Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
lol!!!!



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #122  
Old 1/10/09, 10:13 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Interior GFCI Poll




You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #123  
Old 1/10/09, 10:27 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post


What does his face and your argument have in common.?
Reply With Quote
  #124  
Old 1/10/09, 10:28 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Interior GFCI Poll

Bob, I don't have the skills to insert your mug in the blank face. hth



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #125  
Old 1/10/09, 10:31 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
Bob, I don't have the skills to insert your mug in the blank face. hth
Whatever you say Jimmy.S
Reply With Quote
  #126  
Old 1/10/09, 10:31 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Whatever you say Jimmy.S
Who is Jimmy S.?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #127  
Old 1/10/09, 10:37 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Interior GFCI Poll

Quote:
Originally Posted by mlarson View Post
who is jimmy s.?
interior-gfci-poll-jimmys.jpg
Reply With Quote
  #128  
Old 1/10/09, 10:37 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Help me understand..

How, when two (well respected) electricians state that GFCI is not required in this instance, can anyone continue to vote YES?



They are the specialists, that we say to call,

ie. "Recommend repair (replace/upgrade) by licensed electrician"

This is not the dead horse I am beating, but another horse has come into the barn. This second horse, IMO is much more confusing to me.
Reply With Quote
  #129  
Old 1/10/09, 10:45 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Interior GFCI Poll

Maybe because Joe and I are not well respected Electricians?

Maybe because there is something about being an Inspector that goes beyond codes and whats required.

A checklist report type of guy will blow through and not waste his time to narrate this scenario, while a Inspector that cares about his clients may think it is worth a mention

Perhaps this is why I will never be able to do 4 Inspections a day.

I actually give them their money's worth.

Checklist report guys can keep voting no, but as for me I will continue to use a strong Health and safety aware report.
Reply With Quote
  #130  
Old 1/10/09, 10:49 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Interior GFCI Poll

What's with this check list report crap?

How is that any part of this discussion?

P.S. I use HiPro just like you.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #131  
Old 1/10/09, 11:00 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Maybe because Joe and I are not well respected Electricians?

That's why people are voting yes?

Maybe because there is something about being an Inspector that goes beyond codes and whats required.

So why not GFCI on every outlet?

A checklist report type of guy will blow through and not waste his time to narrate this scenario, while a Inspector that cares about his clients may think it is worth a mention

Perhaps this is why I will never be able to do 4 Inspections a day.

I actually give them their money's worth.

Checklist report guys can keep voting no, but as for me I will continue to use a strong Health and safety aware report.
Bob, it has nothing to do with checklists or speed of inspection.

In this specific instance, the electricians have said it's not needed. And Paul said the NEC is very clear about this.

IMO you are doing your client a dsservice if you call out things that are not needed.

And again, I'm not talking about any Joe the Electrician who is looking to make a buck and says, oh yeah, you need GFCI here, that'll be $150.

There are always scenarios that you can come up with where people do stupid things. We can't mention all of them.

Do you, in every report, tell them that in the event they paint and fail to tape the outlets, that they shouldn't use a scewdriver to try to get the paint out of the outlet holes?

Do you, in every report, tell them that they should not run an extention cord from a non-GFCI outlet to a location where GFCI is required?

Do you, in every report, tell them that AFCI breakers should be installed on all circuits that are not required to have GFCI?

I don't mind the disagreement, but to imply that somehow by calling this out (and ignoring the sparkys) you are doing your clients a better service, is misguided at best.

And to further imply that if we don't call it out, we are somehow not giving our clients "their money's worth" or "don't care" about them, is asinine.

Last edited by rmaday; 1/10/09 at 11:52 AM..
Reply With Quote
  #132  
Old 1/10/09, 11:04 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Perhaps this is why I will never be able to do 4 Inspections a day.

I actually give them their money's worth.
Let's not get nasty Bob.

Not ONE of you have given a legitimate reason as to WHY this receptacle is more deserving of additional protection than the ones just inside the exterior door ways. So I'm trying to figure out the "logic."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #133  
Old 1/10/09, 11:12 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Yeah, what Mike said too..

Quote:
Originally Posted by mlarson View Post
What's with this check list report crap?

How is that any part of this discussion?

P.S. I use HiPro just like you.
Reply With Quote
  #134  
Old 1/10/09, 1:20 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Please explain ,since it is required all kitchen receptacles be GFCI.
GFI protection is only required for the portions that serve the countertop surfaces. Receptacles near the eat-in are would not.
Reply With Quote
  #135  
Old 1/10/09, 1:29 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Interior GFCI Poll

Quote:
Originally Posted by relliott View Post
Paul I see nothing there about 12" below the surface,also wondering about the smiley cover up?

What smiley cover up....do you read everything into everything....it number 8 in done with () around it makes smiley face....so I wanted everyone to know it was an 8 and not a smiley face I had to change it to brackets to make it show the number 8....nothing more.....???

As for the 12"....read the following....I was refering to OTHER areas of the NEC saying the receptacle shown COULD not serve the countertop because of its location:

(5) Receptacle Outlet Location.
Receptacle outlets shall
be located above, but not more than 500 mm (20 in.) above,
the countertop. Receptacle outlets rendered not readily accessible
by appliances fastened in place, appliance garages,
sinks, or rangetops as covered in 210.52(C)(1), Exception,
or appliances occupying dedicated space shall not be considered
as these required outlets.

Exception to (5): To comply with the conditions specified in
(1) or (2), receptacle outlets shall be permitted to be
mounted not more than 300 mm (12 in.) below the countertop.
Receptacles mounted below a countertop in accordance
with this exception shall not be located where the
countertop extends more than 150 mm (6 in.) beyond its
support base.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How long are your poll lines? bchesser Miscellaneous Discussion for Inspectors 16 11/4/08 7:10 PM
Daily Presidential Tracking Poll - 10/19/2008 (McCain Lead Lost) jburkeson1 Miscellaneous Discussion for Inspectors 3 10/19/08 5:16 PM
Washington Home Inspectors Poll sstanczyk Legislation, Licensing & Legal Issues for Inspectors 164 1/30/08 8:30 PM
E&O information poll sstanczyk Miscellaneous Discussion for Inspectors 7 8/19/07 6:54 PM


All times are GMT -4. The time now is 8:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts