I have never seen a downspout run into the interior of the home. Next to the main is a bad idea.

Beside the downspout. I noted these issues.

FPE. Improper labeling. No isolation at sub, Undersized 10 gauge to 40 amp A/C breaker that the exterior data specified 35 amps. Thanks Paul!!

No exterior ground.

The splices in the sub where questionable.

Any other comments or concerns.

The downspouts in the house are classic. I love these old houses. Check out my post for the other pics of the interior spouts.

Thanks

Dave
Attached Thumbnails
inside-gutter-not-you-think-88806-bedford-052-small-.jpg.jpg
Views:	70
Size:	58.2 KB
ID:	8014   inside-gutter-not-you-think-88806-bedford-051-small-.jpg.jpg
Views:	52
Size:	48.9 KB
ID:	8015   inside-gutter-not-you-think-88806-bedford-053-small-.jpg.jpg
Views:	63
Size:	61.0 KB
ID:	8016   inside-gutter-not-you-think-88806-bedford-049-small-.jpg.jpg
Views:	56
Size:	71.6 KB
ID:	8017  
Reply With Quote
  #2  
Old 12/28/06, 6:57 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inside gutter (Not what you think)

Dave,

You are getting QUITE good at the electrical issues....very impressed !

The issue in my mind with this is the clearance issues.......and the foriegn system within MY electrical dedicated space.( Clarrification..( Thanks Pierre..lol... ) I am refering to a space I can't see in this image...above it or below it...but alas I just can't see that in this image.)

Now......that metal gutter ( if it is metal ) is in a position that it COULD become " electrically energized " so......while chances are the client will not remove it......It would not HURT to be suggested it be BONDED to the GEC system......just a thought....

Good call....on the panel.....that one could have tricked a novice......yep...sure enough the panel on the right becomes a "Remote Distribution Panel" and would need to meet the items you stated.

Are their any bushings on the service conductors entering into the panel?

Tricky that one.......the main panel is complying with the 6 or less......and feeding the panel on the right........very nice.

You are doing well..."Grasshopper"...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 12/29/06 at 1:03 AM..
Reply With Quote
  #3  
Old 12/28/06, 7:01 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inside gutter (Not what you think)

However...I have to admit Dave......I can't follow those conductors very well in the first panel......is the panel on the RIGHT being FED from the OCPD on the left......just to be sure?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 12/28/06, 7:46 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,553
Default Re: Inside gutter (Not what you think)

Quote:
Originally Posted by pabernathy
However...I have to admit Dave......I can't follow those conductors very well in the first panel......is the panel on the RIGHT being FED from the OCPD on the left......just to be sure?
The SEC attached to the main 100 amp. The 50 amp at the right was for the stove. These are the wires that are splice in the sub. Home owner is using stove as gas so at this time the 50 amp isnt being used, The new owner may use the stove 220.

The other 40 amp is the dryer. The sub feeds are attaced at the main lugs. Am I calling this right oh wise one? The home owner or whom ever improper labeled the 40 amp dryer breaker as sub feed.

The 40 amp in the sub was 10 gauge and dedicated for the A/C. Thanks to you I now know that I need to read the data plate on the A/C unit.
Reply With Quote
  #5  
Old 12/28/06, 7:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inside gutter (Not what you think)

I would say you are doing a fine job DAVE....keep up the GOOD work and remember...never stop learning...I learn something new everyday of my life.

Ahhh...I will let you call them SUB-PANELS if you would like...lol...but if you want to be a GURU....you will need to call them "Remote Distribution Panels" and I will give you a GOLD STAR

OPPS....not a GOLD STAR.....but a GREEN BOX...even better...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 12/29/06 at 12:22 AM..
Reply With Quote
  #6  
Old 12/29/06, 12:24 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inside gutter (Not what you think)

Paul

The "Dedicated Equipment Space" only pertains to the "footprint" space of the panel equipment above and below the equipent, not to the sides of the equipment.
Reply With Quote
  #7  
Old 12/29/06, 12:32 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inside gutter (Not what you think)

Pierre,

I could not see above it or below it.....so I was making sure if this was an issue to be aware of it...as the image was limited and grasping at straws since I can't see above it or below it in that image.

lol...now you know I know that.........come on now Pierre...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 12/29/06, 12:36 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Inside gutter (Not what you think)

I am more concerned with the fact this panel does not appear to be installed correctly for a "Remote Distribution Panel " as you can see from the Bus Bar in the panel picture.

However I think Dave did a wonderful job finding those things we can't see well from the image...what do ya think.....We give Dave a Green Box for it?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustibles inside fireplace? bmargiotti General Inspection Discussion 8 11/19/07 12:41 PM
Gutter advice dmacy Exterior Inspections 2 11/13/07 12:22 PM
gutter downspout to basement drainage system David Paterson Exterior Inspections 2 12/18/06 7:27 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM


All times are GMT -4. The time now is 12:43 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts