Default Interior GFCI Poll

I know what I would do. How about you? Would you write up no GFCI on a bar wall? The outlet is not in the kitchen, but is within 6 feet of the sink.


interior-gfci-poll-121008-048.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 1/8/09, 9:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Interior GFCI Poll

I would not call it out. It does not serve the counter.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 1/8/09, 9:58 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

With in 6 feet of a utility sink.

Yes I would call it out.
Reply With Quote
  #4  
Old 1/8/09, 10:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

fact is, you can call out anything you want to. You would, however, have no basis in model code or rule of law on which to base your opinion.
Reply With Quote
  #5  
Old 1/8/09, 10:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Quote:
Originally Posted by Marc D. Shunk View Post
fact is, you can call out anything you want to. You would, however, have no basis in model code or rule of law on which to base your opinion.
Marc, you and I disagree on this one. The code states "All 125-volt, single-phase, 15-and 20-ampere receptacles that serve countertop surfaces shall have ground-fault circuit-interrupter protection for personnel."

It doesn't say the outlet has to be in the kitchen. It refers to outlets that "serve countertops". The keyword there is "serve". Could that outlet be used to power a radio on the countertop during a party? Then Disco Dan knocks it into the sink?

Roughly 90% of those outlets in new homes are now protected by GFCI. Those builders must interpret it as required, as I do.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 1/8/09, 10:30 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by Marc D. Shunk View Post
fact is, you can call out anything you want to. You would, however, have no basis in model code or rule of law on which to base your opinion.
Guess I better delete this chart you provided.



Reply With Quote
  #7  
Old 1/8/09, 10:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Interior GFCI Poll

How do you measure 6 ft. from the edge of the sink?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 1/8/09, 10:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
How do you measure 6 ft. from the edge of the sink?
I have measured it with a flexible tape. Usually I just estimate. When you have a bar wall with a sink on the other side of it, there is almost always an outlet directly in front of where the sink is, easily within 6 feet.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 1/8/09, 11:00 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 1,624
Default Re: Interior GFCI Poll

I would not call that out. The "countertop" above the outlet appears to taper down to no more than 8 inches wide. One outlet can be seen on the kitchen side of the wall (left side of picture). I "assume" (I know, I know) that there is another outlet to the left of the sink serving the countertop, directly above and opposite the outlet of concern. You were there, if you feel it was unsafe, regardless of code, recommend it be upgraded to GFCI for safety.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
  #10  
Old 1/8/09, 11:04 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by rnewland View Post
I would not call that out. The "countertop" above the outlet appears to taper down to no more than 8 inches wide. One outlet can be seen on the kitchen side of the wall (left side of picture). I "assume" (I know, I know) that there is another outlet to the left of the sink serving the countertop, directly above and opposite the outlet of concern. You were there, if you feel it was unsafe, regardless of code, recommend it be upgraded to GFCI for safety.
Robert I think the intent of this rule is that an average plug is 6 feet.

Place a corded appliance at the sink and you get shocked.
Make sense?
Reply With Quote
  #11  
Old 1/8/09, 11:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

The bar wall shown is just an example illustration. I see similar setups in 3 out of 5 new homes I inspect. Here's another one from today that I wrote up. Sink on the other side of the opening. Outlet directly below the opening.



interior-gfci-poll-010809-054.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 1/8/09, 11:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
I would not call it out. It does not serve the counter.
Ditto. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 1/8/09, 11:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Interior GFCI Poll

Joe you never did say what year or under which NEC applies to either home.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #14  
Old 1/8/09, 11:13 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
I would not call it out. It does not serve the counter.
Then what does it "serve"? Almost everything you could conceive of plugging into that outlet, except for a vacuum, has to rest on the countertop!



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 1/8/09 at 11:16 PM..
Reply With Quote
  #15  
Old 1/8/09, 11:14 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
Joe you never did say what year or under which NEC applies to either home.
My code quote above was from the 2006 IRC.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How long are your poll lines? bchesser Misc. Discussion 16 11/4/08 8:10 PM
Daily Presidential Tracking Poll - 10/19/2008 (McCain Lead Lost) jburkeson1 Misc. Discussion 3 10/19/08 6:16 PM
Washington Home Inspectors Poll sstanczyk Legislation, Licensing & Legal Issues 147 1/30/08 9:30 PM
E&O information poll sstanczyk Misc. Discussion 7 8/19/07 7:54 PM


All times are GMT -4. The time now is 8:16 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147