Default Inspecting AC equipment on a roof top

Contact me if you want any Code advice

Last edited by jtedesco1; 1/22/08 at 8:53 AM..
Reply With Quote
  #2  
Old 1/20/08, 6:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Yes, there appears to be a track loader on the roof.

Disconnect mounted on an equipment panel designed to be removed.
Reply With Quote
  #3  
Old 1/20/08, 6:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Inspecting AC equipment on a roof top

Joe,

Why not post this over in commercial where it belongs?
Reply With Quote
  #4  
Old 1/20/08, 6:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by mlarson
Why not post this over in commercial where it belongs?
If I had to guess, I'd say it's because rooftop equipment is pervasive in the southwest on single family dwellings too.
Reply With Quote
  #5  
Old 1/20/08, 6:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by Marc D. Shunk
If I had to guess, I'd say it's because rooftop equipment is pervasive in the southwest on single family dwellings too.
Okee Dokee I'm just a Northern boy.

Looks commercial to me anyway.
Reply With Quote
  #6  
Old 1/20/08, 6:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by mlarson
Okee Dokee I'm just a Northern boy.

Looks commercial to me anyway.
Sure, the pic is, but the spirit is the same. I would almost bet that if he had a pic of a resi rooftop equipment hazard, that would have been used instead.
Reply With Quote
  #7  
Old 1/20/08, 6:36 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Inspecting AC equipment on a roof top

Marc how do you know from the pic it is designed to be removed?
Trac loader?
Please provide better explanations.with out code speak.
Reply With Quote
  #8  
Old 1/20/08, 6:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by relliott
Marc how do you know from the pic it is designed to be removed?
I am famaliar with that particular rooftop unit. Plus, you can barely make out the 5/16" headed sheet metal screws along the bottom edge of that panel that facillitate its removal. Any panel on an HVAC piece of equipment that is designed to be removed, whether or not it will ever actually be removed in the future, is not permitted to support the disconnect.
Reply With Quote
  #9  
Old 1/20/08, 6:59 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inspecting AC equipment on a roof top

Marc I don't see any power source (conduit) to the disconnect did they bring it from inside the curb package into the unit cannot tell from the pic. Perhaps the install is not complete. Personally I would not have a problem with the location of the disconnect as all of the panels are removable it does not appear to block any future maint.

The units are to close together the one on the left would have to have the top removed to change out its compressor



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 1/20/08 at 7:02 PM..
Reply With Quote
  #10  
Old 1/20/08, 7:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by cbottger
Marc I don't see any power source (conduit) to the disconnect did they bring it from inside the curb package into the unit cannot tell from the pic. Perhaps the install is not complete.r
These units have some age on them, so I very much think the install is complete. Yes, it is becoming more and more common to bring the power in from underneath, through the interior of the unit and the associated curb kit. Seldom is this accomplished in a compliant manner.
Reply With Quote
  #11  
Old 1/20/08, 7:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by cbottger
Personally I would not have a problem with the location of the disconnect as all of the panels are removable ...
I feel the same way for the most part, but it remains a technical violation. I can't mount one there, but you can certainly say that it presents no hazard if someone does put a disconnect there if you want to.
Reply With Quote
  #12  
Old 1/20/08, 7:08 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by Marc D. Shunk
These units have some age on them, so I very much think the install is complete. Yes, it is becoming more and more common to bring the power in from underneath, through the interior of the unit and the associated curb kit. Seldom is this accomplished in a compliant manner.
Good to see you back where you been missed your professional attitude even thou I do like to Razz you occasionally



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 1/20/08, 7:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Inspecting AC equipment on a roof top

Quote:
Originally Posted by Marc D. Shunk
I feel the same way for the most part, but it remains a technical violation. I can't mount one there, but you can certainly say that it presents no hazard if someone does put a disconnect there if you want to.
I agree what bothers me is when they put them on the service panel to the interior wiring or the compressor area have seen them in that location.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 1/20/08, 7:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

For the most part, the only way to bring the feeder to the unit from within the confines of the curb is when the unit has a disconnect built into it from the factory. It's only been maybe the last 10 years that this has become a popular option.

That rooftop photo might also lack the required convenience receptacle within 50' of the units. I'm not sure if that's something you guys would ever consider calling out or not.
Reply With Quote
  #15  
Old 1/20/08, 7:25 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Inspecting AC equipment on a roof top

Within 25" of the equipment is where the GFCI receptacle is supposed to be located.

210.63

This was in NJ.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM


All times are GMT -4. The time now is 4:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts