Default Improper wire jumper wire

Is it okay to use two different wire sizes on a jumper to a breaker? The breaker is a 20amp with #12 wire on the circuit. There is a jumper wire connected to the #12 wire that is a #14 wire which is connected to the breaker. I believe you need to correct wire size. One electrician told me it was okay and the other said #12 wire should be used on the jumper. Looking for your opinions
Reply With Quote
Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/25/12, 8:39 AM
Terry a. Russell, jr Terry a. Russell, jr is online now
InterNACHI Member
 
Join Date: Jan 2011
Location: hazel park ,mi
Posts: 57
Default Re: Improper wire jumper wire

should be a #12




Terry Russell
serving all of southeast mi
248-722-4288
www.blessedassurancehi.com
Reply With Quote
  #3  
Old 1/25/12, 8:40 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Improper wire jumper wire

The OCPD needs to be smaller or equal to the size listed in 240.4(D) of the NEC. Except for certain installations (not this one) #14 can not be protected at 20 amps.

Quote:
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied.
(1) 18 AWG Copper. 7 amperes, provided all the following conditions are met:
(1) Continuous loads do not exceed 5.6 amperes.
(2) Overcurrent protection is provided by one of the following:
a. Branch-circuit-rated circuit breakers listed and marked for use with 18 AWG copper wire
b. Branch-circuit-rated fuses listed and marked for use with 18 AWG copper wire
c. Class CC, Class J, or Class T fuses
(2) 16 AWG Copper. 10 amperes, provided all the following conditions are met:
(1) Continuous loads do not exceed 8 amperes.
(2) Overcurrent protection is provided by one of the following:
a. Branch-circuit-rated circuit breakers listed and marked for use with 16 AWG copper wire
b. Branch-circuit-rated fuses listed and marked for use with 16 AWG copper wire
c. Class CC, Class J, or Class T fuses
(3) 14 AWG Copper. 15 amperes
(4) 12 AWG Aluminum and Copper-Clad Aluminum. 15 amperes
(5) 12 AWG Copper. 20 amperes
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
jumper wire gmartin2 Electrical Inspections 5 1/23/09 12:45 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 8:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts