Default Interesting article from U/L on armored cable

In the late 1800s and early 1900s, one of the earliest wire raceways was called “moulding” (sic).
It consisted of two pieces of wood, a backing and a capping. The backing had two or more individual grooves, one for each wire, and a capping to cover the grooves. The grooves separated the wires by 1/2 inch, and provided mechanical protection.

Although wood moulding was not intended for use in concealed spaces or damp locations, it was required by the National Electrical Code® (NEC®) to have two coats of waterproof paint, or be impregnated with moisture repellant. This product continued to be permitted by the NEC until the 1935 edition. However, by the mid-1910s, some large cities had banned its use, and wood moulding was being phased out as metal moulding and armored cable were becoming widely available.

Armored cable was first Listed by Underwriters Laboratories Inc. in 1899 for Sprague Electric Co. of New York, and was originally called “Greenfield Flexible Steel-Armored Conductors,” after one of its inventors, Harry Greenfield. Armored cable first appeared in the 1903 NEC.

There were originally two initial versions of this product, one called “AX” and the other “BX,” with the “X” standing for “experimental.” The “BX” version became the one that eventually was produced, and hence the name “BX” stuck. This was the registered trade name of armored
cable for General Electric (GE), who later acquired Sprague Electric. Armored cable made after 1959 requires an aluminum bonding strip under the armor to help improve the conductivity of the armor. This continues to be a popular wiring method today, and is described in Article 320 of the NEC.

Published in the U/L "Electrical Connections" column
Reply With Quote
  #2  
Old 2/25/07, 9:42 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Yeppers.....

The problem with BX today is people are thinking it is listed to use the outer case as a low resistance path EGC and it is not intended for the purpose....so many HI's run into a "FLIP" inspection where the person has replaced the 2 prong with 3 prong plugs and now think it has a good LOW resistance path.....yeah it has a path....but not very LOW in terms of aiding in clearing a fault if you get Objectionable currents running on it it simply can act as a heat strip......seen it a few times in a basement where it was RED as fire........

Don't you hate when companies "experiment" on ya......love it....AX and BX......an experimental project for the consumers....nice.



Paul W. Abernathy
Reply With Quote
  #3  
Old 2/25/07, 11:59 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by pabernathy
Don't you hate when companies "experiment" on ya......love it.....
Are you still whining about that tracking chip the CIA implanted in your head? Get back on your meds, and you'll forget all about that.
Reply With Quote
  #4  
Old 2/25/07, 12:03 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by Marc D. Shunk
Are you still whining about that tracking chip the CIA implanted in your head? Get back on your meds, and you'll forget all about that.
Gee all this time I thought that thin aluminum strip was to hold the fish paper ( anti Short ) in place .

Roy Cooke
</IMG>



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 2/25/07, 2:24 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

The armor af type AC is listed for and perfectly capable of opening the OCD and that is the intent of the EGC.
Reply With Quote
  #6  
Old 2/26/07, 11:24 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by Greg Fretwell
The armor af type AC is listed for and perfectly capable of opening the OCD and that is the intent of the EGC.
AHh....greg I was talking about the old BX...it does NOT have this strip and is not capable of opening a OCPD......been their...seen it with my own eyes.

marc.......I wish I was on the MEDS....been the longest 4 days seminar trip yet...I am still sitting in the airport and no the tracking chip came out years ago....at least thats what the people with the white jackets and padded walls told me.



Paul W. Abernathy
Reply With Quote
  #7  
Old 2/26/07, 3:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

I would still question that if this is a 15 or 20a circuit and the armor is properly connected. That is particularly true if there is already some load current on the circuit. It would take an awful lot of BX to generate 5 ohms of impedance from the inductive effect alone. The fact that this lasted in the market without the strip for 60 years is an indication. Bear in mind there will always be some continuity between the wraps that shunts out the choke effect so it is not one long single inductor.

When folks start screwing in the "greenies" all bets are off.
Reply With Quote
  #8  
Old 2/26/07, 7:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Lasting 60 years is one thing Greg.....converting it to use the outer case as a EGC is another thing. The older BX was simply never listed for this use at all.



Paul W. Abernathy
Reply With Quote
  #9  
Old 2/26/07, 8:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by pabernathy
Lasting 60 years is one thing Greg.....converting it to use the outer case as a EGC is another thing. The older BX was simply never listed for this use at all.
That's true, mainly due to the fact that "listings", as we know them, didn't exist during that era.
Reply With Quote
  #10  
Old 2/26/07, 9:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

NO problem....so I imagine the " GLOWING " BX I see in basements.....hey if you guys like BX.....too all his own.......you know my opinion on it and it stands...



Paul W. Abernathy
Reply With Quote
  #11  
Old 2/26/07, 9:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by pabernathy
NO problem....so I imagine the " GLOWING " BX I see in basements.....
Pictures! Pictures! Or, alternately, calculations!

I'm in several different basements almost every waking day of my life, and I've yet to see such an instance.

If you feel like you're being ganged up on, you are. This inductor theory is a bunch of crapola on a stick. The armor of style BX is no where near a textbook inductor. The bond strip was only added to give 100% assurance that it can never be.

Resist the groupthink, Paul. It's rather unbecoming.
Reply With Quote
  #12  
Old 2/26/07, 10:25 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interesting article from U/L on armored cable

marc, I agree that 99.9% of the time the old BX will open the ocpd, but that still leaves that .1% of the instances where it won't. When I was taking code classes, the instructor on the VHS told of a house fire that he investigated and found the cause to be a very long BX run to a bathroom light that had been shorted for a long time. Over time the drilled holes in the framing became charcoal (there is a term for this I can't remember) and the house caught fire. (I think the instructor was David Shapiro.)

Another electrician reported a dull red glowing BX cable in an attic. I think it was on Mike Holt's site.

There is enough of a chance to where I will not intentionally ever use it for grounding.

Last edited by brian winkle; 2/26/07 at 10:28 PM..
Reply With Quote
  #13  
Old 2/26/07, 10:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Quote:
Originally Posted by Marc D. Shunk
Pictures! Pictures! Or, alternately, calculations!

I'm in several different basements almost every waking day of my life, and I've yet to see such an instance.

If you feel like you're being ganged up on, you are. This inductor theory is a bunch of crapola on a stick. The armor of style BX is no where near a textbook inductor. The bond strip was only added to give 100% assurance that it can never be.

Resist the groupthink, Paul. It's rather unbecoming.
Obviously it would be wasted to have YOU explain objectionable currents and how it could happen with BX....but since you seem to be a FAN of it.......believe what you will.....oh why not ask Mr. Holt about it.......see his opinion on BX being used as a EGC since you seem to be a fan of it...

gang up on me all you wish service man..........it's all good I dont want to question an electrician in a state with no licensing..we will just say Mr. Shunk is for using older BX as a EGC and leave it be at that ( he is entitled to his opinion..)....while other factors can play into it....I saw it......sorry no pictures as I was not doing websites and teaching when I viewed it....

It is futile Brian, we is on a mission tonight it seems.....I guess I am gonna have to run over to Charlottesville and see that MYSTERY CRAPOLA that did not exist.....since Marc seems to be all knowing tonight.

Oh wait...you better go over to Mike Holts and inform Bob he is wrong....

iwire
Member
Member # 47

posteddocument.writeln(timestamp(new Date(2003,9,31,18,52,0), dfrm, tfrm, 0, 0, 0, 0)); October 31, 2003 06:52 PM The old looking cable is BX and it has no ground conductor.

That must be 12/3 or 14/3 White, Black and Red

In your house if it is truly conduit (pipe) it can be and still is used as a grounding conductor.

The old style BX as Wayne has said will read on your meter like a grounding conductor, however under the wrong circumstances it can heat up and glow like a toaster element instead of operating the over current device.

--------------------
Bob
Massachusetts
Posts: 9203 | Registered: Feb 2003 | IP: Logged |



Paul W. Abernathy

Last edited by pabernathy; 2/26/07 at 10:52 PM..
Reply With Quote
  #14  
Old 2/26/07, 11:04 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Where ya at Shunkie....seems like some VERY big names over on the holt site believe BX is also not something that should be used for an EGC....so are you saying to the HI's who have extreme liability that you feel if they choose to convert 2 prong plugs on an old BX system over to 3 prong plugs and simply BOND it .....that they are fine.....hmmmmm......have not been working with HI's very long have you Marc...

I try to KEEP them out of legal issues...NOT set them UP for them.

hmmm....seems I am not alone....

big john
Member
Member # 5871

posteddocument.writeln(timestamp(new Date(2004,4,24,20,9,0), dfrm, tfrm, 0, 0, 0, 0)); May 24, 2004 08:09 PM Wdalrymple,

Not only is your boss violating electrical codes, but if the receptacles are fed by BX (metal sheathed cable lacking any equipment ground) then he is also creating an additional hazard: A ground fault can heat the metal armor of the cable just like a light-bulb filament.

What was only a shock hazard is now a shock hazard and a fire risk.

-John
Posts: 168 | Registered: Jun 2003 | IP: Logged |

posteddocument.writeln(timestamp(new Date(2005,5,11,9,5,0), dfrm, tfrm, 0, 0, 0, 0)); June 11, 2005 09:05 AM
Using the term "BX" for armored cable that is currently manufactured is a mistake, but is widely accepted, hence the slang "BX".

What is really important to understand about the difference between the two types of cable is the grounding path.

The cable sheath of BX is not permitted to be used for grounding purposes, as it is very unreliable as a grounding path. It may work, or it may not .

I believe that AC cable was manufactured sometime in the '50's.

BX cable is generally larger in diameter and sometimes even has a double outer metallic sheath (the worst stuff to deal with when renovating old work ).

When replacing older 2-prong receptacles look for the bonding strip that is manufactured in the cable with AC Cable. If you see the bonding stip, there is a very good chance the box is grounded(bonded).
Pull out your tester, and check from hot conductor to grounded conductor, then from hot conductor to the box, this will give you an indication of whether there is a grounding path. Just remember that you may get a ground path reading off of the old style BX.... again, check for the bonding strip.

Sometimes you will even see the bonding strip of AC Cable is wrapped around a screw in the enclosure - that is not necessary, as it is a "bonding strip", not an equipment grounding conductor.

--------------------
Pierre Belarge
Instructor & Industry Advocate, NY



So marc........when I speak I do so for the SAFETY of the HI industry........so why dont you ask Pierre if he likes the idea of the old BX ( without a bonding strip ) as a EGC....and then lets have HI's ignore this potential issue and they can just defer to you on this topic....sound good?



Paul W. Abernathy

Last edited by pabernathy; 2/26/07 at 11:14 PM..
Reply With Quote
  #15  
Old 2/26/07, 11:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interesting article from U/L on armored cable

Marc,

I have worked for (2) years training these HI's and helping them and I have their BEST interest at heart. There are MANY cased of the old armoured cable causing fires because of its poor qualities...couple that with the OLD breakers they find and the situations they are within and you simply are doing the HI harm by making the statement you have made....

It is FAR from CRAPOLA and I would begin to DEFY you on this......these guys have way more liability that you or I have as they are targets many times and they need to be safe and aware.....how about you READ this article and understand the very first case it reflects........

How can you assist these guys in one breath and put them at risk with the other...all in your attempt to pull punches with me......you dont have to like me as I knew your intent when YOU KNOW WHO asked you to come here.....but do not put these guys at risk making those statements.
Attached Files
File Type: pdf Sleights_paper.pdf (64.1 KB, 174 views)



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting article about mold by litigation. gromicko IAC2 Indoor Air Forum 16 5/5/11 7:48 PM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical Inspections 10 4/17/11 1:43 PM
Did you KNOW this about NM Cable? pabernathy Electrical Inspections 0 12/19/06 8:46 AM
Hey Joe Tedesco pbolliger Electrical Inspections 7 4/11/06 12:17 AM
Ceilings falling with wires in it. jsmith3 Interior Inspections 9 3/16/06 7:24 PM


All times are GMT -4. The time now is 4:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts