  #16  
Old 4/16/06, 5:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: IMO Shuretest VD is weak

Quote:
Originally Posted by dandersen
Is the % voltage drop the issue, or is voltage less than 108 vac with a high % drop?
The drop is the issue. As I stated, excessive VD is an indication of high resistance in the circuit. Resistance translates into heat (that's the reason for the short load duration).

If nothing else, it's an "efficiency" issue.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #17  
Old 4/16/06, 5:15 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: IMO Shuretest VD is weak

Doug

Do you thing VD is a problem?

If it is I can see Shuretest stock going up

I might even buy one

Right now it is my heat gun an the Fluke if as you say you feel you need to check for a VD.

I am also thinking of an additional test for true load testing since the EC in my area do not do it. I have done this type of testing in the Telecom and USN so it is not a problem but would have to buy some equipment and contact my insurance co to see if I could afford the general liability inc

Happy Easter

rlb
Reply With Quote
  #18  
Old 4/16/06, 5:27 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: IMO Shuretest VD is weak

Jeff

Your thoughts


When a device (HVAC etc.) is feed low voltage it will draw more current like a drunken sailor. This will build up more heat in the device and will shorten its live.

I do agree that the two are tied together. And IMO the voltage is the issue not the %. I will give you points for your side -- the NEC keeps talking about % so you must be right.

Is there anyone out there that thinks that the NEC cares about voltage under load??

I know that in my past it was voltage and current the % was not the problem

Sometimes I know I am dating my knowledge but the laws of Physics and basic electricity should not change

Do I sound like I know what I am saying? If I do DO NOT CALL ME son of JOE

Trust me I will change my name an log into NACHI as someone else

rlb
Reply With Quote
  #19  
Old 4/16/06, 6:05 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: IMO Shuretest VD is weak

Smoke test

Here is what I have in my brain as a problem

We test the ckt and it looks OK

Load it down and the weak point starts to heat up. Resistance and VD starts to go up real fast. The device (Stove - HVAC) starts to draw even more current causing the problem to get even worse.

Can not the industry come up with a testing MOP and equipment that will show the problems (small $$) or am I looking for a problem that is only in my house.

I think suretest is leading us down a path that if something goes wrong the HI gets it in the court case when the house burns down and the kid is dead but suretest does not

We and suretest says it is OK

Yes, I have too much time to kill (TV is bad and all projects for today are done)

Just looking for thoughts

Maybe Suretest could check in

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Collateral Damage – Weak Real Estate Market & Mortgage Meltdown jburkeson1 Miscellaneous Discussion for Inspectors 0 4/12/07 4:24 PM
Texas TRCC weak says Dallas Morning News rdawes Miscellaneous Discussion for Inspectors 1 10/18/06 12:10 PM
Basic Electrical Theory Questions- EASY pabernathy Electrical Inspections 41 7/7/06 10:53 AM


All times are GMT -4. The time now is 3:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts