Default I'm guessing this is a code violation???

All of these wirenuts in the panel can't be allowed by the 06 IRC but i can't find anything in there. Any ideas what specific section it's in? if not how should i word this discrepancy in the report?
Attached Thumbnails
im-guessing-code-violation-img_6250000000.jpg  
Reply With Quote
  #2  
Old 11/19/08, 10:43 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: I'm guessing this is a code violation???

Wow, that's a mess.
However, it looks like the original contractor
F'ed
up on his home runs or the panel was moved, regardless, wire nut's are allowed in an enclosure such as a panel and it is OK by code as to the best of my memory.

I would recommend A licenced sparky come out and check it just in case there are loose nuts etc.

I would like to see the rest of the panel. Got a pic of the bottom half?

Last edited by tallen; 11/19/08 at 10:49 PM..
Reply With Quote
  #3  
Old 11/19/08, 10:54 PM
jjackson3 jjackson3 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Warner Robins, GA
Posts: 7
Default Re: I'm guessing this is a code violation???

Thanks for the quick reply! and yes here's the bottom half...
Attached Thumbnails
im-guessing-code-violation-img_6251-panel.jpg  
Reply With Quote
  #4  
Old 11/19/08, 11:00 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: I'm guessing this is a code violation???

That seems OK. That wire in the top right seems a little out of hand though.. To much copper showing IMO..

Hmm, I see a spot or two were there are 2 or more ground wires under one lug.......... Code says otherwise... Report should say these things with NO code reference. Consult a licenced and qualified electrician for further examination and recommendations for repairs ... Or something like that..

Last edited by tallen; 11/19/08 at 11:05 PM..
Reply With Quote
  #5  
Old 11/19/08, 11:10 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I'm guessing this is a code violation???

Some authorities may object to bundling all those wires with a zap strap on the left side. This can lead to a buildup of heat.
I'd want the grounds checked if that was my place, the others would be self evident.
If this is new construction it is indeed a f#$%up. If it's an older house, it's a panel upgrade, may be excusable.

John Kogel
www.allsafehome.ca
Reply With Quote
  #6  
Old 11/19/08, 11:10 PM
jjackson3 jjackson3 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Warner Robins, GA
Posts: 7
Default Re: I'm guessing this is a code violation???

Much thanks Tallen
Reply With Quote
  #7  
Old 11/19/08, 11:13 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: I'm guessing this is a code violation???

Quote:
Originally Posted by jjackson3 View Post
Much thanks Tallen
You are most welcome. I have not had the pleasure of helping anyone on this board for quite some time.
Reply With Quote
  #8  
Old 11/19/08, 11:14 PM
jjackson3 jjackson3 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Warner Robins, GA
Posts: 7
Default Re: I'm guessing this is a code violation???

yup new construction....thanks for the post!
Reply With Quote
  #9  
Old 11/20/08, 6:31 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I'm guessing this is a code violation???

Those wirenuts are 100% legal in that panel, safe, and a very common sight to see.
Reply With Quote
  #10  
Old 11/20/08, 6:49 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I'm guessing this is a code violation???

Quote:
Originally Posted by tallen View Post
Hmm, I see a spot or two were there are 2 or more ground wires under one lug.......... Code says otherwise...
Actually code says that is fine. It's neutrals that must be alone in each hole.
Most modern panels can accept up to three grounds of the same size per hole.
Reply With Quote
  #11  
Old 11/20/08, 6:51 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: I'm guessing this is a code violation???

Wires can be spliced in a panel, providing that the termination is inside the panel. So long as adequate space exists, it is absolutely permissible.
Reply With Quote
  #12  
Old 11/20/08, 7:32 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I'm guessing this is a code violation???

This could be an issue where some crackhead cut all the copper out of the panel to sell for scrap.
Reply With Quote
  #13  
Old 11/20/08, 9:58 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: I'm guessing this is a code violation???

Quote:
Originally Posted by tallen View Post
Wow, that's a mess.

I would recommend A licenced sparky come out and check it just in case there are loose nuts etc.
If we called out a sparky for all the loose nuts - they'd be so busy here on the message board, wouldn't get any work done!



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #14  
Old 11/20/08, 8:22 PM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 55
Default Re: I'm guessing this is a code violation???

Jim I think you've got it right somebody ripped off the wire and the electrician did not want to rerun the home runs again. The NEC allows splices in a panel to fill up to 75% of the cross-sectional area as long as the wires terminate in the panel and are not just feeding through 312-8 NEC. Looks bad but legal.
Reply With Quote
  #15  
Old 11/20/08, 11:03 PM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 549
Default Re: I'm guessing this is a code violation???

Quote:
Originally Posted by jfarsetta View Post
Wires can be spliced in a panel, providing that the termination is inside the panel. So long as adequate space exists, it is absolutely permissible.
...just not used as a junction. Junctions are not permitted.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage/house fire door Steven C. Meyer General Inspection Discussion 15 2/5/08 7:06 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM


All times are GMT -4. The time now is 3:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts