Old 10/1/06, 10:14 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Input please

This is the main entrance/laundry area. I would appreciate knowing how you guys would call this out. The house is 90+ years.

Thanks.
Attached Thumbnails
input-please-img_3554.jpg   input-please-img_3557.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 10/1/06, 10:29 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Input please

Hi Scott,

The unprotected NM (Romex) wiring is obviously a problem, other than that I see no issues.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 10/1/06, 10:31 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Input please

Thanks Gerry, I agree, but what would you recommend doing to remedy it? even though we do not make those recommendations.

Thanks.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #4  
Old 10/1/06, 10:39 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Input please

Steel protection around the cables?

I would also be concerned about the close proximity to the water (washing machine) and the lack of accessability.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 10/1/06, 10:40 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Input please

Looks like a typical 90 year old set up in a home that has not been upgraded in years and years and years. The electrical cables could be protected very easily.
Reply With Quote
  #6  
Old 10/1/06, 11:13 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Input please

The proximity to water is a non-issue. The accessibility is.
The protection of the cables is also an issue.


Like Ray says, this is typical of houses of this era. Before H-Is stuff like this never got a second look and was almost never a problem.
Thing is folks over the years added and changed things. IMO the laundry should have never gone there. Maybe they had no choice? Who knows.
Unfortunately, with the advent of H-Is the current owners of houses like this get burdend with correcting 90 years of mistakes (for lack of a better word).

A wooden box framework covering around the wires would be a perfect protection and also look good. Like was said though, you are not in the position of making this type of suggestion.
Reply With Quote
  #7  
Old 10/1/06, 11:16 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Input please

Quote:
Originally Posted by sfalvey
Thanks Gerry, I agree, but what would you recommend doing to remedy it? even though we do not make those recommendations.

Thanks.
I would like to know if you opened the panel?And if so how?


Mario





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #8  
Old 10/1/06, 11:26 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Input please

Quote:
Originally Posted by Speedy Petey
The proximity to water is a non-issue. The accessibility is.
The protection of the cables is also an issue.


Like Ray says, this is typical of houses of this era. Before H-Is stuff like this never got a second look and was almost never a problem.
Thing is folks over the years added and changed things. IMO the laundry should have never gone there. Maybe they had no choice? Who knows.
Unfortunately, with the advent of H-Is the current owners of houses like this get burdend with correcting 90 years of mistakes (for lack of a better word).

A wooden box framework covering around the wires would be a perfect protection and also look good. Like was said though, you are not in the position of making this type of suggestion.
I would make that suggestion to current homeowner Speedy.
.
Also the ONTARIO ELECTRICAL SAFETY CODE states 1 meter free space in front of panel.I know we are not doing a code inspection ,but I would not open panel with laundry in front of panel.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #9  
Old 10/1/06, 11:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Input please

Peter,

While the HI is not in the position to do so...a good HI would make the suggestion of boxing it in...which is what I would suggest and to be honest with you the client should trust in the HI and that suggestion if anything "Verbal" at best.....is a suggestion in their best interests.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 10/3/06, 9:35 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Talking Re: Input please

Quote:
Originally Posted by sfalvey
This is the main entrance/laundry area. I would appreciate knowing how you guys would call this out. The house is 90+ years.

Thanks.
Defects show the lack of proper working spaces about the electrical equipment not in compliance with the NH State Laws and there is evidence of work done by non licensed and unqualified persons.
Reply With Quote
  #11  
Old 10/3/06, 2:27 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Input please

Thanks for the input guys, and yes, I did open the panel box. I did notice there did not appear to be any grounding to plumbing or on the outside meter box no ground wire running anywhere, let alone to a rod in the ground. And the ddrip loop that was almost horizontal.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #12  
Old 10/3/06, 3:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Input please

Before you condemn the electrician you would have to know when they bought the washing machine
Some could argue the washing machine was portable and was just "saving" the working space for you.
The shelf above it is more troubling from a working space aspect.
I would agree the romex was subject to damage but the fix is pretty easy. Just nail up a 1x2 on each side and cover it with plywood.
Reply With Quote
  #13  
Old 10/3/06, 3:37 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Input please

Actually there are two machines here. They are not pictures of the same space so it is the dryer that is in front of the panel.
Reply With Quote
  #14  
Old 10/3/06, 5:22 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Input please

Quote:
Originally Posted by Greg Fretwell
Actually there are two machines here. They are not pictures of the same space so it is the dryer that is in front of the panel.
It is the same space, the first picture is the washing machine, to the left, the second picture, is the dryer and Breaker panel.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #15  
Old 10/3/06, 5:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Input please

Scott,

I am like Greg in the observation.....both seem to have a wall to the right of them so they don't look like the same locations.

While the clearance is a issue and would not be accepted today I am not sure you can do much on it now other than note it and why it is a safety concern.

As for the NM Cables and such...I would suggest a protective divider be installed around them ( ie: wood and such ) and note why it is a recommendation.

I would do as greg suggests and understand the home is 90 years old as well. On the inside of the panel issues note as you should in your report those that concern you or lack of proper installation and that is about all I would report on in this case.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need some input... dlawrence General Inspection Discussion 24 9/14/07 12:47 PM
Input please.... rhumphries Misc. Discussion 0 2/16/07 10:24 AM


All times are GMT -4. The time now is 9:07 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts