Default Inappropriate circuit breakers (?)

Two of my recent inspections had Square D panels that had dual HOMT circuit breakers that did not appear to be properly seated, nor (as best I could tell from the rating tag) appropriate for the panels, for which only HOM circuit breakers appeared to be appropriate. The breakers in question are on the top right of the panel. See pics for additional data.

I hedged a bit on my write-up, and said the HOMT circuit breakers appeared to be mismatched and poorly seated, and recommended they consult a licensed electrician regarding this.

So, are these circuit breakers acceptable?

Also, do any of you have freakishly similar findings come up within a short period? For example, this year I had a run of several inspections in which the same mid 1980s Bryant furnace model was present.

(Anyone spot the other obvious potentially serious defect in pic #2?)
Attached Thumbnails
inappropriate-circuit-breakers-2007_12210668-trim-breaker-legend.jpg   inappropriate-circuit-breakers-2007_12210664-trimmed-breakers.jpg   inappropriate-circuit-breakers-2007_12210675_260_1.jpg   inappropriate-circuit-breakers-2007_12210674-ed-trim.jpg   inappropriate-circuit-breakers-2007_12210674-ed-model.jpg  

Reply With Quote
  #2  
Old 12/29/07, 8:09 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inappropriate circuit breakers (?)

WOW! I cannot believe someone left a panel like that!

Yes, they are the proper breakers....in a HOM panel that will accept them. That panel does NOT.
Reply With Quote
  #3  
Old 12/29/07, 8:29 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Inappropriate circuit breakers (?)

As expected. Thanks, SP. I take it you caught the other defect ...
Reply With Quote
  #4  
Old 12/29/07, 8:30 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Inappropriate circuit breakers (?)

Good eye, Frank...I'm surprised they didn't hammer them in.

Always good to look closer when one sees retail price tags, too.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 12/29/07, 8:33 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Inappropriate circuit breakers (?)

Yah, Larry, I didn't see any hammer marks ... though Curly might have taken a few from Moe during the installation ...
Reply With Quote
  #6  
Old 12/30/07, 1:28 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inappropriate circuit breakers (?)

I almost took a double look but quickly relized this is a correct breaker but this panel box is not listed to take the twinner breaker at all.

that breaker box only listed for fullsized breaker only.

so that is a good catch.

BTW , IIRC most SqD HOMELINE breakers with twinner verison do have a notched or oversloped in front of the breaker so that way it will not seat in the breaker box fully at all [ the approved breaker box that can take the twinner useally are notched bussbar.]

Merci, Marc

P.S keep in your mind the QO series are diffrent on this matter the latter one do have a cam on rear mounting clip.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 11:40 AM