Default Installed outlet, others don't work...

I think I know the answer to this question but I thought I would get some additional input from you guys before answering.

I have a recent client who installed a GFCI in his laundry room, but now has the following question:
Therefore, I replaced the outlet with a GFCI outlet - upon moving in (I didn't think it was a big deal) - and the GFCI worked fine. Unfortunately, after installing the GFCI outlet, now none of the regular outlets in the dining room work at all. Do you know why this is and what I need to do in order to have a working GFCI outlet in the laundry room and still have my four WORKING dining room outlets?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/24/10, 9:57 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Installed outlet, others don't work...

uhhhh....call an electrician?
Reply With Quote
  #3  
Old 3/24/10, 10:29 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Installed outlet, others don't work...

He unconnected a branch line.
Reply With Quote
  #4  
Old 3/24/10, 10:37 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,567
Default Re: Installed outlet, others don't work...

Have someone with a clue install the outlet properly would be a wise choice I think...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 3/24/10, 10:47 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installed outlet, others don't work...

Besides the wiring mistake made, the dining room receptacle circuit should not be providing power to the washing machine.

Dining room receptacles are supposed to be a 20 amp circuit. They can be part of the 2 small appliance circuits for the kitchen.
Reply With Quote
  #6  
Old 3/24/10, 11:16 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Installed outlet, others don't work...

Thanks guys, that's pretty much where I was at. I didn't know it was supposed to be 20 amp and only connected to the kitchen. That's news to me. So I learned something too.
I appreciate it.
M.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 3/24/10, 11:32 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Installed outlet, others don't work...

I have a hard time encouraging homeowner's to fix their own electrical issues. I inspected a home last week that had numerous serious and some less serious service entrance panel issues. One was improperly labeled white wires used as hot wires. The RE agent was there as I was going over all of my findings with the Buyer and said, when I mentioned that white wire issue "Isn't that something Joe here can fix himself once he gets moved in?" I told her No, that I recommend a qualified electrician for all electrical issues. I explained that taking the dead-front off of the panel exposes one to serious risks and that "instant death' was possible. She got a real chuckle out of that and rolled her eyes and I'm sure told her client later to ignore that issue. What did she tell him about the other more serious ones...I don't know. Anyway, I just don't encourage untrained folks to mess around with the electrical system but that's just me.
Reply With Quote
  #8  
Old 3/24/10, 12:32 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installed outlet, others don't work...

Quote:
Originally Posted by mnahrgang View Post
I didn't know it was supposed to be 20 amp and only connected to the kitchen. That's news to me. So I learned something too.
I appreciate it.
M.
Marc,

Read 210.52(B) for the small appliance circuit info. Summed up, no loads except receptacles from kitchens, dining, breakfast etc.

210.11(C)(2) tells you about the required 20 amp laundry circuit.
Reply With Quote
  #9  
Old 3/24/10, 4:22 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installed outlet, others don't work...

Quote:
Originally Posted by mnahrgang View Post
Thanks guys, that's pretty much where I was at. I didn't know it was supposed to be 20 amp and only connected to the kitchen. That's news to me. So I learned something too.
I appreciate it.
M.

Yes they're required to be on a 20 amp circuit, however it does not have to be on with the kitchen, that's just one option. You could run a separate 20 amp circuit for the dining room.
Reply With Quote
  #10  
Old 3/24/10, 4:30 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installed outlet, others don't work...

Run extension cords to the dining room.
Reply With Quote
  #11  
Old 3/24/10, 4:47 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Installed outlet, others don't work...

Quote:
Originally Posted by ldapkus View Post
Run extension cords to the dining room.

...and put a multiplyer on each cord so they can have enought outlets.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM