Quote:
I went back and fixed per suggestion. My 3-light tester showed the circuit as being grounded, my sure tester showed and un-grounded circuit. I learned from this post. Thanks to all the inputs. I may not use that chaep tester anymore as it definitely fooled me!!!!!!!!!!!! Chuck Yezza, President 1st Choice Property Inspectors Inc. NACHI #05012083 Concord, Ohio 440-6678458 cyezza@roadrunner.com www.1stcpi.com |
|
#47
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The sure test looks for a low impedance path (<1 ohm), the 3 light tester only shows you have enough of a path to light a neon. (meg ohms).
|
|
#48
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mike nobody picked up on my question, what do you think?
With a 2 wire circuit to the garage, couldn't the installer drive a rod and connect the ground to the neutral? (no other metalic paths) 250.32(B)(2) Nothing in that rule says it has to be a feeder, it can be a single branch circuit. |
|
#49
|
||||
|
||||
|
Running to DC to catch a flight and wish I had gotten in on this earlier.....seems very interesting...
I will say this......the Earth is never to be considered an effective path to do anything.....driving a rod at a building, lamp post and what have you has nothing to do with the electrical system....serves no viable function in the electrical system as it pertains to the dwelling...other than lightning and surges...and in regards to 250.32(B)(2)...more so Lightning. It is essential to provide an effective fault path to clear OCPD's.....in regards to GFCI's...they detect leakage which results in a magnetic field in the transformer of the GFCI resulting in the circuitry to cut out.....leakage of 4-6mA will cause it to open......leakage because of improper installation, bad equipment, improper connections and so on will make the GFCI activate and is part of the sources for nusi. tripping.... Ok....gotta run......flight leaves in 3 hours and I have a 2 hour trip...Oh....No Greg.......the exception to 250.32(B)(2) still provides this path....via the grounded conductor...but you knew that.....later fellas.....have fun. Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#50
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I never said a ground rod alone would open the breaker on a fault, nor was that my intent. Only that it would operate the GFCI on a bolted fault like they had in the garage door scenario.
My 250.32(B)(2) was directed at the top note in this thread and yes you are using the grounded conductor as the grounding path, specifically allowed in this situation ... until the 2008 is adopted. Mike was implying that in the desert he lives in it would take over 800 8' ground rods (at >20,000 each) to get under 25 ohms. I knew they had a drought but I didn't realize it was that bad Last edited by Greg Fretwell; 11/26/07 at 11:17 AM.. |
|
#51
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Othere sections of the NEC would not allow the connection of the electrode system to the neutral of a branch circuit any where on the system. The allowance to bond to the neutral at the second building is not the only allowance in the NEC for allowing the neutral to act as an equipment grounding conductor. See 250.140 |
|
#52
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I suppose we could argue about this for a month or two but the phrase you highlighted was about GFCI protection, not defining what they mean by "supply". If they meant "feeder" to the exclusion of branch circuits why didn't they use that word at the top of the article? It is really a moot point since the whole thing was deleted in the 2008 code.
As far as I know this was the last place that allowed the neutral to also act as the EGC on the line side of the service disconnect. |
|
#53
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Quote:
Quote:
|
|
#54
|
||||
|
||||
|
I just wanted to interject and say....I LOVE you guys......thehehehehe
Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 7:57 AM |
| GFCI Safety Notice | rcooke | Electrical | 1 | 10/30/07 12:29 PM |
| Garage GFCI | rdale | Electrical | 29 | 8/8/07 4:06 PM |
| Shower stall light/fan on garage GFCI | lprinzi | Electrical | 3 | 10/31/06 4:13 PM |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical | 0 | 7/7/06 12:24 PM |