Interior Inspections 10 5/23/06 9:27 PM


All times are GMT -4. The time now is 8:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts