Quote:
|
|
#17
|
||||
|
||||
|
Mike
I want to be clear on this. 100amps on startup is ok for 12/2 awg. "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#18
|
||||
|
||||
|
Quote:
Without providing a label or a model number an definitive answer cannot be given. 100 Amp on start is not the issue. The trip curve of the protection device and the length of time the current is actually at that level are. hth He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#19
|
||||
|
||||
|
Quote:
Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#20
|
||||
|
||||
|
Quote:
Though I would think the LRA would be more accurate a number. He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#21
|
||||
|
||||
|
M# HS25-411-1P
S#5193E36753 Lennox "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#22
|
||||
|
||||
|
Hi Gary,
Here the installation instructions Incvluding 18 amp RLA and 40 amp breaker http://hvacpartsshop.net/HS25_Series.pdf Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#23
|
||||
|
||||
|
Gerry
Thanks, do you have this and anymore sites saved, water heater, etc? If so, is there a way I can get them from you? I searched and couldn't find this info. Thanks again for your help. "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#24
|
||||
|
||||
|
Quote:
BTW a quick tip is just Googling the series rather than the whole model # e.g. I just google HS25, found it real fast. Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#25
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If you Google, try these guys, send them a buck or two if you like it.
http://scroogle.org/cgi-bin/scraper.htm It is Google without the Ebay ad, the Amazon ad and a dozen others. They also don't set and track cookies. Nuff said? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 10:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 4 | 3/25/07 11:41 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 2:08 AM |