Default Installing disconnect

How difficult is it to install a main disconect on a panel without one? The SEC were 1/0 copper.
Reply With Quote
  #2  
Old 7/28/07, 12:08 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Installing disconnect

How difficult is it to make a car "run?" The car is red.

Well, it could be as simple as turning the key, or as complex as building the engine. . .

Do you see where I'm going with this?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/28/07, 12:23 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installing disconnect

Nevermind.
Reply With Quote
  #4  
Old 7/28/07, 12:38 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Installing disconnect

It's easy Dylan, call an Electrician.
Reply With Quote
  #5  
Old 7/28/07, 8:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

Agreed...this is not a DIY forum so I as well wont go into installing a disconnect.....contact a local electrician and have it done right.

With that said...it is not difficult if you know what you are doing, I usually say to DIYer's that if you have to ask it probably means someone else should do it...not being a smart ***** either...just wanting you to be safe is all as you are going to be dealing with unprotected conductors at some point in a service disconnect installation and it is important to know what is going on....important to know the POCO has removed the meter....and all permits are in place.



Paul W. Abernathy
Reply With Quote
  #6  
Old 7/28/07, 9:49 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installing disconnect

Thanks guys. I am in no way going to be performing this type of work, just had a moment of curiosity is all. I, for some reason, have been seeing this in quite a few recent inspections.
Reply With Quote
  #7  
Old 7/28/07, 11:04 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Installing disconnect

Quote:
Originally Posted by dbucknavich
Thanks guys. I am in no way going to be performing this type of work, just had a moment of curiosity is all. I, for some reason, have been seeing this in quite a few recent inspections.
Your origianl question as asked CANNOT be answered. Jeff had the best analogy.

Typically are not "added" to services. They are installed from the start.
Reply With Quote
  #8  
Old 7/28/07, 11:37 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

Can always be added to a service with no disconnection means ahead of it, simply means we have more work to do...but most certainly can be added if the existing panel is not actually compliant with a disconnection means and does not meet the exceptions provided by the NEC®

Agreed it should be engineered into the start of the project, however I see many old homes that have poor electrical systems, no OCPD on the panel itself and do not meet the exceptions layed out in the NEC®.

I have installed a many service disconnetion means ahead of older panels....but true fact is we end up updating the panels anyway...lol



Paul W. Abernathy
Reply With Quote
  #9  
Old 7/28/07, 11:44 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

In fact......if the panel is old you may have another option...Eaton® makes a remodel insert that is used alot in replacement of FPE and Zinsco panel by removing the inner guts.....replaceing with with their UL Approved insert and it has a main breaker in it.....then you have your main breaker....and main OCPD and all done.....in that option.

Do a service upgrade or swap out...and install a new panel with a main breaker within it....done.....( provided we are talking about closest point of entrance ).....

And on the FAR end spectrum....maybe it is a panel that will accept a backfed breaker....and ind. holding clip and space in the panel available for it....another possible option....depending of course on the panel in question.



Paul W. Abernathy
Reply With Quote
  #10  
Old 7/28/07, 11:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

with the 1/0 CU...if it is the main service panel...and is directly inline with the outside meter...then the service size would I assume be 175A service...if the panel you are speaking of is a remote distribution panel it would be 150A on the 1/0 CU......if remote it should have a disconnection means ahead of it anyway......if not....good reason to recommend an upgrade as those conductors feeding it are not protected...



Paul W. Abernathy
Reply With Quote
  #11  
Old 7/28/07, 11:54 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Installing disconnect

Thanks for building the engine for us Paul. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 7/28/07, 12:10 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 2,074
Default Re: Installing disconnect

Quote:
Originally Posted by pabernathy
In fact......if the panel is old you may have another option...Eaton® makes a remodel insert that is used alot in replacement of FPE and Zinsco panel by removing the inner guts.....replaceing with with their UL Approved insert and it has a main breaker in it.....then you have your main breaker....and main OCPD and all done.....in that option.

Do a service upgrade or swap out...and install a new panel with a main breaker within it....done.....( provided we are talking about closest point of entrance ).....

And on the FAR end spectrum....maybe it is a panel that will accept a backfed breaker....and ind. holding clip and space in the panel available for it....another possible option....depending of course on the panel in question.
Paul
is this insert a good switch out for all old panels or just those listed &
keeping market area in mind what is typical cost for this item
Reply With Quote
  #13  
Old 7/28/07, 12:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

Actually it has been used in MANY older panels.....in fact I just did one in an old pushmatic panel....removed everything down to the empty enclosure...contacted Eaton® with what I wanted...was a simply 100A rated switch out...conductors were already sized properly...simple....replaced the guts and it is UL approved for the installation.

The insert is not expensive.....I believe my 20 CKT 100A insert was about 120.00 around about...my office takes care of the billings and so on...anyway it is just an option for older enclosures.....not a solution for all senerios by any means.....



Paul W. Abernathy
Reply With Quote
  #14  
Old 7/28/07, 12:25 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Installing disconnect

Dennis,

It is kinda like the Listed Breaker thing.......we see the new CL ( Classified ) breakers alot and they fit in ITE, Seimens, Gould and they have them for Square D QO and Homeline and so on.......anyway some will believe they are not listed to go in the manufactures panel unless they say they can...well the UL has said they can......if the manufacturer says their warranty is void if it is done...they open themselves up for a lawsuit because of a legal lawsuit that said manufacturers can't do that on replacement parts if tested in their equipment and approved by 3rd party.....anyway long story short....an insert is only that....an insert.......but is a possibly soution for some situations....but not all.



Paul W. Abernathy
Reply With Quote
  #15  
Old 7/28/07, 12:28 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 2,074
Default Re: Installing disconnect

Thanks Paul its always to know other options, I'm in beginning stage of revamping my house and the panel is on the list
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Exterior Service Disconnect Clearances? rcramer Electrical Inspections 18 7/28/07 1:12 PM
50 amp disconnect for 1600sf condo kmccullough Electrical Inspections 5 4/10/07 8:49 PM
Well pump disconnect sfalvey Plumbing Inspections 0 11/17/06 12:23 AM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 12:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 12:32 PM


All times are GMT -4. The time now is 8:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts