  #31  
Old 1/9/09, 9:00 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,642
Default Re: Interior GFCI Poll

I would say it with in 6 foot Many appliances come with a 6 foot cord
Reply With Quote
  #32  
Old 1/9/09, 9:08 AM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: Interior GFCI Poll

I look at as if a home owner can mess something up they will. So as a safety measure I would call it out.Whether code requires it or not.
Reply With Quote
  #33  
Old 1/9/09, 1:18 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
also wondering about the smiley cover up?
That's an eight with end parenthases (even if I can't spell it)

try it turns into

So, it reads one through eight.
Reply With Quote
  #34  
Old 1/9/09, 1:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Interior GFCI Poll

Quote:
Originally Posted by gpallotta View Post
So as a safety measure I would call it out.Whether code requires it or not.
So, do you advise clients not to buy homes that are in the flight path of an airport? Where do you draw the line when giving your opinion on perceived safety??

Codes are our guidelines, whether you "quote" them or not. The receptacle in question does not require GFCI protection - period.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #35  
Old 1/9/09, 1:33 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by bkelly2 View Post
Tritto
Quatro!

If it was meant to "serve" the counter top, it'd be much higher on the wall.
Reply With Quote
  #36  
Old 1/9/09, 1:48 PM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: Interior GFCI Poll

Jeffery

Yes codes are guidelines but so is personal experience. I have been to many a party (We Italians have massive parties)where electrical appliances sit on top of the wall (Counter) plugged in willy nilly(and many don't have common sense or hope to much on luck) all over the place and all it would take is one bump and the least the could happen is one fried appliance or the worst someone seriously hurt.If I can make that area a little safer for them through a recommendation I do. If they chose not to follow it so be it.

Yes I follow code but sometimes you have to give that little extra.
Reply With Quote
  #37  
Old 1/9/09, 1:52 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Interior GFCI Poll

You guys can recommend what ever you like but when the seller refuses to pay for it because it is code compliant you may get to pay for the upgrade.

Be careful out there.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #38  
Old 1/9/09, 2:19 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Interior GFCI Poll

That is a common place for receptacle installations here because many kitchens border family rooms or living rooms. They are not required by our AHJ to be GFCI protected as they are considered a required installation for the living or family room.

For those of you that would require the receptacle to be GFCI protected, do you recommend that office desk receptacles have GFCI protection. Heck, If I spill my beer on the power strip, I could get a big bad shock!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #39  
Old 1/9/09, 2:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Interior GFCI Poll

I understand your reasoning Gerry, but that type of recommendation is unwarranted. The flight path scenario was pretty extreme, so I'll give you another one. . .

Receptacles located on interior walls, just inside entry doors - do you recommend these be upgraded as well? After all, someone may run a cord to the exterior for their power tools, or perhaps a radio on the back porch.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #40  
Old 1/9/09, 2:33 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

OK
Let me ask you guys about kitchen counters.
What if you have a split counter with a stove in the middle and a sink on the left side ,but a receptacle on the right counter.

I suppose you see no need for GFCI on the right counter ,since there is no sink on it.

After all they will not plug in on the right counter and set the appliance on the left counter ,near the sink.Especially if it is 10 feet away.

Please explain ,since it is required all kitchen receptacles be GFCI.
Reply With Quote
  #41  
Old 1/9/09, 2:41 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

I think you answered your own question...

Quote:
Originally Posted by relliott View Post
it is required all kitchen receptacles be GFCI.
Kitchens are generally considered potentially wet locations. I wasn't involved in the writting of the code, but my guess is has more to do with water reaching the appliance rather than the appliance reaching the water. JMO

Last edited by rmaday; 1/9/09 at 2:45 PM..
Reply With Quote
  #42  
Old 1/9/09, 2:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Please explain ,since it is required all kitchen receptacles be GFCI.
You have answered your own question good job.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #43  
Old 1/9/09, 2:44 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by rmaday View Post
I think you answered your own question...



Kitchens are generally considered wet locations.
Yes but the wet bar has a better chance of being a shock hazard than a sinkless kitchen island or the right hand side counter ,so I actually dis-agree with Paul,which bothers me on a deep mentor type level.
Reply With Quote
  #44  
Old 1/9/09, 2:47 PM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: Interior GFCI Poll

Jeffery

No I wouldn't.

I'll give you one. In an apartment building that was being renovated there was no outlet in the washroom, it was easier to install one under the light switch in the hallway by the door rather than run a line. The ESA (gov't electrical) inspector required it to be gfci even though it was technically on the other side of the wall. When asked he replied potential use of that outlet by people in the washroom could be deemed a safety hazard.

The same could be said for the above outlet by the bar.

Last edited by gpallotta; 1/10/09 at 5:29 PM..
Reply With Quote
  #45  
Old 1/9/09, 2:49 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by gpallotta View Post
Jeffery

No I wouldn't.

I'll give you one. In an apartment building that was being renovated there was no outlet in the washroom, it was easier to install one under the light switch in the hallway by the door rather than run a line. The tssa (gov't electrical) inspector required it to be gfci even though it was technically on the other side of the wall. When asked he replied potential use of that outlet by people in the washroom could be deemed a safety hazard.

The same could be said for the above outlet by the bar.
Common sense of use.

Good point, as one needs to look at intent.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How long are your poll lines? bchesser Miscellaneous Discussion for Inspectors 16 11/4/08 8:10 PM
Daily Presidential Tracking Poll - 10/19/2008 (McCain Lead Lost) jburkeson1 Miscellaneous Discussion for Inspectors 3 10/19/08 6:16 PM
Washington Home Inspectors Poll sstanczyk Legislation, Licensing & Legal Issues for Inspectors 147 1/30/08 9:30 PM
E&O information poll sstanczyk Miscellaneous Discussion for Inspectors 7 8/19/07 7:54 PM


All times are GMT -4. The time now is 6:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts