Default Incorrect Wire?

Here are a couple of pic's from todays inspection.
There is a 40 amp double pole breaker, third on right, for the AC, that is wired using 12/2 romex? The wire for that size of breaker is to small correct? But the amps on the ac says, 23.6amp.

The second pic shows oxidation on the lead feeding the panel is this an issue that should be called out?

[ATTACH]incorrect-wire-corosin.jpg[/ATTACH]
Attached Thumbnails
incorrect-wire-double-pole.jpg  



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 7/17/08, 10:19 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 739
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Incorrect Wire?

AC loads do not use the same wire sizes as regular branch circuits. The breakers are sized for the starting current. The wire is sized for the run current. To verify proper wire sizes you need to look at the nameplate to check the minimum circuit size.
Reply With Quote
  #3  
Old 7/17/08, 10:37 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Jim
The minimum is 23.6 amps



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 7/17/08, 11:02 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Hi Gary,

I can't comment on the wire guage (but that ain't a 12/2) it many be a 12awg, but the real issue is that the compressor is I think an upgrade from the homes original one, and the new one requires less amps than the original, if that is the only disconnect for the AC then it is "over fused" however it may have an outside disconnect rated lower.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 7/17/08, 11:21 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Gerry
It does have a pull fuse at the unit outside.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 7/17/08, 11:26 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Gerry
It does have a pull fuse at the unit outside.
What is that rated at??

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 7/17/08, 11:29 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

30amps. Buy isn't that for when the unit is being serviced? That way the power can be disconnected at the unit. It doesn't trip?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 7/17/08, 11:40 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
30amps. Buy isn't that for when the unit is being serviced? That way the power can be disconnected at the unit. It doesn't trip?
Gary, it's still a fuse isn't it??? that will blow at 30 amps, well before the breaker would trip wouldn't it??

Do you have a picture of the data plate you can post?

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 7/18/08, 6:01 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

What about the first pic with the oxidation? Is this an issue that should be called out? Could that connection become a problem in the furture?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 7/18/08, 6:53 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Gerry
The wire being used for the AC is 12/2 awg. It is stamp on the outside of the wire. Wouldn't this wire be under sized for the breaker,40amp, even though the min. amps is 23.6 on the boiler plate?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #11  
Old 7/18/08, 7:58 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Gerry
Quote:
Originally Posted by nbhi
The wire being used for the AC is 12/2 awg. It is stamp on the outside of the wire. Wouldn't this wire be under sized for the breaker,40amp, even though the min. amps is 23.6 on the boiler plate?



When dealing with any motor load the breaker or fuse MUST be able to let the motor start.
The fuse or breaker is installed for the SOLE purpose of opening in the event that the hot wires get shorted to each other or to some part of the metal that encloses them.

The AC unit will have an integral overload device that is responsive to motor current. This integral over load will open in the event that the unit starts overheating and also protects the conductors that are installed to the unit.
Reply With Quote
  #12  
Old 7/18/08, 9:40 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

So Mike, The wire being smaller than the breaker, which is 40 amps double pole, is ok, since the amps on the boiler plate,ac, is 23.6amps?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #13  
Old 7/18/08, 9:51 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Gerry
The wire being used for the AC is 12/2 awg. It is stamp on the outside of the wire. Wouldn't this wire be under sized for the breaker,40amp, even though the min. amps is 23.6 on the boiler plate?
Gary, as others have said you really need the manufacturers installation instructions. A 12awg is rated for 25amps when starting a motor (a compressor is a motor) If the Full load amp figure is 23.6amps for that compressor it should normaly run at about 75% of that or about 18 amps, the breaker size should also be that recommended by the manufacturer (the 30 amp outside disconnect MAY be correct).

The reason I am saying I doubt that the conductors are a 12/2 is that both the wires feature black insulation, I have never seen a 12/2 where both conductors are black. That is not to say that the wires are not 12awg, I just don't think that that is a 12/2 cable assembly.

Do you have either a picture of the data plate or the model number, the former should list the conductor and OCPD ratings, or if you have the model # you should be able to find a copy of the installation instructions on the web.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #14  
Old 7/18/08, 10:49 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Gerry
They colored the white wire black.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #15  
Old 7/18/08, 11:28 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Gerry
They colored the white wire black.
Ah, OK that I couldn't see. Normally they just put a piece of tape on it to indicate an ungrounded conductor.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 5:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts