Default Insulation Stripped back too far....need narrative.

Looking for a narrative explaining why the insulation on the main service conductors shouldn't be stripped back too far.
Attached Thumbnails
insulation-stripped-back-too-far-need-narrative-308-highland-horizon-7-9-11-021.jpg  



George Russell
George Russell Professional Inspections
Austin,Texas
TREC # 10215
512-296-9538
http://georgerussellprofessionalinspections.com/
http://www.facebook.com/austinhomeinspections

Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/11/11, 7:55 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Insulation Stripped back too far....need narrative.

Quote:
Originally Posted by grussell View Post
Looking for a narrative explaining why the insulation on the main service conductors shouldn't be stripped back too far.
Please explain the hazard you see.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 7/11/11, 7:58 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Stripped back too far....need narrative.

Although it may be sloppy IMO there really is no hazard or violation worth mentioning.
Reply With Quote
  #4  
Old 7/11/11, 8:14 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Insulation Stripped back too far....need narrative.

I agree - no big deal here. The only real issue you have is with the grounding conductors that are attached to the neutral terminal on a remote (sub) panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 7/11/11, 8:43 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Stripped back too far....need narrative.

Are you sure it's a sub panel? Since it's on the outside of the building I would guess that the conduit on the right side comes from the meter enclosure.

Reply With Quote
  #6  
Old 7/11/11, 9:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Insulation Stripped back too far....need narrative.

No, not completely sure. I can see the bonding strap now that you've enlarged the picture, so it's possible this is service equipment. Although I wouldn't expect to see both a neutral and EGC coming from the meter enclosure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/11/11, 10:35 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Insulation Stripped back too far....need narrative.

George, first off let me say that I do not think the wires in your photo are excessively stripped. If I did, I might use something like:
Quote:
The importance of removing the correct length of insulation. Most electrical devices including switches and receptacle outlets show on the molding a strip gauge. This is the length of insulation that should be removed to make the best connection possible with the device. Stripping the wire insulation too short can produce an insecure connection and could produce an overheated area which could in time end up arcing and burning away from the connection which would produce a loss of continuity in the circuit, or a loss of power from that point on in the circuit. A wire that is stripped too long can become a hazard because it will allow the extra bare area of the conductor to be vulnerable for coming into contact with other wires such as the ground, or could become a danger to anyone who may come in contact with the wired device.
Other than NEC 110.3(b) Mfg Rqmts I'm not aware of another citation that is applicable. Common sense does come into play though.
Reply With Quote
  #8  
Old 7/11/11, 10:40 AM
George E. Russell George E. Russell is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Austin,Texas
Posts: 943
Default Re: Insulation Stripped back too far....need narrative.

It's the main. The sub is in the garage. Thanks All!!



George Russell
George Russell Professional Inspections
Austin,Texas
TREC # 10215
512-296-9538
http://georgerussellprofessionalinspections.com/
http://www.facebook.com/austinhomeinspections

Reply With Quote
  #9  
Old 7/11/11, 11:06 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Insulation Stripped back too far....need narrative.

What are the other breakers for?
I see a couple of grounded conductors and all are 240 circuits.
Dryer and kitchen stove?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 7/11/11, 11:21 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Stripped back too far....need narrative.

Quote:
Originally Posted by jpope View Post
No, not completely sure. I can see the bonding strap now that you've enlarged the picture, so it's possible this is service equipment. Although I wouldn't expect to see both a neutral and EGC coming from the meter enclosure.
Yes, unless that is a GEC run in the service raceway then it should not be there. There should be no EGC's on the line side of the service disconnects. For what it's worth I can only see 3 conductors.
Reply With Quote
  #11  
Old 7/11/11, 6:46 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Insulation Stripped back too far....need narrative.

It could use one of these
Attached Thumbnails
insulation-stripped-back-too-far-need-narrative-myershubground.jpg  



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #12  
Old 7/11/11, 6:50 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Insulation Stripped back too far....need narrative.

Quote:
Originally Posted by Robert Meier View Post
Yes, unless that is a GEC run in the service raceway then it should not be there. There should be no EGC's on the line side of the service disconnects. For what it's worth I can only see 3 conductors.
I guess you're right. The stranded AL comes from the other side...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 7/11/11, 7:02 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Stripped back too far....need narrative.

Quote:
Originally Posted by gwells View Post
It could use one of these
Why would it need a hub?
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/11/11, 7:15 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Insulation Stripped back too far....need narrative.

These wires are stripped too far:

insulation-stripped-back-too-far-need-narrative-p6233128.jpg insulation-stripped-back-too-far-need-narrative-p6233127.jpg

My comment on the report:
"It appears that the insulation has been stripped excessively on the right side of the panel at the breakers. Recommend having a licensed electrician repair as needed."



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org

Last edited by dhays; 7/11/11 at 7:20 PM..
Reply With Quote
  #15  
Old 7/12/11, 12:34 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Insulation Stripped back too far....need narrative.

Most breakers have wire strip lengths/gauges marked on them. I would expect that main panel lugs would have something similar in the instructions or listing. And the reasons for that would be similar.

That does appear to be more wire stripped off the feeders than I would expect to see. Might be a concern related to incidential contact with a bare feeder wire for someone working inside that panel. It's also possible that an appropriate amount of the insulation was stripped off, but the wire was not fully inserted into the lug.

I would have made a note of it, but not as a significant issue if there appeared to be a solid connection. Maybe something along the lines of ...

Quote:
There appears to be more than the usual amount of bare wire exposed at the connection for the large feeder wires inside the panel. This should be checked by a licensed electrician next time any work is performed inside the panel, and corrected as needed.
And for what it's worth it does look like all 6 ground wires are run with the 4 circuits to the inside of the house. Jeff ... you might have seen a stripe on one of the 3 feeder wires that looked like a ground.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 7/12/11 at 3:26 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
History of Insulation with Masonry mcyr General Inspection Discussion 7 2/27/08 7:53 PM
Insulation blankets rray Plumbing Inspections 35 12/9/06 9:38 AM
Wood fiber insulation? bwooddell Interior Inspections 3 3/22/06 9:58 PM