Default If this were your home--replace FP box?

I am not an inspector, just a concerned homeowner...

Last night I was watching a home show where an inspector cautioned a buyer about an FP box (going as far to say that it would be difficult to get insurance). Sitting here today, I realize that I also have an FP stab-lock box.

I've done a great deal of reading this morning, and realize that there are many unofficial warnings. I am leaning toward replacement, though I have never had any sign of a problem. I believe that this a 125 amp box, installed in 1981.

Looking for your professional opinion and experience--would you replace this if it were in your home?

Thank you!
Reply With Quote
  #2  
Old 2/10/08, 2:54 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

I can tell you from first hand experience that FPE breakers often fail to trip when they should. I am an electrician, and my professional advice is to have the panel replaced. After all, overcurrent protection is one of the main reasons for breakers, and the FPE often does not live up to that requirement. The fact that you have no sign of a problem is meaningless. You have no way to know if your breakers should have tripped in the past and didn't.
Reply With Quote
  #3  
Old 2/10/08, 2:56 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

FP boxes have concerns. However if there is no indications of issues leave it alone.


However if it where my house. I would call a local licensed electrician who has a good reputation and ask for a quote to replace it. If the quote was within my budget, it would be on his schedule to replace that day.

hope this helps,

Curt
Reply With Quote
  #4  
Old 2/10/08, 3:42 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by cgoyette
FP boxes have concerns. However if there is no indications of issues leave it alone.


However if it where my house. I would call a local licensed electrician who has a good reputation and ask for a quote to replace it. If the quote was within my budget, it would be on his schedule to replace that day.

hope this helps,

Curt
Curt,
Are you running for office or going bipolar, on us?

Carrie,

Follow Marc's advice he is a well respected source of A+ information and I advise my clients of the need to have evaluated whenever I encounter FPE.

Here is an example of a different type panel that had gone undetected until I showed up for an inspection.

Note the fused marks on the bus bar, never seen under the breakers and the current owners never disclosed any problems. Why would they they were also unaware.
Not if, but when was this going to become property or life loss, issue?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:22 PM..
Reply With Quote
  #5  
Old 2/10/08, 3:48 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by badair
Curt,
Are you running for office or going bipolar, on us?
Why did I sound like Hillary?

Its one of those rare instances where both answers work. You have issues easy to say replace. I am no fan of FP but if there are no issues its hard as a HI to say replace....easy as a HOME OWNER to say replace.....hence my answer.
Curt


AKA soon to be running for office.....Not
Reply With Quote
  #6  
Old 2/10/08, 3:52 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by Carrie Kirscht
I am not an inspector, just a concerned homeowner...

Last night I was watching a home show where an inspector cautioned a buyer about an FP box (going as far to say that it would be difficult to get insurance). Sitting here today, I realize that I also have an FP stab-lock box.

I've done a great deal of reading this morning, and realize that there are many unofficial warnings. I am leaning toward replacement, though I have never had any sign of a problem. I believe that this a 125 amp box, installed in 1981.

Looking for your professional opinion and experience--would you replace this if it were in your home?

Thank you!
What country are you in .
The Canadian FP I do believe are different then USA.
They are no concern here and are still manufactured and I have one in my home .
I am not changing it .
...Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 2/10/08, 3:52 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: If this were your home--replace FP box?

I'm of the school of thought that says HI's are not qualified to determine the need for replacement hence my standard report wording is:
Quote:
The home is equipped with a Federal Pacific brand electrical panel which have been shown to be problematic. Independent laboratory testing indicates some models of these panels are prone to problems that can lead to failures of the panel, fire hazards, lack of proper protection of circuits and other serious issues. I recommend a careful, detailed analysis of these panels by a licensed electrician to determine if any corrective action is needed.
Reply With Quote
  #8  
Old 2/10/08, 3:59 PM
Carrie Kirscht Carrie Kirscht is offline
New User
 
Join Date: Feb 2008
Posts: 3
Please Note: Carrie Kirscht is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by rcooke
What country are you in .
The Canadian FP I do believe are different then USA.
They are no concern here and are still manufactured and I have one in my home .
I am not changing it .
...Cookie
I'm in the US. I do believe they are different and that I have the problematic variety....
Reply With Quote
  #9  
Old 2/10/08, 4:05 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by Carrie Kirscht
I'm in the US. I do believe they are different and that I have the problematic variety....
Well, there you go, you answered your own question.

If it was my home it would be replaced, too.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 2/10/08, 4:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by Carrie Kirscht
I am leaning toward replacement, though I have never had any sign of a problem.
I love when I hear things like this. "I've been here for 20 years and it's never had a problem."

If there were documented issues regarding the airbags in your car, would you say the same thing? After all, they've been there for X# years and there has never been a problem. . .

That's most likely because you've never had to rely on them [airbags or breakers].

The panel and it's components are a safety system, much like the airbags in your car. When there is a problem, you want your safety systems to work flawlessly. Otherwise, the results could be catastrophic.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/10/08, 5:50 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

Carrie,
Like Marc I am a licensed and insured electrical contractor.
When I bought my home in 1993 it had an FPE panel that was in fine shape physically.
I replaced it within one week of moving in.

Does that tell you anything?
Reply With Quote
  #13  
Old 2/10/08, 6:32 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by Speedy Petey
Carrie,
Like Marc I am a licensed and insured electrical contractor.
When I bought my home in 1993 it had an FPE panel that was in fine shape physically.
I replaced it within one week of moving in.

Does that tell you anything?
yea says you got a great QOUTE.....LOL
Reply With Quote
  #14  
Old 2/10/08, 8:22 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: If this were your home--replace FP box?

Quote:
Originally Posted by cgoyette
yea says you got a great QOUTE.....LOL
Reply With Quote
  #15  
Old 2/10/08, 9:16 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: If this were your home--replace FP box?

Carrie, I also always reccommend immediate evaluation by a licensed electrician. As an HI we can't really say something must be replaced. If it was my home it would be replaced ASAP. you may want to cruise around on this site. http://www.inspect-ny.com/fpe/fpepanel.htm
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IR In The Market Place jmckenna1 Thermal Imaging, Infrared Cameras & Energy Audits 4 12/18/07 6:43 PM
Home Inspector Listings Part Two jbowman Miscellaneous Discussion for Inspectors 8 8/29/06 8:52 PM


All times are GMT -4. The time now is 8:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts