Default Inexpericense will get you KILLED

This was from this morning see the male plug hanging by the middle screw hole on the dead front. My 40 years of experience working high voltage HVAC saved my life today. I treat all electrical as if it has power applied even male plugs when in see them going into a panel.

This apparently was used last winter for a backup generator to back feed the main panel. The dumbA** just unplugged from the generator and left everything connected and when the power came back on the male plug was still hot no telling how long it has been hanging there. I can just picture someone grabbing that male plug to move it out of the way



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 10:15 PM..
Reply With Quote
  #2  
Old 10/15/07, 5:00 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Inexpericense will get you KILLED

Generator was running?

tom

P.S. Since I have a knack for finding energized junction boxes, I went out and got EH rated shoes.

Last edited by tdietrich1; 10/15/07 at 5:05 PM..
Reply With Quote
  #3  
Old 10/15/07, 5:02 PM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,122
Default Re: Inexpericense will get you KILLED

Charley, thanks for sharing, and I'm glad you're still with us . . . I'm sure it will help many of us to be always remember to be careful and trust nothing when it comes to electricity.



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."
Reply With Quote
  #4  
Old 10/15/07, 5:08 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inexpericense will get you KILLED

Quote:
Generator was running?
No not since the last ice storm over a year ago



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 10/15/07, 5:12 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by tdietrich1
Generator was running?

The bottom left breaker looks like the generator input point.
The cable shown in the picture most likely goes into the wall under the pictured area and into that breaker.

A 30 amp female outlet is needed in the wall to obtain a "poor mans generator hookup" not a long hot cable.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 10/15/07, 5:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inexpericense will get you KILLED

Th
Quote:
e bottom left breaker looks like the generator input point.
The cable shown in the picture most likely goes into the wall under the pictured area and into that breaker.
That is correct there was a A/C type pull out disconnect just out of the picture below the panel that is what made me check for power.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 10/15/07, 5:24 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inexpericense will get you KILLED

Charley, may I please use those photos? They are GREAT example to the idiots who use these suicide cords and how unsafe they are.

All I ever hear is "I'll be careful........"
Obviously someone was NOT so careful!
Reply With Quote
  #8  
Old 10/15/07, 5:43 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by Speedy Petey
Charley, may I please use those photos? They are GREAT example to the idiots who use these suicide cords and how unsafe they are.

All I ever hear is "I'll be careful........"
Obviously someone was NOT so careful!
Go for it by all means



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 10/15/07, 6:28 PM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,122
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by cbottger
That is correct there was a A/C type pull out disconnect just out of the picture below the panel that is what made me check for power.
Do you have a picture of the pull-out? I've learned much from this post, thanks!



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."
Reply With Quote
  #10  
Old 10/15/07, 6:36 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by wchris1
Do you have a picture of the pull-out? I've learned much from this post, thanks!
For example...

http://www.sealhardware.com/detail.asp?sku=2264828



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 10/15/07, 6:43 PM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,122
Default Re: Inexpericense will get you KILLED

Thanks Larry! I was thinking along the line the pullout being the cable itself was in the wall/on the wall somehow, thanks for the clarification.



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."

Last edited by wchris1; 10/15/07 at 6:46 PM..
Reply With Quote
  #12  
Old 10/15/07, 7:05 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inexpericense will get you KILLED

Charley,

Your to mean to be killed by mear electricity! It would take the Hoover dam full electrical output to send you to the grave! That Homeowner special would only have tickled you a bit!


Seriously electricity is dangerous and needs to be respected, can see it cant smell it and its sneaky.

Thanks for sharing,
Curt
Reply With Quote
  #13  
Old 10/15/07, 7:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inexpericense will get you KILLED

Exactly why NACHI needs to ensure everyone is aware of electrical issues and hazards...and frankly why educators do what we do.....hoping to keep you safe and going home at night....safe.



Paul W. Abernathy
Reply With Quote
  #14  
Old 10/15/07, 8:14 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by cbottger
This was from this morning see the male plug hanging by the middle screw hole on the dead front. My 40 years of experience working high voltage HVAC saved my life today. I treat all electrical as if it has power applied even male plugs when in see them going into a panel.

This apparently was used last winter for a backup generator to back feed the main panel. The dumbA** just unplugged from the generator and left everything connected and when the power came back on the male plug was still hot no telling how long it has been hanging there. I can just picture someone grabbing that male plug to move it out of the way

Thanks for sharing Charley!! I will definitely keep on eye out for connections like this in the future. And I'm happy to hear that you "Survived" the Inspection.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #15  
Old 10/15/07, 8:51 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Inexpericense will get you KILLED

Quote:
Originally Posted by Speedy Petey
Charley, may I please use those photos? They are GREAT example to the idiots who use these suicide cords and how unsafe they are.

All I ever hear is "I'll be careful........"
Obviously someone was NOT so careful!
MEE TOO? PLEEEASE?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home inspection killed multiple sales. gromicko Miscellaneous Discussion for Inspectors 24 1/9/07 12:45 PM
We are going to get killed!! jferry Miscellaneous Discussion for Inspectors 9 1/4/07 7:28 PM
Steve Irwin "Crocodile Hunter" Killed by Stingray wforsyth Miscellaneous Discussion for Inspectors 77 10/28/06 4:22 PM
Mould Killed 200> ccrooker Canadian Inspectors 0 10/10/06 2:13 PM


All times are GMT -4. The time now is 4:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts