Default What if this was found in a dwelling?

Have you ever found this type of installation in a dwelling?

Last edited by jtedesco1; 6/12/08 at 5:38 PM..
Reply With Quote
  #2  
Old 3/22/08, 10:25 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

In 40+ years of working in and around buildings including farms, a dairy, under a licensed electrician for 3 years and 24+ years inspecting, have never seen that setup. The horizontal must be a 6-15R . In the right (or wrong may be better term) setup, this will cause frequent tripping. Is it still allowed?

PS: The more I think about it........If I wrote codes, I wouldn't allow it!!

Last edited by Brian A. MacNeish; 3/22/08 at 10:41 AM..
Reply With Quote
  #3  
Old 3/22/08, 10:28 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

As long as a grounding means existed it's fine.
I've seen those devices but never wired one.
Reply With Quote
  #4  
Old 3/22/08, 10:56 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by Brian A. MacNeish
In 40+ years of working in and around buildings including farms, a dairy, under a licensed electrician for 3 years and 24+ years inspecting, have never seen that setup. The horizontal must be a 6-15R . In the right (or wrong may be better term) setup, this will cause frequent tripping. Is it still allowed?

PS: The more I think about it........If I wrote codes, I wouldn't allow it!!
Yes you could get frequent tripping ,but you also can get frequent Tripp on a regular circuit with two high loads plugged in.
Unusual set up but no difference then we get in a panel with various loads fed from Breakers.
You can get the same unbalance in the main breaker.

...Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #5  
Old 3/22/08, 11:03 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by jtedesco1
Have you ever found this type of installation in a dwelling?
Joe, good topic

i have installed many of these in apartments just under a window in years gone by.

This will allow either a 120 volt or a 240 volt window air conditioner to be used.
Reply With Quote
  #6  
Old 3/22/08, 11:25 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by Mike Whitt
Joe, good topic

i have installed many of these in apartments just under a window in years gone by.

This will allow either a 120 volt or a 240 volt window air conditioner to be used.

Aha!!! The special use receptacle for warm climates.

By your codes, does this have to be a dedicated circuit?
Reply With Quote
  #7  
Old 3/22/08, 11:57 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by Brian A. MacNeish
Aha!!! The special use receptacle for warm climates.

By your codes, does this have to be a dedicated circuit?
Yes .
Reply With Quote
  #8  
Old 3/22/08, 12:29 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by Mike Whitt
Yes .
Then as code writer, I'd probably put it back in!!!

You can see I come from cold climes.....snow flurries and 28*F at noon here. Live on the ocean....may have wanted AC here 1 or 2 days in 15 years.
Reply With Quote
  #9  
Old 3/22/08, 3:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Why would this have to be a dedicated circuit unless you specifically knew it was for a window AC or some other large load?
I could see this in a shop where you might have a mix of 120 and 240v tools which would be used one at a time in different locations.

BTW this picture comes from the handbook where they are talking about multiwire circuits.

I have exactly this type of 3w +g circuit going to my pool pump and heater although it is hard wired, not cord and plug. The 240 runs the pump and one leg plus neutral of that goes to the gas heater igniter and blower. (as required by the heater instructons)

The only real code requirement is this must be fed with a double pole breaker. (the point of the picture Joe posted)
Reply With Quote
  #10  
Old 3/22/08, 8:02 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Then be careful with the loads on this duplex receptacle to prevent nuisance tripping. The total amperage on the phase wire common to both halves of the receptacle is additive rather than subtractive as it is in a split kitchen counter receptacles or other three conductor installations with shared neutral. It would be easy to get over 15 amps in a shop situation such as a 240 volt table saw and a 120 volt dust collector
Reply With Quote
  #11  
Old 3/22/08, 9:15 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

You certainly have to match the load to the circuit but that is true anywhere. Mike's example (a window shaker outlet) would be the perfect use for a device like this.
Usually a dust collector would be on a circuit by itself anyway since they can be a true 2hp motor.
I'm sure Joe was just pointing out that this is a legal configuration and you could be using 120v loads on each side and a 240v across the two if they were small enough.

BTW to see this in a real life application most people see frequently, look at ranges and dryers. Both usually have a mix of 120 and 240v loads on the same circuit.
Reply With Quote
  #12  
Old 3/22/08, 9:24 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by Brian A. MacNeish
Then be careful with the loads on this duplex receptacle to prevent nuisance tripping. The total amperage on the phase wire common to both halves of the receptacle is additive rather than subtractive as it is in a split kitchen counter receptacles or other three conductor installations with shared neutral. It would be easy to get over 15 amps in a shop situation such as a 240 volt table saw and a 120 volt dust collector
You can do the same with Receptacles any where in the home .
Electric Heater 1,000 watts and some one plugs in a saw.
You have just exceeded the 15 amp Breaker .

Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #13  
Old 3/23/08, 2:45 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: What if this was found in a dwelling?

Quote:
Originally Posted by jtedesco1
Have you ever found this type of installation in a dwelling?
Thank you for this post, Joe. From an HI perspective, this one is very relivant. I have not seen one of these but if I did I would be posting here looking for help. If I understand right this is similar to the way an electric oven or dryer pulls off one leg for lights and controls.
Reply With Quote
  #14  
Old 3/23/08, 2:56 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

The only time I've seen those receptacles has been for under-window receptacles installed in the 60's. I suppose they were for either a 110 or 220 window air conditioner? In any event, it's a moot point nowadays, since nobody will be installing them new. My price book says that I've have to charge almost 200 bucks to put one in. I suppose a home inspector could run into one every once in a while, but unless you've have a sharp eye, you might not realize that the other half of the duplex is a 240V arrangement. Something to keep in the back of your mind.
Reply With Quote
  #15  
Old 3/23/08, 3:14 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What if this was found in a dwelling?

Why so much Marc. A Leviton 5842 (the commercial grade, 20a model 120/240 receptacle) is only 7 bucks or so from the online guys. You have some 12/3 and a 2 pole breaker vs 12/2 and a single pole.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
2 questions staylor5 Electrical Inspections 14 12/18/09 3:32 AM
Panels of all types found around the USA! jtedesco1 Electrical Inspections 7 1/11/08 8:26 PM
Found in attic klott Miscellaneous Discussion for Inspectors 7 5/3/07 6:35 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 7:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts