Default As an inspector & not an electrician...

As an home inspector & not an electrician how would you report the following.
(What I mean is in the eyes of a home inspector would you report on the mentioned issues) (as an electrician I would think you would consider a sloppy install)

The romex above the panel. Would you recommend securing or not report about this.

The grounds being intertwined together. Should they be individualy connected to the ground bar.

The bare aluminum wire has been cut to fit the lug at the top left of the panel.

This is a sub panel not the main.

Any other issues you would report on?
Attached Thumbnails
inspector-and-not-electrician-107007-009-small-.jpg.jpg
Views:	158
Size:	56.6 KB
ID:	15246   inspector-and-not-electrician-107007-010-small-.jpg.jpg
Views:	152
Size:	64.5 KB
ID:	15247   inspector-and-not-electrician-107007-012-small-.jpg.jpg
Views:	137
Size:	63.8 KB
ID:	15248   inspector-and-not-electrician-107007-011-small-.jpg.jpg
Views:	152
Size:	58.6 KB
ID:	15249  
Reply With Quote
  #2  
Old 10/16/07, 9:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: As an inspector & not an electrician...

When I (a home inspector) see "crap" like this, I defer the whole mess, rather than try to list each visible defect.

The panel and its components have been improperly and unprofessionally installed and/or modified, and should be repaired by a qualified electrician.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/16/07, 9:08 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: As an inspector & not an electrician...

If this is a sub-panel what is that bare wire out the bottom for???
Reply With Quote
  #4  
Old 10/16/07, 9:12 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,937
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by dmacy
As an home inspector & not an electrician how would you report the following.
(What I mean is in the eyes of a home inspector would you report on the mentioned issues) (as an electrician I would think you would consider a sloppy install)

The romex above the panel. Would you recommend securing or not report about this.
I do not think I would say any thing on this ...
The grounds being intertwined together. Should they be individualy connected to the ground bar.
.I feel the grounds need a mechanical joint A wing nut or split bolt..
The bare aluminum wire has been cut to fit the lug at the top left of the panel.
..Yes this is not good.
This is a sub panel not the main.

Any other issues you would report on?
I would say what I see that needs correction and recommend they get an electrician to repair as required immediately.
I expect you saw other things in the Home, plates missing, GFCIs required Covers missing ect.



..... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #5  
Old 10/17/07, 6:56 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 744
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: As an inspector & not an electrician...

I don't think that the ground has been cut. It looks like it was previously terminated in a lug and retains the shape of the set screw. Also notice the compound around the depressed area.

The individual branch circuit ground must be terminated to the buss. Most buss bars will accept 2, of the same size, terminated in 1 hole.
Reply With Quote
  #6  
Old 10/17/07, 7:28 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: As an inspector & not an electrician...

David,

Nice catch.

Like Jeff P. stated....Defer the entire panel to a licensed Electrician.

You've got too many issues here. It appears that the Electrician was smoking some good stuff during this installation.
Reply With Quote
  #7  
Old 10/17/07, 9:07 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,553
Default Re: As an inspector & not an electrician...

Thanks for the replies.

Since this is an educational forum would someone care to enlighten me with being specific on the violations with this panel. Are there any safety concerns or are these NEC specific violations.

As Speedy mentioned why is there a ground wire at the bottom of the sub panel. Shouldnt this be attached at the main.

Speaking of the main. I didnt take off this cover by the meter as it was shared with another unit. Maybe I should have. Would you?
Attached Thumbnails
inspector-and-not-electrician-107007-003-small-.jpg.jpg
Views:	70
Size:	31.5 KB
ID:	15269  
Reply With Quote
  #8  
Old 10/17/07, 12:39 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: As an inspector & not an electrician...

He didn't say but if this is a sub in a detached building it would need another ground electrode system ... or this could just be bonding pipes.
As for the combined grounds, the only real violation is they are not joined with a listed splicing method. There is nothing that says you need to take all EGCs back to the grounding bus. In fact, as long as the conductor is sized to the largest O/C device served, they can all come back on one wire. The exception to that is the swimming pool underwater light. (EGC must be insulated and unspliced)
They should have secured the Romex at the top of the panel tho.
Reply With Quote
  #9  
Old 10/17/07, 12:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by dmacy
Speaking of the main. I didnt take off this cover by the meter as it was shared with another unit. Maybe I should have. Would you?
That cover should not be removed by a Home Inspector. Not because it's "shared," but because it's part of the lateral and meter base.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 10/17/07, 11:14 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by jpope
That cover should not be removed by a Home Inspector. Not because it's "shared," but because it's part of the lateral and meter base.
Are you sure about that, Jeff? I inspect panels that look like this one, and the right half of the panel contains the servivce disconnects. This looks like one of those.
Reply With Quote
  #11  
Old 10/17/07, 11:31 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by Speedy Petey
If this is a sub-panel what is that bare wire out the bottom for???
You are the Sparky, Petey. You explain it.

We are just lowly HIs, and our job is to generate work for your kind



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 10/18/07, 12:11 AM
wsiegel wsiegel is online now
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: As an inspector & not an electrician...

Jeff,

I agree with Paul on that one.
Reply With Quote
  #13  
Old 10/18/07, 12:28 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by wdecker
You are the Sparky, Petey. You explain it.

We are just lowly HIs, and our job is to generate work for your kind
It was an honest question. I obviously can't see where it goes. Maybe it goes to a ground rod that is not needed in this case.
MOST DIYers think a ground rod is needed at ANY sub-panel.
Reply With Quote
  #14  
Old 10/18/07, 2:52 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by pdickerson
Are you sure about that, Jeff? I inspect panels that look like this one, and the right half of the panel contains the servivce disconnects. This looks like one of those.
To me, it looks like the right half is the lateral gutter, where there would be nothing other than spliced conductors. The disconnects appear to be beneath each meter.

If there are breakers and a dead-front in the right side, by all means, remove the cover, but that's not how it looks from my perspective. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 10/18/07, 2:59 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: As an inspector & not an electrician...

Quote:
Originally Posted by jpope
To me, it looks like the right half is the lateral gutter, where there would be nothing other than spliced conductors. The disconnects appear to be beneath each meter.
Yeap...they sure are.........
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrician signs off 'ganged neutrals'...now what? mgault Electrical Inspections 16 6/3/07 12:09 AM
Electrician or handyman repair? srowe Electrical Inspections 8 1/4/07 10:21 AM
Help Wanted: Electrician (Full Time/Illinois) ebadofsky Miscellaneous Discussion for Inspectors 0 9/12/06 8:14 PM
Electrician Help bkelly2 Plumbing Inspections 1 4/27/06 7:56 PM


All times are GMT -4. The time now is 3:23 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts