Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
So Mike, The wire being smaller than the breaker, which is 40 amps double pole, is ok, since the amps on the boiler plate,ac, is 23.6amps?
This is correct. The AC unit will pull around 18.88 amps running but will need to pull around 100 amps in order to start. The trip curve of a 40 amp breaker will allow the AC unit to start and the integral over load will protect the unit and conductors from overload in the event something were to go wrong with the compressor.
Reply With Quote
  #17  
Old 7/18/08, 2:34 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Mike
I want to be clear on this. 100amps on startup is ok for 12/2 awg.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #18  
Old 7/18/08, 3:43 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,556
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Mike
I want to be clear on this. 100amps on startup is ok for 12/2 awg.
Gary,
Without providing a label or a model number an definitive answer cannot be given.

100 Amp on start is not the issue. The trip curve of the protection device and the length of time the current is actually at that level are.

hth



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #19  
Old 7/18/08, 3:56 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Mike
I want to be clear on this. 100amps on startup is ok for 12/2 awg.
where the heck did the 100amps come from?

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #20  
Old 7/18/08, 4:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,556
Default Re: Incorrect Wire?

Quote:
Originally Posted by gbeaumont
where the heck did the 100amps come from?

Gerry
Post #16 by Mike Whitt.

Though I would think the LRA would be more accurate a number.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #21  
Old 7/18/08, 6:44 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

M# HS25-411-1P
S#5193E36753
Lennox



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #22  
Old 7/18/08, 7:50 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Hi Gary,

Here the installation instructions Incvluding 18 amp RLA and 40 amp breaker

http://hvacpartsshop.net/HS25_Series.pdf

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #23  
Old 7/18/08, 8:13 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Incorrect Wire?

Gerry
Thanks, do you have this and anymore sites saved, water heater, etc? If so, is there a way I can get them from you? I searched and couldn't find this info. Thanks again for your help.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #24  
Old 7/18/08, 8:21 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Incorrect Wire?

Quote:
Originally Posted by nbhi
Gerry
Thanks, do you have this and anymore sites saved, water heater, etc? If so, is there a way I can get them from you? I searched and couldn't find this info. Thanks again for your help.
I just googled it, I'm a realy good googler though

BTW a quick tip is just Googling the series rather than the whole model # e.g. I just google HS25, found it real fast.

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #25  
Old 7/18/08, 11:55 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Incorrect Wire?

If you Google, try these guys, send them a buck or two if you like it.

http://scroogle.org/cgi-bin/scraper.htm

It is Google without the Ebay ad, the Amazon ad and a dozen others.
They also don't set and track cookies. Nuff said?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 8:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts