Default Re: Interior GFCI Poll

Quote:
Originally Posted by jfunderburk View Post
Then what does it "serve"? Almost everything you could conceive of plugging into that outlet has to rest on the countertop!
Vacuum cleaner, light for the hutch the new owner is going to place right there, Vanilla plug-in, etc.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
  #17  
Old 1/8/09, 10:25 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

One can't assume it is for anything other than something on the counter.

Do you guys that do not call it out ever call out island counters in the kitchen.

Rethink your position.
Reply With Quote
  #18  
Old 1/8/09, 10:29 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,388
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Good point Bob. Rarely could any appliance on the island reach the sink. If you look at it strictly from a potential hazard standpoint, the bar wall is more serious.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #19  
Old 1/8/09, 10:30 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 1,818
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
One can't assume it is for anything other than something on the counter.

Do you guys that do not call it out ever call out island counters in the kitchen.

Rethink your position.
Of course. I was just going by what I saw in the picture. The rest of my comment was that Joe was there. If he felt it was unsafe, regardless of code, write it up. Had I actually been there, I may have written it up too.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
  #20  
Old 1/8/09, 10:35 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
One can't assume it is for anything other than something on the counter.
One can assume it is for the vacuum. For the counter, it would be up higher.


Quote:
Originally Posted by relliott View Post
Do you guys that do not call it out ever call out island counters in the kitchen.

Rethink your position.
I'm rethinking that one, but it's a different question.

John Kogel
www.allsafehome.ca
Reply With Quote
  #21  
Old 1/8/09, 10:35 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,388
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Robert, those bar walls are all pretty much the same. You don't have to be there to grasp this issue.

Here's how I write it up for anyone who may be interested:

"One or more outlets on the bar wall within six feet of the kitchen sink was not provided with ground-fault protection. We recommend upgrading the outlets to have ground fault protection. GFCI receptacles are life saving devices and have been required within 6 feet of the sink since 1987 and at all outlets serving kitchen counters since 1996."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #22  
Old 1/8/09, 10:47 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,554
Default Re: Interior GFCI Poll

Quote:
Originally Posted by jpope View Post
Ditto. . .
Tritto

Appliances no longer have cords long enough to reach the pictured outlet.



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #23  
Old 1/8/09, 10:49 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,392
Default Re: Interior GFCI Poll

The "six feet" wording is not in the 2006 code so I would change that verbiage.


I write it up as a safety upgrade.

The reason it is wired to the GFCI circuit on new homes is to save wire, not to meet any code.


Also, its not about just the sink, the kitchen is considered a potentially wet area.

Some houses have a butlers pantry with a countertop that is 15 feet from the kitchen sink and most code inspectors are requiring these to be GFCI also.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #24  
Old 1/8/09, 10:53 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Unmoderated Guest
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,355
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by bkelly2 View Post
Tritto

Appliances no longer have cords long enough to reach the pictured outlet.
So have all the older ones been thrown away?
Reply With Quote
  #25  
Old 1/8/09, 10:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,388
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Quote:
Originally Posted by bkelly2 View Post
Appliances no longer have cords long enough to reach the pictured outlet.
OK, my obtuse friends, forget the pictured outlet. Picture in your mind an outlet on the bar wall within 6 feet of the sink! That's what this is about.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #26  
Old 1/8/09, 11:00 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Where is that bearded guy when you need him.
(Paul)

This was a good post, Joe.
Reply With Quote
  #27  
Old 1/9/09, 12:00 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,554
Default Re: Interior GFCI Poll

Quote:
Originally Posted by ccurrins View Post
So have all the older ones been thrown away?

Well ya, after they got all wet.



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #28  
Old 1/9/09, 12:23 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,388
Send a message via Yahoo to jfunderburk
Default Re: Interior GFCI Poll

Brian, that was funny!



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #29  
Old 1/9/09, 12:26 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,688
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interior GFCI Poll

Point is......in the picture shown has a receptacle that is more than 12" below the counter surface ANYWAY so it can't serve any counter top so if this is a kitchen it would not need GFCI....REGARDLESS of what you think a person might plug into it.

If you have a Wet Bar application then within 6' of the wetbar sink would apply but in the picture i see it is not a Wet Bar......so NOPE...GFCI not required.

The point is the NEC ( which is concerned about safety just as much as anyone ) is very specific on where GFCI is applied and where it is not.

210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
FPN: See 215.9 for ground-fault circuit-interrupter protection
for personnel on feeders.

(A) Dwelling Units.
All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through ( shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use [ROP 2–50]
[ROP 2–40, 2–41, 2–51]
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a dedicated branch circuit for
electric snow-melting or deicing equipment shall be permitted
to be installed in accordance with 426.28.
(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
[ROP-2–41, 2–40, 2–56, 2–57]
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the requirements
of 210.52(G). [ROP 2–40]
(6) Kitchens — where the receptacles are installed to serve
the countertop surfaces
(7) Laundry, utility, and wet bar sinkswhere the receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
[8]Boathouses




Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.

Last edited by pabernathy; 1/9/09 at 12:30 AM..
Reply With Quote
  #30  
Old 1/9/09, 1:34 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by pabernathy View Post
Point is......in the picture shown has a receptacle that is more than 12" below the counter surface ANYWAY so it can't serve any counter top so if this is a kitchen it would not need GFCI....REGARDLESS of what you think a person might plug into it.

If you have a Wet Bar application then within 6' of the wetbar sink would apply but in the picture i see it is not a Wet Bar......so NOPE...GFCI not required.

The point is the NEC ( which is concerned about safety just as much as anyone ) is very specific on where GFCI is applied and where it is not.

210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
FPN: See 215.9 for ground-fault circuit-interrupter protection
for personnel on feeders.

(A) Dwelling Units.
All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through ( shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use [ROP 2–50]
[ROP 2–40, 2–41, 2–51]
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a dedicated branch circuit for
electric snow-melting or deicing equipment shall be permitted
to be installed in accordance with 426.28.
(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
[ROP-2–41, 2–40, 2–56, 2–57]
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the requirements
of 210.52(G). [ROP 2–40]
(6) Kitchens — where the receptacles are installed to serve
the countertop surfaces
(7) Laundry, utility, and wet bar sinkswhere the receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
[8]Boathouses

Paul I see nothing there about 12" below the surface,also wondering about the smiley cover up?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How long are your poll lines? bchesser Misc. Discussion 16 11/4/08 7:10 PM
Daily Presidential Tracking Poll - 10/19/2008 (McCain Lead Lost) jburkeson1 Misc. Discussion 3 10/19/08 5:16 PM
Washington Home Inspectors Poll sstanczyk Legislation, Licensing & Legal Issues 147 1/30/08 8:30 PM
E&O information poll sstanczyk Misc. Discussion 7 8/19/07 6:54 PM