Default inspection procedural checklist

how's this CHECKLIST for inspecting an electrical panel?

Any input?

Thanks, dudes.

Inspection procedural checklist for electrical panel (BOARD).doc



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
  #2  
Old 2/29/08, 2:20 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: inspection procedural checklist



Here it is so you don't have to open a WORD file:


INSPECTION PROCEDURAL CHECKLIST

for inspecting an electrical panel

  • Follow InterNACHI Standards of Practice
  • Wear personal safety protection, including glasses and gloves
  • Check adequate workspace
  • Panel must be readily accessible
  • Use proper inspection tools, including magnet handle, insulated screwdriver, and flashlight
  • Check adequate illumination at workspace
  • Measure height of main disconnect
  • Inspect cabinet front cover
  • Check for incorrect type of screws or missing screws at the cabinet front cover
  • Inspect panelboard
  • All disconnects must have specific identification
  • Check for inspection stickers and dates
  • Check for identified filler plates
  • Identify main overcurrent device
  • Determine size of service
  • Safe removal of cabinet front cover
  • No foreign objects or contamination inside cabinet
  • Check entrance conductors and lugs
  • Identification of grounded conductor
  • Check clamps, connectors, and bushings
  • No open knockouts permitted
  • Check for disconnected or loose conductors
  • Inspect main bonding jumper
  • Inspect main grounding electrode conductor (GEC)
  • Check for doubled neutrals
  • Check for doubled hot conductors
  • Identify any breakers that are not permitted by manufacturer
  • No white wires on breakers
  • Test GFCIs and AFCIs
  • No doorbell transformers inside cabinet
  • Check for loose equipment grounding conductor (EGC)
  • Check for ampacity or overfusing defects
  • No melted conductor insulation
  • No rust, corrosion, or water inside cabinet
  • No gaps between cabinet and wallboard greater than 1/8 inch
  • Check multiple cables in connectors
  • Check for damage to wires
  • Check for damage to insulation sheathing
  • Inspect for exposed live wires
  • Check identified handle ties
  • Read the label on the cabinet front cover
  • Identify product name and type of cabinet from label
  • Confirm amps and volts are identified on label
  • Inspect the panelboard diagram
  • Count maximum number of poles from the diagram
  • Confirm location of main bonding jumper
  • Identify twin or ½ breakers
  • In subpanel, confirm the grounds and neutrals are isolated or floating
  • Never leave exposed panelboard unattended
  • Replace cabinet cover correctly



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #3  
Old 2/29/08, 4:37 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Lots more here too!
Reply With Quote
  #4  
Old 2/29/08, 5:12 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Are the two of you brothers?

Sometimes you will find a white wire attached to a breaker such as for water heaters and air conditioners.

The requirement to reidentify was in the exceptions until the 1999 code cycle and even then wasn't enforced by all code officials.
Reply With Quote
  #5  
Old 2/29/08, 5:20 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

I'm curious why that list has "measure height of main disconnect"? I know what this is getting at, but it is not what it says.
Reply With Quote
  #6  
Old 2/29/08, 5:22 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: inspection procedural checklist

Thanks for the list .
I have saved it as a reminder.
Reply With Quote
  #7  
Old 2/29/08, 5:23 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: inspection procedural checklist

Mark I was curious about that too.
What off hand is the height requirment on the main dis-connect?
Reply With Quote
  #8  
Old 2/29/08, 5:33 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Quote:
Originally Posted by relliott
Mark I was curious about that too.
What off hand is the height requirement on the main dis-connect?
The highest disconnect (not main disconnect, could be any breaker) is not allowed to be over 6 feet, 7 inches off the deck or grade. Some panels are oriented with their main at the bottom, in which case the highest currently installed breaker can't exceed that 6 foot, 7 inch mark (2 meters for the people who measure with Communist rulers). I was just curious why the checklist is only concerned about the main, since any breaker installed too high can present a hazard to the person attempting to service it. Additionally, small buildings may not have a 'main', per se. They might have up to six individual breakers, so you'd want to measure to the highest one of the group.
Reply With Quote
  #9  
Old 2/29/08, 5:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: inspection procedural checklist

Ah yes the six throw rule.
Reply With Quote
  #10  
Old 2/29/08, 6:00 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

This may just be common sense, but I didn't see any thing about checking the floor for moisture or water below the panel. Todays inspection had 2 inches of water in the basement. Old house changed over to apartments, I didn't check the 4 electrical panels.

Gary
Reply With Quote
  #11  
Old 2/29/08, 6:25 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Quote:
Originally Posted by Mike Whitt
Are the two of you brothers?

Sometimes you will find a white wire attached to a breaker such as for water heaters and air conditioners.

The requirement to reidentify was in the exceptions until the 1999 code cycle and even then wasn't enforced by all code officials.
From the 1993 NEC:

"310-12(c) Ungrounded Conductors.
Conductors that are intended for use as ungrounded conductors, whether used as single conductors or in multiconductor cables, shall be finished to be clearly distinguishable from grounded and grounding conductors.

Ungrounded conductors shall be distinguished by colors other than white, natural gray, or green; or by a combination of color plus distinguishing marking. Distinguishing markings shall also be in a color other than white, natural gray, or green, and shall consist of a stripe or stripes or a regularly
spaced series of identical marks. Distinguishing markings shall not conflict in any manner with the surface markings required by Section 310-11(b)(1).

Exception: As permitted by Section 200-7."
Reply With Quote
  #12  
Old 2/29/08, 7:17 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: inspection procedural checklist

Good checklist!

Here's a few more to add in...

Report location of panel (required by some states and just a good idea.)
Report any breakers found turned off.
Report lack of proper readable labeling.
Look closely at main lug bolts/threads to see if one was never torqued.
Double check no breakers were knocked to off while installing front cover.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 2/29/08, 7:26 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: inspection procedural checklist

Hahaha ..Gary you can file that under plumbing or foundation.
Reply With Quote
  #14  
Old 2/29/08, 7:38 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Quote:
Originally Posted by jtedesco1
From the 1993 NEC:


"310-12(c) Ungrounded Conductors.
Conductors that are intended for use as ungrounded conductors, whether used as single conductors or in multiconductor cables, shall be finished to be clearly distinguishable from grounded and grounding conductors.

Ungrounded conductors shall be distinguished by colors other than white, natural gray, or green; or by a combination of color plus distinguishing marking. Distinguishing markings shall also be in a color other than white, natural gray, or green, and shall consist of a stripe or stripes or a regularly
spaced series of identical marks. Distinguishing markings shall not conflict in any manner with the surface markings required by Section 310-11(b)(1).


Exception: As permitted by Section 200-7."
Did you read 200-7 found on page 32?
i believe that you will find that the requirement to identify the white or gray conductor when being used as an ungorunded conductor in the exceptions
Reply With Quote
  #15  
Old 2/29/08, 9:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: inspection procedural checklist

Quote:
Originally Posted by bking
Good checklist!

Here's a few more to add in...

Report location of panel (required by some states and just a good idea.)
Report any breakers found turned off.
Report lack of proper readable labeling.
Look closely at main lug bolts/threads to see if one was never torqued.
Double check no breakers were knocked to off while installing front cover.
I was working in a panel this morning, and the breaker labeled "fire alarm system" was turned off. My guess is that the battery for the fire alarm is also long since dead. This was an apartment building. There was some monkey business going on in this place anyhow, since the "owner panel" was empty of its former breakers, and there were some suspicious breakers distributed among the tenant panels. (all the panels were next to each other in a line). Not too hard to put two and two together on that one.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Roofing checklist mboyett Roofing Inspections 21 6/2/11 10:45 PM
Radon Mitigation System Checklist dmacy Ancillary Inspection Services & Additional Topics 5 1/9/09 4:50 PM
Texas inspection report NCR checklist jonofrey Miscellaneous Discussion for Inspectors 9 10/17/06 9:25 AM