  #1  
Old 10/22/08, 4:47 PM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Impedance testing

I have been using this “wiggy” for the past couple years ever since AFGI circuits and Ketik water service pipe was approved in Edmonton and area. I visually inspect the panel bonding to the copper water service pipe when copper is used but last week (I do not know why, maybe instinct) I decided to measure the ground impendence on the wall socket next to the main electrical panel. I was shocked (no pun intended) to find 8.04 ohms resistance on the ground. According to the literature that comes with the Ideal meter 0.25 ohms is max for sensitive electronic equipment and 1 ohm for all other uses. This prompted additional testing. I found 9.08 ohms and 4,05 ohms on two addition circuits.
Has anyone else found this?
Should we do more ground impedance testing?
Do you think this procedure be added to the SOP?



Vern Mitchinson_CCHI_CMI
Registar
AlbertaNACHI
International Association of Certified Home Inspectors of Canada
Reply With Quote
  #2  
Old 10/22/08, 4:53 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Impedance testing

Isn't impedance testing done when you have a hard time fathering children?
Reply With Quote
  #3  
Old 10/22/08, 5:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Impedance testing

Impedance testing is done routinely in the UK, but not so much in North America. I absolutely would not rely on any field ground impedance measurements unless the instrument had a current calibration certificate. The margin of error on an uncalibrated instrument (or an instrument not specifically designed with impedance measurements in mind) can be greater than than the entire range of typical ground impedance measurements encountered in the field.
Reply With Quote
  #4  
Old 10/24/08, 11:19 AM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Re: Impedance testing

IDEAL SURETEST CIRCUIT ANALYZERS




Larger picture

The IDEAL SureTest™ electrical circuit analyzer with arc fault (AFCI) and ground fault circuit interrupter (GFCI) detects arcing faults in electrical circuits that could cause fires

ITEM #: ST61165
$319.95
I'm using this meter to do the testing and it is accurate.
Has anyone else found this?
Should we do more ground impedance testing?
Do you think this procedure be added to the SOP?



Vern Mitchinson_CCHI_CMI
Registar
AlbertaNACHI
International Association of Certified Home Inspectors of Canada
Reply With Quote
  #5  
Old 10/24/08, 4:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Impedance testing

Quote:
Originally Posted by vmitchinson View Post
I'm using this meter to do the testing and it is accurate.
Maybe it is, but you can't prove it without current calibration.
Reply With Quote
  #6  
Old 10/24/08, 4:43 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Impedance testing

Quote:
Originally Posted by jbraun View Post
Isn't impedance testing done when you have a hard time fathering children?
No, Jim...you're thinking of "impudence".

I know it's hindered me on several occasions...back in the day.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 10/24/08, 10:29 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Impedance testing

Vern

Yes this should be part of sop

Calibration is a question but not a big one -- one resistor that is checked when the meter is just calibrated or new can be checked to be sure it is OK plus the mfg requirements is OK

I started finding ground problems with my eye - then started using a good meter that is 20 years old

I draw the line when neutral and ground are at 0 to .25 ohm (boot leg ground) and neutral to ground greater than 1 ohm

At the breaker box where the neutral and the ground are common .25 is my limit

If I can find a real ground in the home like a water pipe and a ground on a socket that are in reach of my meter leads (kitchen - bath room - laundry - copper pipes) 2 ohms is my limit

Remember that 25 ohm is the magic number for a good earth ground

My home is very much less because of a what I have done to make it so.

How to measure the 25 ohms is outside the SOP because of a lot of BS about how to do it with out spending a lot of $$ on meters and time

Remember that most of our inspections are by eye and time is real short to get an inspection done

A broken or missing ground is easy and fast - A bad one is probably a bad connection that one can wiggle with ones hand

The use of a meter takes time and extra knowledge but I think it should be part of an inspection esp with Florida being the electrical storm area that it is

Trust me after the amount of $$ that I have lost because of electrical storms - good testable grounding is the word

Please understand that DC resistance and AC impedance are not the same and is another thread

Lighting likes low AC impedance and can not be SOP - Too much knowledge training and equipment

Good thread

rlb
Reply With Quote
  #8  
Old 10/24/08, 10:39 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Impedance testing

Marc

What is this BS?

What is "current" calibration?

One day - week - year - etc. -- and who can do the calibration? - like I can do it myself if I can trace my standards back to the national bureau of standards which is easy

Remember we are only checking one wire for a good connection

rlb
Reply With Quote
  #9  
Old 10/24/08, 10:41 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Impedance testing

Marc

The proof can be done with a calibration "CHECK" after the test

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture in slabs mcyr Structural Inspections 7 8/20/07 7:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 10:26 PM
Is this for real? hgordon IAC2 Indoor Air Forum 47 10/30/06 9:31 PM
Arizona, one day mold cert dbucknavich General Inspection Discussion 4 6/26/06 9:32 PM